Transfer SNVT (network variables) between lon devices in a TAC Vista Classic scenario
  • Transfer SNVT (network variables) between lon devices in a TAC Vista Classic scenario
‎2018-09-11 01:12 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 03:20 AM
Transfer SNVT (network variables) between lon devices in a TAC Vista Classic scenario.
Can't bind in classic network; how to send SNVTs from one lon device to another?
TAC Vista Classic scenario LonWorks devices
If you are using TAC Vista in a classic scenario, no real SNVT bindings can be made.
Use object transfer to send the values. Note that the server have to be running for the values to be transferred.
For more info on how to set up object transfer, see Chapter 14 in the TAC Vista Technical Manual.
Tags (2)