Sigma Programmable object must respond to several digital object state changes

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Sigma Programmable object must respond to several digital object state changes
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1039 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Sigma Programmable object must respond to several digital object state changes

Picard Product_Support
‎2018-09-06 12:11 PM

Issue

A Programmable object must respond to a DI change in state, and then reset ready for the next change.

Product Line

Satchwell Sigma

Environment

  • Programmable
  • Digital states
  • Status
  • DI

Cause

The programmable object will monitor the state of a number of other digital objects and if they change state, then an external alarm enunciator via a digital output point, will be enabled.

To allow subsequent changes to be seen on the same point, the object value must return to zero, even if the changed state remains on after 60 seconds.

Resolution

The following object will check the state of four objects, but others can be added if required.

Object numbers 33 - 37 are the monitored objects.

Timer is set to 60 seconds, but can be set as required. (Line 110)

Alarm priority can be set as required. (Line 120)

10 XInt = 0
20 IF POINT 0|33 ON THEN XINT = XINT + 1
30 IF POINT 0|35 ON THEN XINT = XINT + 1
40 IF POINT 0|36 ON THEN XINT = XINT + 1
50 IF POINT 0|37 ON THEN XINT = XINT + 1
60 IF XINT > YINT THEN GOTO 100
70 IF TIME LEFT THEN GOTO 120
80 IF XINT = 0 THEN YINT = 0
90 RETURN FALSE "reset"
100 YINT = XINT
110 SET TIMER 60
120 ALARM 1
130 RETURN TRUE "Alarm"

 

Labels (1)
Labels:
  • Satchwell BAS & Sigma
Tags (1)
  • Find more articles tagged with:
  • 8229
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of