Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,826
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 432
    • 433
    • 434
    • …
    • 509
  • Next »

Is there an X Driver available for BACnet MS/TP?

Issue Can a Netcontroller II be used to communicate directly to BACnet MS/TP devices? Environment BACnet MS/TP RS-485 XDriver Netcontroller 2, NC2 bCX9640 Cause No X Driver is listed for BACnet MS/TP. Resolution There is no X Driver available for the BACnet MS/TP protocol to allow a NC2 to communicate to 3rd party MS/TP devices. However a bCX1 4040 can directly communicate to BACnet MS/TP on its Comm2 and is BTL listed to confirm compatibility. Also a bCX1 9640 can be converted to a 4040 by flashing it with the 4040 flash file available on the Extranet.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • Andover Continuum
1098 Views

M1500 on a V232

Issue Will a M1500 actuator fit onto a V232 valve? Environment M1500 Forta V232 Venta Cause Application assistance on Forta M1500 and Venta series V232 valve. Resolution The M1500 will fit, but since the V232 is only available in DN25,32, 40 and 50 size, we recommend using the smaller M400 or M800 instead.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • Field Devices
1861 Views

Replacement for Satchwell DDT0001 Duct Temperature Sensor due to obsolescence.

Issue Replacement for Satchwell DDT0001 Duct Temperature Sensor.  Environment Satchwell Sensor DDT DDT0001 Cause Obsolescence of Satchwell DDT0001 Duct Temperature Sensor. Resolution Replace Satchwell DDT0001 Duct Temperature Sensor with Schneider Electric STD660 Duct Temperature Sensor. The Schneider Electric STD660 provides the same functionality as the Satchwell DDT0001, differing only in its appearance, dimensions and terminal identification. The Schneider Electric STD660 Terminals are not polarised.    
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • Field Devices
1995 Views

Viewing white screens in R2 when browsing web pages in Internet Explorer 9

Issue Viewing white screens in R2 when browsing web pages in Internet Explorer 9   Environment R2 and G3 Niagara Cause Java conflict with Internet Explorer 9 Resolution Disable java option next generation plug-in: Open Java console under Control Panel Menu Go to Advance options Tab Expand Java Plug-in Uncheck Enable the next generation Java Plug-in Restart Browser for changes to take effect
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • TAC IA Series
1388 Views

Does Continuum support the use of Lotus Notes for emailing and paging of alarms.

Issue Customer does not have Microsoft Outlook/Exchange, only Lotus Notes/Domino. Environment Keywords: Email, Page, Lotus Notes Cause Customer wants email and paging of alarms but does not use Microsoft Outlook and Exchange. Resolution Lotus Notes is not a supported application for emailing or paging of alarms. Microsoft Outlook with Exchange is the only supported program for this application.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • Andover Continuum
971 Views

When converting a Niagara R2 server station from xml to db, the conversion fails with the following message: Could not create node "tridium.apps.ProgramNode".tridium.fo...

Issue When converting a Niagara R2 server station from xml to db, the conversion fails with the following message: ERROR: c:\niagara\r.301.529.v1\stations\PMHBASSERVER\config.xml(865566,98):  Could not create node "tridium.apps.ProgramNode".tridium.foundation.IllegalChildException E_ILLEGAL_CHILD_DUP_NAME {Command}    at tridium.foundation.node.NodeLifeCycle.pasteErrorCheck(NodeLifeCycle.java:153)    at tridium.foundation.node.NodeLifeCycle.paste(NodeLifeCycle.java:68)    at tridium.foundation.prism.Prism.commitTransactionImpl(Prism.java:1484)    at tridium.foundation.prism.Prism.commitTransaction(Prism.java:779)    at tridium.foundation.prism.NodeTransaction.commit(NodeTransaction.java:76)    at tridium.xml.node.NodeHandler.createNode(NodeHandler.java:105)    at tridium.xml.node.NodeHandler. (NodeHandler.java:42)    at tridium.xml.node.NodeHandler.startElement(NodeHandler.java:140)    at tridium.xml.TParser.doSTag(TParser.java:225)    at textuality.lark.Lark.reader(Lark.java)    at textuality.lark.Lark.readXML(Lark.java)    at tridium.xml.TParser.parse(TParser.java:121)    at tridium.tools.DbAdmin.readXml(DbAdmin.java:472)    at tridium.tools.DbAdmin.convert(DbAdmin.java:292)    at tridium.tools.DbAdmin.main(DbAdmin.java:168)    at tridium.tools.DbAdmin.main(DbAdmin.java:122)    at sun.reflect.NativeMethodAccessorImpl.invoke0(Native Method)    at sun.reflect.NativeMethodAccessorImpl.invoke(Unknown Source)    at sun.reflect.DelegatingMethodAccessorImpl.invoke(Unknown Source)    at java.lang.reflect.Method.invoke(Unknown Source)    at tridium.nre.Nre.mainImpl(Nre.java:663)    at tridium.nre.Nre.main(Nre.java:603) Parse of XML failed.  ----- End of input -----   Environment Niagara R2 Cause The conversion fails due to two program objects having duplicate names. Resolution Open the xml file using a xml editor (like Notepad++).  Navigate to line # 865566, character # 98 and identify the program object's name. Rename the program object by adding an additional character (like a number '1' or a letter 'a').  Save and close. Run the conversion to db again.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • TAC IA Series
1329 Views

License requirement for Excel Reports in Vista 5.1.X

Issue A specific license module is required for running reports in Excel from TAC Vista Environment Microsoft Excel 2003 / 2007 / XP Report generator : Report Generator...........................000882231 Report Generator – Upgrade..................000883231 Report Generator – 1 year subscription ..........000884230 TAC Vista version 5.1.X  Cause A separate license module for Vista Reports Generator is included in some license packages, but is sometimes required to be ordered separately if Reports are required as a feature. Resolution Part no 000882231 is for the Report Generator license in Vista version 5.1.X.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • TAC Vista
1254 Views

Detection of a "security threat" or vulnerability by Microsoft Security Essentials when downloading I/A Series G3

Issue Detection of a "security threat" or vulnerability by Microsoft Security Essentials when downloading I/A Series G3 Environment I/A Series G3 (all versions up to 3.6.31) Cause Recently, Oracle(R) has issued a critical patch update to address security vulnerabilities that currently exist within all versions of Java SE (Standard Edition).  Due to this patch update, Microsoft Security Essential scans have been updated to identify this as security vulnerability.  The detection by Microsoft Essentials is not a virus but a warning of a potential vulnerability that could be exploited for malicious use if precautions are not taken (e.g. firewalls, strong passwords, etc.). It is likely that McAfee, Norton, and other antivirus programs will also be issuing updates which identify this as vulnerability.  If the Niagara JRE is identified as vulnerability, it could lock down or quarantine the JRE, thus rendering Niagara unable to operate. Note: Oracle(R) is the owner of Java since 2009, although you still often see "Sun Hotspot" in references. Resolution In most cases, it is not critical that a new JRE (Java Runtime Environment) release be installed for I/A Series G3.  Typically, G3 resides behind a firewall and / or strong passwords are being used however, if required and/or directed by Product Support, the following procedure can be used to manually update the JRE on the Windows based Enterprise Server, Engineering Workstation, or I/A Series G3 ENC (Soft JACE) platforms.  JRE version 6 (update 31 or higher) is required. Note in steps below, / is your I/A Series G3 installation folder.     Download and install the desired JRE version 6 (update 31 or higher) from the Oracle web site.  For example,  Java SE Runtime Environment 6 Update 32 can be downloaded from http://www.oracle.com/technetwork/java/javase/downloads/index.html.  Select and download Windows x86 Offline (32-bit) for 32-bit platforms or Windows x64 (64-bit) for 64-bit platforms. The default installation folder is /Program Files/Java/jre(x) where (x) is the version. Stop all running Niagara stations and exit all Workbench instances. From a Niagara Console window, execute: plat uninstalldaemon Rename //jre to //jre_old Copy /Program Files/Java/jre(x) to / and make sure to rename the copied folder to jre. Copy //jre_old/lib/ext/mail.jar to //jre/lib/ext/mail.jar Copy //jre_old/jreVersion.xml to //jre/jreVersion.xml Update the version="n.n.n.n" string in the //jre/jreVersion.xml file to match the new JRE version. From a Niagara Console window, execute: plat installdaemon Restart Workbench and any stations.      
View full article
Picard Product_Support
‎2018-09-11 12:00 AM

Labels:
  • TAC IA Series
1331 Views

UNC event log shows multiple reboots and/or "Station Watchdog Timeout" messages.

Issue UNC station is frequently rebooting on its own and occasionally reports "Station Watchdog Timeout" in the error log. Environment I/A Series UNC 510 or UNC-520 Cause System Monitor task is causing the UNC to reboot. Typically this is caused by incorrect information in the drivers.properties file of the UNC. Resolution This issue can be corrected by editing the drivers.properties file in the UNC. To edit this file, Log into the UNC using the Admin tool. Select the Installation tab the select [Edit drivers.properties].  The file will be displayed in the text editor. Look for a line that reads sysmon.enable=true If the line is present, edit the line changing so that it reads sysmon.enable=false If the line is NOT present, add the line sysmon.enable=false at the end of the file. Select Save from the File menu to save the changes. Select Close from the File menu to close the editor. After editing the file, the station must be restarted to allow the change to take effect.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • TAC IA Series
1511 Views

Sigma Programmable object must respond to several digital object state changes

Issue A Programmable object must respond to a DI change in state, and then reset ready for the next change. Product Line Satchwell Sigma Environment Programmable Digital states Status DI Cause The programmable object will monitor the state of a number of other digital objects and if they change state, then an external alarm enunciator via a digital output point, will be enabled. To allow subsequent changes to be seen on the same point, the object value must return to zero, even if the changed state remains on after 60 seconds. Resolution The following object will check the state of four objects, but others can be added if required. Object numbers 33 - 37 are the monitored objects. Timer is set to 60 seconds, but can be set as required. (Line 110) Alarm priority can be set as required. (Line 120) 10 XInt = 0 20 IF POINT 0|33 ON THEN XINT = XINT + 1 30 IF POINT 0|35 ON THEN XINT = XINT + 1 40 IF POINT 0|36 ON THEN XINT = XINT + 1 50 IF POINT 0|37 ON THEN XINT = XINT + 1 60 IF XINT > YINT THEN GOTO 100 70 IF TIME LEFT THEN GOTO 120 80 IF XINT = 0 THEN YINT = 0 90 RETURN FALSE "reset" 100 YINT = XINT 110 SET TIMER 60 120 ALARM 1 130 RETURN TRUE "Alarm"  
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Satchwell BAS & Sigma
1039 Views

Replacement for Satchwell DR2253 Temperature Sensor due to obsolescence.

Issue Replacement for Satchwell DR2253 Temperature Sensor. Environment Satchwell Sensor DR DR2253 Cause Obsolescence of Satchwell DR2253 Temperature Sensor. Resolution The Satchwell DR2253 Temperature Sensor is replaced with the Schneider Electric STR614 Temperature Sensor. The Schneider Electric STR614 provides the same functionality as the Satchwell DR2253, differing only in its appearance, dimensions and terminal identification. The Schneider Electric STR614 terminals are not polarised.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Field Devices
1084 Views

Is it possible to use an analog valve on the TAC Xenta 121-FC even if I want to have the LED mode indicator on a STR-101 through STR-107?

Issue When using STR101 to STR-107 connected to a TAC Xenta 121-FC, the LED Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC, which is the only analog output on the TAC Xenta 121-FC device. Environment TAC Xenta 120-FC STR-101 STR-102 STR-103 STR-104 STR-105 STR-106 STR-107 Cause When using any of STR-101 to STR-107 connected to a TAC Xenta 121-FC, the LED Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC device, which is the only analog output on the TAC Xenta 121-FC device. Resolution In ZBuilder, it is possible to move the Status LED from the default location at Y1 to K1-4. In this case you also need to have an external power supply with 5 Volt DC for the LED indicator. It is also possible to use 24 Volt AC power supply for the LED indicator, however this will make an incorrect temperature reading of about 0.5 degree C. In this case, add a 5 kΩ resistance (4.7 - 5,1 kΩ) ¼W in one of three possible positions: Between G and KC1 Between K1 and LED 16 Between Mx 15 and M. The resistor must be placed outside the STR device.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • TAC Vista
1147 Views

Spring return actuator for VF208W butterfly valve

Issue In some applications a spring return actuator is requested/required Environment VF208W Cause application requirement Resolution No spring return actuator is currently available for VF208W. However, there is a plan for this in the near future.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Field Devices
1455 Views

M-SM damper actuator replacement

Issue Since the M-SM actuator no longer is available, a replacement is requested. Environment M-SM 8700000000 MD20B-24 8751025000 AUX Switches: Old: S1-B 9141000000 S2-BB 9141010000 New: MD-S1 9141060000 MD-S2 9141061000 Cause Replacing obsolete actuator  Resolution The M-SM is replaced by the MD20B-24. If AUX switches are used, S1-B is replaced by MD-S1, and S2-BB is replaced by MD-S2.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Field Devices
1085 Views

Unable to run Database Initialization. Receive error stating that "You must have NT local administrator access...".

Issue Unable to run the  Database Initialization application. Receive error stating that "You must have NT local administrator access...". Even after logging in as a local administrator the same error occurs. Environment Continuum Cyberstation Windows Server 2008 Domain Cause The instances of this that have been reported all seem to be where there has been an upgrade to or new installation of Windows Server 2008 where the system is part of a Domain. It is not entirely understood at this time but something to do with the Domain policies being pushed down to the Workstations is causing problems.   Resolution Until the cause can be properly identified, a workaround that has worked in most cases has been to create/setup a local Administrator account and then run Database Initialization as an Administrator. Shut down all Cyberstations. Right-click Database Initialization and select "Run as... Administrator". With the EUR domain in the UK the following has been found - XP                 - "Right click" on the "Database Initialization shortcut" and “Run As” use local admin - Windows 7 - "Shift" & "Right click" on the "Database Initialization shortcut" and “Run as a different user”, use local admin
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Andover Continuum
1532 Views

Is it possible to change the colors for the alarm list in Webstation?

Issue Is it possible to change the colors for the alarm list in Webstation? Environment TAC Vista Webstation 5.1.x   Cause The colors for the alarm list in Webstation are inherited from Vista Workstation.  Resolution To change the colors for the alarm list in Webstation change the colors for the alarm list in Workstation and Webstation will inherit the colors. Change the colors in workstation: Right click on a alarm in the alarm list and open the properties for it. Go to "Customize". Click on the "Text" tab. Change the color. Open the "File" menu and "Save My Program Settings"
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • TAC Vista
1171 Views

Transfer SNVT (network variables) between lon devices in a TAC Vista Classic scenario

Issue Transfer SNVT (network variables) between lon devices in a TAC Vista Classic scenario. Can't bind in classic network; how to send SNVTs from one lon device to another? Environment TAC Vista Classic scenario LonWorks devices Cause If you are using TAC Vista in a classic scenario, no real SNVT bindings can be made. Resolution Use object transfer to send the values. Note that the server have to be running for the values to be transferred. For more info on how to set up object transfer, see Chapter 14 in the TAC Vista Technical Manual.
View full article
Picard Product_Support
‎2018-09-11 01:12 AM

Labels:
  • TAC Vista
1526 Views

Stuffing box Type T

Issue Spare stuffing box (packing box) that fits a number of older valves. Environment Stuffing box Type T part no 0802064005 V221 V223 V265 V294 V295 V298 V353 V395-1 V396-1 Cause This spare stuffing box fits a number of different valves from the old and current TAC Schneider Electric portfolio. Resolution Stuffing box Type T part no 0802064005 fits the following valves: V221, V223, V265, V294, V295, V298, V353, V395-1, V396-1 NB: this product will be terminated by Dec 31, 2013.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Field Devices
1096 Views

What does the message "This Part has Alternate Replacements" mean in regards to the MNL-800-101, as displayed in iPortal?

Issue What does the message "This Part has Alternate Replacements" mean in regards to the MNL-800-101, as displayed in iPortal? Environment MNL-800-101 Cause See Product Announcement PA-207 regarding a parts shortage regarding the capacitor used for memory backup on the MNL-800-101 Resolution The MNL-800-102 is being shipped as a replacement for the MNL-800-101 until such time as the capacitor parts shortage has been resolved. As documented in Product Announcement PA-00207, the capacitor used for memory backup power storage in the MNL-800-101 is temporarily unavailable.  The capacitor used in the MNL-800-102 does not have the same temperature rating (-13 Deg F instead of -40 Deg F).
View full article
Picard Product_Support
‎2018-09-10 12:37 PM

Labels:
  • TAC IA Series
1058 Views

How to safely de-commission an Access Controller with configured Doors and Personnel.

Issue How to safely de-commission an Access Controller with configured Doors and Personnel. Environment Continuum Cyberstation Access Controllers Cause In the past, when deleting Access controllers from a live site, problems have been encountered with controllers that had pending Personnel distributions. Resolution As long as there are no pending distributions to the controller, deleting the controller from Continuum should be problem free. The problem with distributions begins when a controller is still defined in the database but is not online. Any changes to personnel in this offline controller will be "buffered" until the controller comes back online. Deleting the controller device object out of the database stops these distributions from being attempted in the first place.   The most comprehensive method of removing personnel from a controller during de-commissioning is to do the following: For the Personnel, remove access to the Areas that the controller supplies access too. These changes will then distribute down to the controller and remove these personnel from it. Once the distributions are complete, remove the Areas from the door objects in the controller, if not using profiles.  (When using profiles in the Personnel Manager do not remove Areas, this can potentially cause database issues)  Then to complete the de-commissioning, delete the controllers Device object from the Continuum database.  
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Andover Continuum
1326 Views
  • « Previous
    • 1
    • …
    • 432
    • 433
    • 434
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of