Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Field Devices
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "field devices"

View in: "Building Automation Knowledge Base" | Community

721 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 37
  • Next »
Label: "Field Devices" Show all articles

SHD100: Using 24V AC power supply and 4-20mA output signal

Issue The data sheet only lists AC power supply as an option when using the 0-10V output signal Environment SHD100 006902320 SHD100-T 006902330 Cause Sensor configuration options. Resolution For a transmitter the operating (normal) current is at once the measuring signal. If a rectified output is requested this means that DC voltage as supply voltage is required.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • Field Devices
1650 Views

Replacing M15C on brand X butterfly valve

Issue Since the M5/M15 series actuator is no longer available, a replacement actuator is requested.  Environment M15 M9B TRV mounting kit 8600991000 Cause Replacing obsolete actuator. Resolution M9B together with the TRV mounting kit should work.
View full article
Picard Product_Support
‎2018-09-06 12:18 PM

Labels:
  • Field Devices
1142 Views

Modulating actuator for VG221F

Issue Which actuator is suitable for the MG221F valve when modulating control signal (0-10V) is required? Environment VG221F M800 M1500 Forta Cause There are a few different actuators listed in the VG221F documentation, but not all of them are available with modulating 0-10V control signal.  Resolution The Forta M800 and M1500 are both listed as suitable actuators for the VG221F, and both are capable of using the modulating 0-10V control signal.
View full article
Picard Product_Support
‎2018-09-06 12:17 PM

Labels:
  • Field Devices
1325 Views

Replacement for Forta M500B actuator.

Issue Since the Forta M500B actuator is no longer available in our portfolio, a replacement is requested. Environment TAC Forta M500B M400 M800 Cause Replacing old, obsolete actuator. Resolution Depending on valve size and required force, Forta M400 or M800 are the recommended replacement actuators.
View full article
Picard Product_Support
‎2018-09-06 12:16 PM

Labels:
  • Field Devices
979 Views

Replacement for actuator M6B.

Issue Since the actuator M6B is no longer available in our portfolio, a replacement actuator is requested. Environment M6B VTRM Cause Replacing the obsolete M6B actuator. Resolution There is no replacement actuator for the M6B in the Schneider Electric portfolio. However, the manufacturer ESBE (http://www.esbe.se/) should still have the M6B in their portfolio in both 0-10V and 4-20mA versions. No cross reference to their part numbers are currently available.
View full article
Picard Product_Support
‎2018-09-06 12:21 PM

Labels:
  • Field Devices
1174 Views

Stuffing box for valve V392

Issue Replacement stuffing boxes for V392 Environment V392 Spare stuffing boxes: DN15 type V: 0804343005 DN15 type X: 0804362005 (glycol) DN20-50 type T: 0802064005 DN20-50 type Q: 0804724005 (glycol) Cause Replacement parts for obsolete valve V392 Resolution Spare stuffing boxes for DN15 was withdrawn in 20101231. For DN20-50, they will be withdrawn in 20141231. Please contact your Orders Dept for more details and availability.
View full article
Picard Product_Support
‎2018-09-06 12:15 PM

Labels:
  • Field Devices
1017 Views

Controlli MVL56 (Forta M700) spare parts

Issue Spare parts availability for Controlli MVL56 (Forta M700) Environment Controlli MVL56 Forta M700 Cause Replacement parts   Resolution Due to the spring return design of this actuator, no spare parts are available, with the possible exception of the PCBA. Any repairs should be done by the factory for safety reasons. However, MVL56 is a Controlli product and they should be contacted directly for further details. If the M700 fails after the warranty then a new actuator is required, the MG900 SR is a lower cost alternative to the M700.
View full article
Picard Product_Support
‎2018-09-06 12:15 PM

Labels:
  • Field Devices
1999 Views

Can more than one MS41-7153 actuator be paralleled when being driven by a MNB series controller?

Issue Can more than one MS41-7153 actuator be paralleled when being driven by a MNB series controller? Environment MNB series controller Several MS41-7153 actuators controlled by a common signal. Cause Series of parallel dampers are to be controlled by the same control signal. Resolution Yes several MS41-7153 actuators can be driven by the analog output from a MNB series controller. There are two acceptable methods of providing parallel control. 1. Control the first actuator using either the voltage output or current output from the controller and cascade control from the feedback AO of one actuator into the AI of the next actuator.  The AO of the last actuator should be routed back to the controller to provide feedback confirmation of the damper operation.  In this way should any damper fail, the feedback will indicate that one (or more) of the actuators did not drive to the desired position.  Using this method there is theoretically no limit to the number of actuators that could be driven from one controller AO output.  When controlling a series of actuators in this manner, you must make sure that the power to the actuators are phased correctly, especially if using more than one transformer.   2. Alternate method for use with four or less actuators.  Up to four actuators may be driven using the 4-20 ma drive from the controller.  The 500 ohm resistor should be connected across the actuator wired closest to the controller.  When using this method, and more than two actuators are being parallel controlled, the resistance of the parallel resistor may need to be increased slightly or the drive signal may need to be increased by as much as 2.5% to make up for the parallel resistance effect of the 80 k-ohm input impedance of the actuators.
View full article
Picard Product_Support
‎2018-09-06 12:15 PM

Labels:
  • Field Devices
  • TAC IA Series
1054 Views

Replacement for Forta with STS safety feature

Issue The STS safety feature for Forta actuators is obsolete since a few years. Environment Forta STS M700 MG900 Cause With the Forta STS battery safety feature no longer available, a replacement actuator with similar safety function is requested. Resolution Depending on torque requirements, the Forta M700 and Forta MG900 spring return actuators are available. Just make sure the correct closing direction (stem up/stem down) is defined when ordering these actuators.
View full article
Picard Product_Support
‎2018-09-06 12:15 PM

Labels:
  • Field Devices
1116 Views

Pressure sensor using 4-20 mA signal

Issue Are there any pressure sensors in the Schneider Electric portfolio that uses the 4-20mA signal? Environment Pressure sensor Cause Cannot find any 4-20mA pressure sensors in the current portfolio Resolution No pressure sensor in the current portfolio is using the 4-20mA signal
View full article
Picard Product_Support
‎2018-09-06 12:15 PM

Labels:
  • Field Devices
1210 Views

Mounting MF20/MF40 actuator in 90 degrees position

Issue Is it possible/suitable to mount the MF20 or MF40 actuator in 90 degrees angle out from the valve VF208W? Environment MF20 MF40 VF208W Cause In some applications/environments it is hard to fit in the actuator on top of the valve due to space limits. Resolution There should be no problem mounting the actuator / linkage in a 90 degree angle out from the valve.
View full article
Picard Product_Support
‎2018-09-06 12:14 PM

Labels:
  • Field Devices
1014 Views

Replacing actuator M44PBB on valve STM-G

Issue Both valve and actuator in question are obsolete. In this case the valve is still OK, while the actuator is in need of replacement. Environment M44 STM-G M9B/24 8601010000 mounting kit 8600990000 Cause Replacement of obsolete actuator Resolution M9B/24 (8601010000) together with mounting kit 8600990000 will replace the M44PBB when used on STM-G. The only feature missing would be the potentiometer.
View full article
Picard Product_Support
‎2018-09-06 12:14 PM

Labels:
  • Field Devices
1096 Views

VG221F and Glycol

Issue Is it possible to use the VG221F valve in applications with a glycol content up to 50%? Environment VG221F Cause Some valves are not suitable for use in applications with glycol content in media. Resolution The VG221F can be used in applications with deaerated water with glycol-type antifreeze agent (max 50%)
View full article
Picard Product_Support
‎2018-09-06 12:13 PM

Labels:
  • Field Devices
962 Views

Replacement valve for V354

Issue Since the V354 is obsolete, a replacement valve is requested. Environment V354 part no 7315425000 Spare stuffing box part no 0804629005 Cause Replacing obsolete valve  Resolution No replacement valve is available. Pipe work is required due to port configuration. A spare stuffing box, part no 0804629005, is available for ordering.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • Field Devices
1912 Views

M1500 on a V232

Issue Will a M1500 actuator fit onto a V232 valve? Environment M1500 Forta V232 Venta Cause Application assistance on Forta M1500 and Venta series V232 valve. Resolution The M1500 will fit, but since the V232 is only available in DN25,32, 40 and 50 size, we recommend using the smaller M400 or M800 instead.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • Field Devices
2066 Views

Replacement for Satchwell DDT0001 Duct Temperature Sensor due to obsolescence.

Issue Replacement for Satchwell DDT0001 Duct Temperature Sensor.  Environment Satchwell Sensor DDT DDT0001 Cause Obsolescence of Satchwell DDT0001 Duct Temperature Sensor. Resolution Replace Satchwell DDT0001 Duct Temperature Sensor with Schneider Electric STD660 Duct Temperature Sensor. The Schneider Electric STD660 provides the same functionality as the Satchwell DDT0001, differing only in its appearance, dimensions and terminal identification. The Schneider Electric STD660 Terminals are not polarised.    
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Labels:
  • Field Devices
2218 Views

Replacement for Satchwell DR2253 Temperature Sensor due to obsolescence.

Issue Replacement for Satchwell DR2253 Temperature Sensor. Environment Satchwell Sensor DR DR2253 Cause Obsolescence of Satchwell DR2253 Temperature Sensor. Resolution The Satchwell DR2253 Temperature Sensor is replaced with the Schneider Electric STR614 Temperature Sensor. The Schneider Electric STR614 provides the same functionality as the Satchwell DR2253, differing only in its appearance, dimensions and terminal identification. The Schneider Electric STR614 terminals are not polarised.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Field Devices
1188 Views

Spring return actuator for VF208W butterfly valve

Issue In some applications a spring return actuator is requested/required Environment VF208W Cause application requirement Resolution No spring return actuator is currently available for VF208W. However, there is a plan for this in the near future.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Field Devices
1569 Views

M-SM damper actuator replacement

Issue Since the M-SM actuator no longer is available, a replacement is requested. Environment M-SM 8700000000 MD20B-24 8751025000 AUX Switches: Old: S1-B 9141000000 S2-BB 9141010000 New: MD-S1 9141060000 MD-S2 9141061000 Cause Replacing obsolete actuator  Resolution The M-SM is replaced by the MD20B-24. If AUX switches are used, S1-B is replaced by MD-S1, and S2-BB is replaced by MD-S2.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Field Devices
1260 Views

Stuffing box Type T

Issue Spare stuffing box (packing box) that fits a number of older valves. Environment Stuffing box Type T part no 0802064005 V221 V223 V265 V294 V295 V298 V353 V395-1 V396-1 Cause This spare stuffing box fits a number of different valves from the old and current TAC Schneider Electric portfolio. Resolution Stuffing box Type T part no 0802064005 fits the following valves: V221, V223, V265, V294, V295, V298, V353, V395-1, V396-1 NB: this product will be terminated by Dec 31, 2013.
View full article
Picard Product_Support
‎2018-09-06 12:11 PM

Labels:
  • Field Devices
1181 Views
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 37
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore