Issue
When wiring a TS-58011-774 Platinum RTD sensor to a DMS Microsmart MSC-MPC controller, what are the acceptable offset values for accurate temperature readings? Can the wire length exceed 200 feet?
Product Line
TAC IA SeriesEnvironment
- DMS Microsmart controllers
- TS-58011-774 Platinum RTD sensor
Cause
A significant offset (approximately 6°F) was required to match readings with a handheld calibration device, raising concerns about wiring length and sensor accuracy.
Resolution
- Offset Values: There is no fixed maximum or minimum offset value. Proper wiring minimizes the need for large offsets.
- Wire Length: Do not exceed 200 feet.
- Recommended Cable: Belden #9501 (AWG24).
- Calibration Steps:
- Review the sensor installation guide (F-24874) for Software Setup (page 3).
- Use the temperature/resistance table (page 5) to verify sensor accuracy.
- Apply appropriate offset values to correct wire-induced error.
- If necessary, use SOCALC (page 4) to create custom SCALE and OFSET values.
Reference: TS-58000 Series Platinum RTD Room Sensor Installation Guidelines (F-24874)