Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 414
    • 415
    • 416
    • …
    • 501
  • Next »

SCD100 output signal

Issue There is a confusion regarding the output signal options since the data sheet states 0-10V, 0-5V and 2-10V in different places  Environment SCD100 SCD100-D Cause Incorrect output signal range Resolution The output signals available are 0-10V and 0-5V.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Field Devices
982 Views

Visitor Management Software: EasyLobby

Issue Can the EasyLobby software be integrated to I/NET Seven only, or can it be integrated to the I/NET Host Tool? Do you have a detailed configuration guide to integrate to I/NET systems? Is there any Visitor Management Software (VMS) that works with I/NET? Product Line TAC INET Environment I/NET Seven I/NET Host Tool EasyLobby Visitor Management Software (VMS) Easy Lobby Cause I/NET site and client is requesting a Visitor Management Software Resolution Concerning EasyLobby, they have a full integration to I/NET; however, it was not a joint effort. They did it on their own without I/NET R&D involvement. I/NET development/PSS has never tested it, and will not support the integration in any way. Please contact  EasyLobby support if there are any integration issues. The product is only supported on Continuum because Continuum in Boston & EasyLobby did that integration together. EasyLobby obtained a copy of v2.40 of I/NET and did their own interface without Product Support Services.  For third party individual management software programs which work with I/NET, search the Knowledge Base for "ID Works."
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • TAC INET
1770 Views

When trying to install the I/A Series Software (release 514 or later) on a new computer, an error is displayed that indicates Java is required. Where do I get it and what version...

Issue When trying to install the I/A Series Software (release 514 or later) on a new computer, an error is displayed that indicates Java is required.  Where do I get it and what version is required? Environment I/A Series R2 Software release 5.14 or later. Cause Microsoft can no longer distribute the Java JRE (Java Runtime Environment) with its operating systems.  The I/A Series R2 software, release 514 and later, requires the industry standard Java JRE to be installed on the computer before installing the I/A Series software. Resolution Download and install the latest available release of Java version 6 or 7, based on your version of Windows. The software can be downloaded from the web site http://www.java.com.  The site normally detects your operating system and provides the proper version when you click the [Free Java Download] button on that site. Java version 6 update 10 is the minimum recommended release for the I/A Series R2 software.
View full article
Picard Product_Support
‎2018-09-06 12:54 PM

Labels:
  • TAC IA Series
1301 Views

Continuum HVAC Programmers Edition, Security Programmers Edition and Integrated Programmers Edition?

Issue What is the difference between Continuum  HVAC Programmers Edition, Security Programmers Edition and Integrated Programmers Edition?  Environment Continuum CyberStation  Cause Do not know the difference between Continuum  HVAC Programmers Edition, Security Programmers Edition and Integrated Programmers Edition?  Resolution HVAC Programmers Edition is for configuring, programming and administering HVAC systems. Security Programmers Edition is for configuring, programming and administering Security systems. Integrated Programmers Edition is for configuring, programming and administering HVAC and Security systems.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Andover Continuum
1470 Views

In upgrading to WorkPlace Tech 5.x from 4.x, what is there to understand about the project files during this conversion?

Issue In upgrading to WorkPlace Tech 5.x from 4.x, what is there to understand about the project files during this conversion? Environment WorkPlace Tech 4.x, 5.x Cause Host operating system changing from Windows XP to Windows 7 and WorkPlace Tech 4.x is not compatible with Windows 7. Resolution A few things to keep in mind: When a drawing from 4.x is opened in 5.x for the first time, the conversion may take awhile. Be patient and let it finish. Once the drawing is converted to 5.x, it cannot be converted back to 4.x. Keep a backup of the 4.x files just in case. Similarly, once a controller is downloaded with a database using 5.x, the controller will no longer work with WorkPlace Tech 4.x. If, for some reason, it needs to be used with WorkPlace Tech 4.x, then its database will have to be reloaded using 4.x first.  
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • TAC IA Series
1098 Views

What is the default IP address configured with a new jace-nxt for Niagara G3?

Issue What is the default IP address configured with a new jace-nxt for Niagara G3? Environment Jace-nxt Jace-nxs Cause Initial powerup connection with Workbench Resolution A new JACE-NX controller with Niagara G3 has the following TCP/IP settings for its two Ethernet ports:   Primary (top) port: 192.168.1.19n (static IP) with subnet mask: 255.255.255.0      where the last numeral (n) matches the last numeral in the JACE's serial number   Secondary (bottom) port: disabled in BIOS, no assigned address   Usage of secondary port requires attaching a local console (keyboard, mouse, monitor) to the JACE-NX, rebooting the unit, then entering BIOS setup at power-on self test (POST) to enable the port.   Intended usage of the secondary port is for isolating a "driver's" Ethernet traffic from the primary port. Enabling the secondary port is generally discouraged, unless deemed absolutely necessary.   The primary factory-assigned IP address should also be listed on the packing slip that accompanied the JACE. If needed, change these IP network settings during your startup commissioning of the JACE.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • TAC IA Series
1591 Views

The Xenta Server can't be Downloaded in XBuilder

Issue When downloading the XBuilder project to the Xenta Server, an error shows that the connection to the Xenta Server is timeout. But the ping to the Xenta Server is fine. Environment Xenta Server Xenta 511, 527, 701, 711, 721, 731, 913 Vista Cause The possible cause is that there is proxy setting in the IE browser. It may cause the communication issue with XBuilder and Xenta Server. Resolution Cancel the proxy setting in the Connection setting of IE browser.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • TAC Vista
1566 Views

VZ308 ports

Issue Defining flow direction in VZ308 valve. Environment VZ308 Cause Flow direction definition in mixing application. Resolution As described in the data sheet: The valves should be installed as mixing valves, with ports connected as: Port AB: Combined flow outlet Port A: Controlled flow inlet Port B: Bypass inlet
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Field Devices
1283 Views

Spare stuffing box for valves

Issue Which valves will the part no 100108000 spare stuffing box fit, and which sizes of these valves? Environment 100108000 (1-001-0800-0) spare stuffing box (Venta) V241, V341, V231, V232, V211, V211T, V212, V212T, V311, V311T Cause suitable spare stuffing box Resolution 100108000 (1-001-0800-0) spare stuffing box (Venta) works with the following valves in all dimensions:  V241, V341, V231, V232, V211, V211T, V212, V212T, V311, V311T
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Field Devices
1438 Views

Plain English error: The specified directory service attribute or value does not exist.

Issue While trying to create a point mirroring program with multiple lines. Several (but not all) lines with references to remote Infinet points indicate the above error.  Environment CyberStation v1.93 Plain English IDE Net2 with Infinet2's Cause The following error occurs on several lines of a program being saved: "The specified directory service attribute or value does not exist" Resolution Reload the remote controllers (the Infinet controllers with the points creating the errors in the PE program) Delete the mirroring point program in the Net2. Reload the Net2. Recreate the program in the Net2 and save successfully.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Andover Continuum
1464 Views

Process to Move I/NET system from one machine to another

Issue Process to Move I/NET system from one machine to another so that all configuration settings remain the same. Environment I/NET Cause When copying an I/NET system from one machine to another, one must ensure that all configuration data remains the same.  This data is not all stored within an SQL back up, so additional steps are required. Resolution Back up original PC  -  Back up the Database Open I/NET DbCreate Application Select Verify Db.  Press Start, Ensure there are no errors Select Backup Press Start, Save the file to an external drive  -  Back up the Graphics Files Note the exact folder path for I/NET Graphics (example: C:\Inet Seven Data\Graphics) Copy all Graphics files to an external drive  -  Back up the I/NET Host Configuration (I/NET must be shut down) Open the registry editor (Start - Run - regedit) Expand the HKEY_Local_Machine Folder Expand the SOFTWARE folder Expand the CSI - Control Systems International folder Expand the I/Net 200 Folder Expand the Configurations Folder Right click on the active configuration profile and select Export Save this to an external drive  -  Back up the AMT Configuration (I/NET must be shut down) Open the registry editor (Start - Run - regedit) Expand the HKEY_Local_Machine Folder Expand the SOFTWARE folder Expand the CSI - Control Systems International folder Expand the I/Net 200 Folder Right Click on the Host Configuration folder and select Export Save this to an external Drive Restore to new PC Install I/NET onto the new PC  -  Restore the Database Open I/NET DbCreate Application Select Restore Press Start Choose the file created during the backup process Close DbCreate  -  Restore the Graphics Files Create the exact folder path for I/NET Graphics used on the previous machine (example: C:\Inet Seven Data\Graphics) Copy all Graphics files to this new location.  -  Restore the I/NET Host Configuration (I/NET must be shut down) Copy the file created during the backup process to the new machine Double click on this file to restore registry settings  -  Back up the AMT Configuration (I/NET must be shut down) Copy the file created during the backup process to the new machine Double click on this file to restore registry settings
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • TAC INET
1470 Views

Attempting to "export" BACnet points from an I/A Series G3 ENC-410 or ENC-520 generates the following "Fault: Server capability is not licensed."

Issue Attempting to "export" BACnet points from an I/A Series G3 ENC-410 or ENC-520 generates the following "Fault: Server capability is not licensed." Environment I/A Series G3, ENC-410, ENC-520 Cause By default, the ENC-410 and ENC-520 platform supports BACnet IP and BACnet Ethernet as a Client only.  Attempting to configure the BACnet IP or BACnet Ethernet to serve or export BACnet point data will generate the fault. Resolution BACnet export capability is enabled through the purchase of the Enterprise Connectivity Pack (P2P) option.  The part number for the ENC-410 is ENC-410-P2P.  This feature enables Peer-to-peer connectivity ENC-to-ENC and ENC-to-Enterprise Network Server communications links, as well as the BACnet Export capability. The part number for the ENC-520 is ENC-520-P2P.  This feature enables Peer-to-peer connectivity ENC-to-ENC and ENC-to-Enterprise Network Server communications links, as well as the BACnet Export capability.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • TAC IA Series
1290 Views

COV updates fail to re-establish after referenced controller comes back from a power failure.

Issue Change of Value updates fail to re-establish after referenced controller comes back from a power failure. The referencing program goes to Disabled. Environment Continuum BACnet Cause Remote point mapping program goes to Disabled when the referenced control is offline. With the program disabled, the COV subscriptions are not re-established until the program is re-enabled manually or is reloaded to the controller. Resolution Setup a Line E at the end of your program. When an error occurs, and before the program disables, the program will cycle to line E and the below code will be executed.    Fallthru Program . . . Line E   ErrorCount = ErrorCount +1  'numeric created to store number of times it hits this line.   stop   Looping Program . . . Line E   ErrorCount = ErrorCount +1  'numeric created to store number of times it hits this line.   goto wait30 Line wait30 If ts > 30 then goto xxx 'goto top of program for another attempt                
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Andover Continuum
1491 Views

Where to find Loytec NIC drivers

Issue Where to find Loytec NIC drivers Environment Loytec NIC drivers Cause Need to get the latest drivers for loytec NIC. Resolution All drivers can be found at Loytec.com under Support - Downloads. The one for the NIC is called NIC - LOYTEC Network Interface Software
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • TAC Vista
1261 Views

VZ308 with Normally Open (NO) actuator

Issue Need an actuator that is Normally Open in case of power failure or similar. Environment MZ308 actuator Cause No currently available actuator fulfills this requirement Resolution Controlli MVR actuator will be suitable for this type of application.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Field Devices
947 Views

Running 220V through the Forta S2 switches

Issue When replacing a EM5C BB actuator with a TAC Forta, the EM5C BB may have had  220V running through the switches to control pumps or similar.  Environment TAC Forta with S2 option Cause Using the S2 option to control 220V power supply. Resolution The S2 option is in no way designed to handle 220V, and we do NOT recommend this.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Field Devices
1062 Views

STD300 flange material

Issue There is a difference between the STD300 sensor flanges compared to the ones pictured in the data sheets. Environment STD300 Cause Design differences between picture on data sheet and actual sensor. Resolution There was a slight design change on the sealing flange a while ago where the metal piece was replaced by a plastic flange. This to get a more flexible surface to the duct, and therefore a better seal.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Field Devices
1024 Views

Reason Code 12 error during Send to Database.

Issue Continuum displays Reason Code 12 error During Send to Database on BACnet/IP device. Environment 3rd party BACnet Continuum BCX4040 BACnet over IP Cause Third party device is not accessible to Continuum following configuration change by vendor. Resolution Restore communication to 3rd party device.
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • Andover Continuum
1370 Views

Alarms no longer showing up in Active Alarm View on Continuum SU.

Issue Following a reboot of CyberStation, alarms continue to be logged but are not displayed in Active Alarm View. Environment CyberStation Active Alarm View Continuum Database Initialization Cause Alarms not being displayed in Active Alarm View. Resolution Performed a Database Initialization with Enhanced Alarm Logging and Enhanced Alarm Delivery selected on the workstation.
View full article
Picard Product_Support
‎2018-09-06 12:49 PM

Labels:
  • Andover Continuum
2212 Views

Always have SNVT on the top level in the application, and not in HFB

Issue New SNVTs are not always added in the end of the XIF-file when using HFB-blocks. Environment TAC Menta TAC Xenta Programmable Controllers Xenta 280, Xenta 281, Xenta 282, Xenta 283, Xenta 300, Xenta 301, Xenta 302, Xenta 401, Xenta 401:B Cause When using HFB-blocks in TAC Menta, the HFB will only be in the application file, and will never be sent down to the device. However, all the blocks belonging to an HFB will be stored together in the application file, this means that if you add a SNVT inside an HFB, it will not always be added last in the XIF-file. Resolution When program SNVT in TAC Menta, always put the SNVT on the top level in TAC Menta, and not inside an HFB block.
View full article
Picard Product_Support
‎2018-09-06 12:49 PM

Labels:
  • TAC Vista
1442 Views
  • « Previous
    • 1
    • …
    • 414
    • 415
    • 416
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore