Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1824 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 18
    • 19
    • 20
    • …
    • 92
  • Next »
Label: "TAC IA Series" Show all articles

Modbus device integration to I/A Series R2 requires encode and decode of integer type registers to bytes.

Issue Modbus device integration to I/A Series R2 requires encode and decode of integer type registers to bytes. In this particular case, the Modbus device is a Patterson-Kelly ENVI boiler where the HIGH byte and LOW byte of a standard Modbus integer represent individual values.  However, the solution can be applied to other devices as required. Environment I/A Series R2, Modbus Cause Application - integration of Modbus into I/A Series R2 Resolution The attached R2 program objects can be used to encode or decode values as required. ModbusIntToBytes - Program will take the input integer value and decode to individual byte values as float status type values. ModbusBytesToInt - Program will take individual float status type values and encode bytes to a Modbus integer. Download ModbusIntBytePgms zip file ...
View full article
Picard Product_Support
‎2018-09-10 06:29 AM

Labels:
  • TAC IA Series
1318 Views

Finding LON devices under a different domain length with NodeUtil.

Issue  Unable to find or learn devices under Niagara. Environment R2 or G3 Niagara Cause Unable to find or learn devices under Niagara.  The LON device or devices may be configured to a different domain length.  Resolution To find devices under a different domain length download procedure click here
View full article
Picard Product_Support
‎2018-09-10 01:54 AM

Labels:
  • TAC IA Series
1172 Views

Outside dimensions of the enclosure for the MNB-1000? Part Number MNB-1000-ENC.

Issue Outside dimensions of the enclosure for the MNB-1000? Part Number MNB-1000-ENC. Environment Plant Controller, MNB-1000 Enclosure for the Plant Controller, MNB-1000-ENC Cause Need to determine mounting clearances. Resolution Outside dimensions are 12" wide x 11 1/4" high x 2 5/8" deep. See the figure below, from the MNB-1000 Installation Instructions, F-27347-3. (Figure 3, p.3.)   Click here for a link to F-27347.
View full article
Picard Product_Support
‎2018-09-10 01:54 AM

Labels:
  • TAC IA Series
1975 Views

NXT will not communicate using RS-485 port 3

Issue NXT will not communicate using RS-485 port 3 Environment R2/AX Niagara Cause Incorrect documentation of communication port number and RS-485 wiring diagram Resolution New document is available with correct comport number 4 and RS-485 wiring diagram.  To download a copy click on link T-NXT-MtgWiring Guide
View full article
Picard Product_Support
‎2018-09-06 01:24 PM

Labels:
  • TAC IA Series
2982 Views

A Network 8000 GCM / LCM displays the error "Insufficient System RAM" and can no longer be accessed via the front panel display or via the serial ports with XPSI softwa...

Issue A GCM / LCM stops working and displays the error message "Insufficient System RAM".  It no longer responds to information requests via the front panel keyboard/display nor via XPSI software connected on either of the available serial ports. A power cycle restores functionality but only for a limited amount of time (ie: hours or days). Environment Network 8000 GCM-84000 series GCM-86000 series LCM-84000 series LCM-85000 series LCM-88000 series Cause Free system ram drops below minimum requirements: Any GCM with sys ram below 18k Any LCM with sys ram below 10k Resolution The amount of free system ram must be kept above minimum requirements. Use Tech Bulletin 95-33 for troubleshooting the GCM / LCM.  It is a comprehensive guide providing both hardware and software suggestions that will increase free system ram.
View full article
Picard Product_Support
‎2018-09-10 01:29 AM

Labels:
  • TAC IA Series
1663 Views

"Flash clear" procedure for GCM Ethernet NIMs (GCM-ETH-001) with firmware prior to revision 11.2P.

Issue Significant changes and improvements were introduced with firmware revision 11.2P, including a streamlined "Flash clear" procedure. For Ethernet NIMs with firmware revisions prior to 11.2P, the procedure was documented in Technical Bulletin 99-56 (see below). The procedure in bulletin 99-56 was a revision of the procedure in the original NIM Networking and Configuration Practices manual, F-25955, which is no longer available. The current version of the manual, F-25955-4, applies only to NIMs with firmware  revisions 11.2P and 11.2T. Environment Ethernet NIM for network 8000; GCM-ETH-001 with firmware revision prior to 11.2P. Cause "Flash clear" procedure was changed in firmware revision 11.2P Resolution Follow the "Flash clear" procedure per Technical Bulletin 99-56.
View full article
Picard Product_Support
‎2018-09-10 12:55 AM

Labels:
  • TAC IA Series
1440 Views

How do you archive the BACnet device backup data that was saved with the WorkPlace Commissioning Tool?

Issue Customer wants to archive the BACnet controller backup images created through the Backup function of the WorkPlace Commissioning Tool. Environment WorkPlace Tech Tool software version 5.7.x or newer Windows XP Professional or Windows 7 Professional Cause The actual location of the Backup folder has changed between Windows XP and Windows 7 Resolution If the computer operating system is Windows XP, the specified backup project folder is in the following location: c:\Documents and Settings\All Users\Application Data\WorkPlace Tech\Backups If the computer operating system is Windows 7, the specified backup project folder is in the following location: c:\ProgramData\WorkPlace Tech\Backups Further information on the contents of the backup project folder can be found in the Release Notes documentation for WorkPlace Tech Tool 5.7.2, F-27526-2, pages 10-13.  Please note that the full file path shown in this document is based on the use of the Windows XP operating system.
View full article
Picard Product_Support
‎2018-09-10 12:45 AM

Labels:
  • TAC IA Series
1396 Views

Schneider Electric Building Automation Systems and FDA Compliance

Issue The FDA requires Building Automation systems to meet their standards which are outlined in Chapter 21 CFR and FDA Part 11. Environment Vista I/NET Andover Continuum TAC I/A-series Satchwell Sigma Cause Finding documentation on Schneider Electric Building Automation Systems which comply to The Food and Drug Administration rules. Resolution Vista 21CFRPart11 support in TAC Vista 5.pdf FL-VISTA-REGIND-A4 mod RO.pdf I/NET - currently unavailable Andover Continuum With the addition of the 21 CFR Part 11 compliance pack, Continuum can meets these requirements. Satchwell Sigma SoftwareOverview.pdf Advanced Security Module.pdf Note: Validation to 21CFR Part 11 can only be performed on whole operational systems and as such, a sub-system comprising the Satchwell Sigma building management system cannot be validated in it own right. Satchwell Sigma would normally be validated as part of a whole operational system. TAC I/A Series - currently unavailable
View full article
Picard Product_Support
‎2018-09-10 12:30 AM

Labels:
  • Andover Continuum
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC INET
  • TAC Vista
4716 Views

New UNC-410 will not save a changed IP address.

Issue The IP address can be entered into a UNC-410 using the Admin Tool but after rebooting or power cycling the device, the IP address is reset back to the factory default. Environment I/A Series (Niagara) R2 UNC-410-2(-N) with serial number greater than 36218 Cause The newer UNC hardware manages stored OS configuration data in a different manner than the older UNC-410 devices.  Because of this change, the factory default operating system has the capability to read, but not permanently change the device IP address. Resolution You must use the Admin Tool Installation Wizard to install the r2.301.527 (or newer) version of the OS and NRE (system software) before you can save any new Ethernet address information to the UNC. Follow the procedure in the UNC-410 installation manual (F-27391) section "Upgrade, License and Configure the Host" to install the OS and NRE system software and to configure the required software modules.  Click here to see the referenced page of the manual.
View full article
Picard Product_Support
‎2018-09-06 01:34 PM

Labels:
  • TAC IA Series
1238 Views

Is there a wiring diagram available for the HOA BACnet Series Digital Output Override Cards for IA BACnet Controllers?

Issue Is there a wiring diagram available for the HOA BACnet Series Digital Output Override Cards for IA BACnet Controllers? Environment IA, MNB-300, MNB-1000, MNB-1000-15, BCS-HOA-3-BACNET, BCS-HOA-4-BACNET Cause Is there a wiring diagram available for the HOA BACnet Series Digital Output Override Cards for IA BACnet Controllers? Resolution A wiring diagram on the HOA card can be viewed in the attached document.
View full article
Picard Product_Support
‎2018-09-06 01:39 PM

Labels:
  • TAC IA Series
1871 Views

A Niagara R2 UNC-510 will not perform a "save runtime db" command.

Issue Attempting to make programming changes to a Niagara R2 UNC-510 station.  After the changes are done, performing a backup fails.  The "save runtime db" does not complete. Environment Niagara R2 UNC-500, UNC-510 Cause The backup process (save runtime db command) requires free memory on the smart media card.  There must be enough free memory to (at least) equal the size of the .sns file. The smart media card (listed as '/sm' on the Summary tab of the Admin Tool) holds the station database (.sns file), graphic images, and other files accessible using the Remote Library. The table below summarizes flash drive volumes and usages by model.  Note that a jace in the table is a UNC. Refer to the Niagara Capacities Engineering Notes for more information. Resolution Access the Remote Library via Workplace Pro and delete unnecessary files.  As files are removed, monitor the Free File Space on the Summary tab in Admin Tool.  When the '/sm' increases a few kilobytes, try performing a 'save runtime db'.  If the command is successful, then the free file space created is adequate.  If it does not, repeat steps 2 and 3 until it is.
View full article
Picard Product_Support
‎2018-09-10 12:15 AM

Labels:
  • TAC IA Series
1885 Views

A MicroZone II (MZ2) indicates "cold reset" or "warm reset". What do these diagnostic messages mean?

Issue A MicroZone II (MZ2) indicates "cold reset" or "warm reset". What do these error messages mean? Environment MicroZone II (MZ2) controller Cause The error messages are in response to interruptions to the controller's  24 Vac power. Resolution For a detailed explanation of the "cold reset" and "warm reset" messages, see the MicroZone II Programmer's Manual, F-23118, "System Resets". Click here  to see an excerpt from the manual.
View full article
Picard Product_Support
‎2018-09-10 12:14 AM

Labels:
  • TAC IA Series
1623 Views

Cannot find the ProView display from Distech in a Niagara R2 station

Issue In a new installation, the ProView display (never configured previously) is powered and wired to the LON trunk back to a UNC-520.  In the station's LonWorks Service, a Find completes but the ProView display does not appear. Environment Niagara R2 version 529 or newer ProView Cause "New" ProView displays are somewhat unpredictable when added to a Niagara R2 station for the first time. Once it has been commissioned and programmed, its behavior improves. Resolution Add the appropriate shadow object from the 'distech' jar file (Ecdis210) to a container under the lonTrunk. The programID for the ProView display is:  90:0:83:32:b:84:4:15 In the LonWorks Service - Lon Device Manager, highlight the just-added Ecdis210 object and Commission. Use the SrvPin method to learn the neuronID (ProView display's service pin is located on the bottom to the left). Once the commission process complete, ProView is now available for programming.
View full article
Picard Product_Support
‎2018-09-10 12:09 AM

Labels:
  • TAC IA Series
1147 Views

How to configure a Niagara R2 UNC as a LON Node

Issue How to configure a Niagara R2 UNC as a LON Node  Environment Niagara R2 Cause How to configure a Niagara R2 UNC as a LON Node  Resolution Steps to configure UNC as LON Node
View full article
Picard Product_Support
‎2018-09-10 12:10 AM

Labels:
  • TAC IA Series
1106 Views

Niagara G3 (NiagaraAx) Open NiCS (Niagara Compatibility Statement)

Issue Niagara G3 (NiagaraAx) Open NiCS (Niagara Compatibility Statement) Environment Niagara G3 (NiagaraAx) Cause NiCS attributes: Niagara G3 (NiagaraAx) licenses has brandId="TAC". A station's ability to accept NiagaraAx data from another NiagaraAx station depends on the accept.station.in="*" field in its license. A station's ability to share NiagaraAx data with another NiagaraAx station depend on the accept.station.out="*" field in its license. A station's ability to allow a copy of WorkBench to connect to it and engineer the station depends on the accept.wb.in="*" field in its license. A copy of WorkBench's ability to connect to a NiagaraAx station to engineer it depends on the accept.wb.out="*" field in its license. (Where "*" is the brandId) 'Open' licenses may be required when there is a need to: Allow sharing of a station's NiagaraAx data to another station which has a different brandId in its license. Accept NiagaraAx data from another station which has a different brandId in its license. Allow a WorkBench connection from a copy of WorkBench that has a different brandId in its license. Allow a copy of WorkBench to connect to a station which has a different brandId in its license. Resolution Niagara G3 open NiCS licenses have the following: “accept.station.in="*”; “accept.station.out="*”and “accept.wb.in="*”and “accept.wb.out="*”. The "*" is a wildcard designation to allow all brandIds. You can specify new licenses to have open NiCS by selecting the 'Request open NiCS (Niagara Compatibility Statement)' checkbox in the I/A Series G3 license request forms. You will need to purchase the part IA-LIC-CHG for each existing Niagara G3 that needs to have an open NiCS. 
View full article
Picard Product_Support
‎2018-09-10 02:49 AM

Labels:
  • TAC IA Series
2431 Views

How many controllers can be connected to an ASD bus before a repeater is required?

Issue How many controllers can be connected to an ASD bus before a repeater is required? Environment Global controller with an ASD bus connected (GCM, UNC, ENC, LNC-100, SIM-CCN, SIM-MTECH, SIM-TRANE, SIM-YORK) ASD controller (LIM-1,MicroFlo II, MicroZone II, MN-ASDI integrator, PEM-1) Cause Requirements for ASD bus installation. Resolution A maximum of 32 nodes are allowed for each ASD bus segment.  Each controller and repeater count as one node, so a bus segment with a master (GCM, UNC, etc.) and a repeater can have 30 other nodes on it ( MZII, MN-ASDI, etc.) For details, See the Network 8000 Hardware Installation Practices manual, F-23061-1, "Network & Communication Wiring", "Repeaters - RS-485".
View full article
Picard Product_Support
‎2018-09-10 02:48 AM

Labels:
  • TAC IA Series
1324 Views

How to set an LNC-100 back to factory-default settings.

Issue How to set an LNC-100 back to factory-default settings. This will erase all block programming and device configuration. Environment Network 8000 LNC-100 and related controllers based on the GCM-861X0 series platform, including the GCM-86110, GCM-86120, SIM-CCN, SIM-MTECH, SIM-TRANE, and SIM-YORK Cause Sometimes it is necessary to manually clear the controller EEPROM in order to reload a database. Resolution Follow the steps below: Backup the controller database. Clear the controller's EEPROM. This is accomplished by pushing the reset button and the EE CLR button and holding both for at least 20 seconds before releasing. The reset process is complete when the top two red LEDs on the right edge of the controller begin blinking in their normal sequence (second LED blinks twice as fast as top LED). This process will clear the user programmable memory (including all block programming), returning the controller to its original factory condition. This step is important as it insures there will be no conflict between the new revisions firmware and the older version. The procedure above is excerpted from Technical Bulletin 99-27 , steps 1 and 2.
View full article
Picard Product_Support
‎2018-09-09 10:51 PM

Labels:
  • TAC IA Series
1872 Views

Can a computer installed with Workplace Tech 5.7.7 be re-installed with 5.7.6?

Issue What issues, if any, are there to replacing Workplace Tech 5.7.7 with 5.7.6 on a Windows XP computer? Environment Workplace Tech 5.7.7 and 5.7.6 Cause none Resolution Workplace Tech version 5.7.7 comes with new firmware for the MNB-1000.  It is better to use version 5.7.7 with any MNB-1000 controllers installed with the new firmware.  This is especially true on job sites adhering to GSA guidelines. If the computer is only used with MNB-1000 controllers running previous firmware releases, then re-installing version 5.7.6 won't create any issues. Review the release notes below for more details. Release Notes - WorkPlace Tech 5.7.7
View full article
Picard Product_Support
‎2018-09-10 01:26 AM

Labels:
  • TAC IA Series
1285 Views

Error when running WorkPlace Tech 4.0 for the first time, "Microsoft Visual C++ Runtime Library, Runtime Error!"

Issue When trying to run Workplace Tech 4.0 for the first time, it may not start successfully, and an error message will be displayed: "Microsoft Visual C++ Runtime Library, Runtime Error!" Environment Workplace Tech version 4.0 Visio 2002, SR1 Windows XP Professional, Service Packs 1-3 Windows 2000 Professional, Service Pack 4 Cause The error is typically caused by not initializing Visio 2002 before running WPT 4.0 for the first time. Resolution See Technical Bulletin TB04-02, which details the issue and resolution.
View full article
Picard Product_Support
‎2018-09-10 01:22 AM

Labels:
  • TAC IA Series
1357 Views

When using a USB to RS-232 adapter and an MN-CIM, cannot connect to MicroNet 2000 controllers. Receive an ERROR = -510.

Issue When using a USB to RS-232 adapter and an MN-CIM, cannot connect to MicroNet 2000 controllers. Receive an ERROR = -510. The problem has also been seen on laptops with an integral serial port. Environment Laptop computer running the MN-CI or MN-FLO-BAL software tools,  any version MN-CIM Controller interface Module Cause One cause of ERROR = -510 is that the serial port or USB to RS-232 adapter does not supply enough power to the "port-powered" MN-CIM. When the CI software is running, but not communicating on the U-LINK, it requires only 12 mA at 5 VDC. To communicate on the U-LINK, the MN-CIM requires 14 mA at 5 VDC from the DTR control line of the port.  Some computers have a mechanism to sense the increased current draw and shut down the DTR line. This loss of power causes the MN-CIM to reset, and after 3 attempts to communicate the MN-CI software issues the ERROR= -510 message. Resolution See Technical Bulletin 01-104 for information  on the Patton Electronics power supply adapter, model 3PMF9-BC.
View full article
Picard Product_Support
‎2018-09-06 01:46 PM

Labels:
  • TAC IA Series
2172 Views
  • « Previous
    • 1
    • …
    • 18
    • 19
    • 20
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of