When downloading the XBuilder project to the Xenta Server, an error shows that the connection to the Xenta Server is timeout. But the ping to the Xenta Server is fine.
  • Xenta Server
  • Xenta 511, 527, 701, 711, 721, 731, 913
  • Vista
The possible cause is that there is proxy setting in the IE browser. It may cause the communication issue with XBuilder and Xenta Server.
Cancel the proxy setting in the Connection setting of IE browser.