Issue
Following a reboot of CyberStation, alarms continue to be logged but are not displayed in Active Alarm View.
Environment
- CyberStation
- Active Alarm View
- Continuum Database Initialization
Cause
Alarms not being displayed in Active Alarm View.
Resolution
Performed a Database Initialization with Enhanced Alarm Logging and Enhanced Alarm Delivery selected on the workstation.