Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,837
  • TAC IA Series 1,820
  • TAC INET 1,458
  • Field Devices 720
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 11
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 486
    • 487
    • 488
    • …
    • 507
  • Next »

"Invoke or BeginInvoke cannot be called on a control until the window handle has been created" Error when Installing SQL 2008

Issue When installing SQL server 2008 or SQL 2008 R2 to manually an instance for I/NET, Vista or Continuum, sometimes an error "Invoke or BeginInvoke cannot be called on a control until the window handle has been created" will show up. Environment SQL 2008 / SQL 2008 R2 Vista I/NET Continuum SmartStruxure Cause This issue is happening because of a behavior change in .NET that is exposing an issue with SQL Setup User Interface (UI). Resolution Generally, if you just rerun the installer, it won't hit the issue again. If this can't help, just manually create a C:\temp folder and it will work fine.
View full article
Picard Product_Support
‎2018-09-06 09:36 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC INET
  • TAC Vista
2104 Views

Function Block applications made in TAC Menta may not import into StruxureWare Building Operation

Issue When importing a file from TAC Menta into StruxureWare Building Operation Functional Block Editor, the import of the application file fails. Environment TAC Vista TAC Xenta StruxureWare Building Operation Cause The following characters are not allowed in object names in StruxureWare Building Operation. • / • " • ? • * • ~ • White space is not allowed in the beginning or the end of an objects name. • . (period) is not allowed in the beginning of an objects name. Colon (:) is not allowed either, but will automatically be replace by an underscore (_) when importing   In TAC Vista, signal names could contain the character "/". In SmartStruxure, this character is not allowed. Resolution Remove illegal characters from object names in the Function Block program.
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1694 Views

Access denied error creating ContinuumDB

Issue Access denied error creating ContinuumDB Environment Cyberstation SQL Server Cause Firewall blocking Resolution Ensure the firewall at both the WS and the SQL Server are not blocking the DB creation process. Turn off all aspects of McAfee or Norton Anti-Virus. In particular, McAfee On-Access Virus Scanning can cause this
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • Andover Continuum
1232 Views

Losing VAS client connection; getting error: java.lang.outofmemoryerror: unable to create a new native thread.

Issue Losing VAS client connection; getting error: java.lang.outofmemoryerror: unable to create a new native thread. Environment R2 VAS 2.50 Cause Users at the client were not signing off but rather switching users causing multiple connections to VAS from the same pc.  Resolution Ensure user is logging off, not just switching users.
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • TAC IA Series
921 Views

Is RS-485 node activation required on a 57xx series acx to connect the SCH-PIM400-485

Issue Normally using RS-485 on an ACX 57xx requires nodes to be activated to work so ordering and price could be affected by this Environment ACX57xx Schlage PIM 400-485 Cause The Schlage PIM RS-485 unit uses RS485 for communication and it's important to know if node activation is required for the Schlage solution to work Resolution The Schlage PIM RS-485 does use RS-485 for communication, but it doesn't require node activation on the comm port. The Schlage solution uses an XDriver instead in order to communicate RS-485 to the PIM
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • Andover Continuum
1158 Views

Is it possible to use the analog output on the TAC Xenta 121-FC even if I want to have the Occupancy mode indicator on a STR150?

Issue When using STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC, which is the only analog output on the TAC Xenta 121-FC device. Environment TAC Xenta 121-FC STR150 Cause When using a STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC device, which is the only analog output on the TAC Xenta 121-FC device. Resolution In ZBuilder, it is possible to move the Occupancy Mode indication from the default location at Y1 to K1-4. In this case you also need to have an external power supply with 5 Volt DC for the Occupancy Mode indicator.
View full article
Picard Product_Support
‎2018-09-06 09:35 AM

Labels:
  • TAC Vista
1250 Views

Can a G3 / AX Jace do fox tunneling?

Issue Customer has a Jace-7 installed with two NICs.  It's installed with 3.7.106. NIC 1 (192.168.1.101) is communicating with 3 other jaces on-site with IP addresses of 192.168.1.102, 103, & 104. NIC 2  (public address) is accessed remotely with Workbench. Is there a way to access the stations (remotely) running on 192.168.1.102, 103 & 104 with fox tunneling? Environment Niagara G3 / AX Cause There is no Enterprise Server on site, just the four Jaces. Resolution Jaces cannot act as Proxy Servers so fox tunneling is not supported on anything except a server.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • TAC IA Series
1415 Views

Actuator feedback is connected to a MNL controller and displays a negative '%open" position.

Issue A customer installed a critical valve with an actuator containing a potentiometer for a positional feedback connection. The potentiometer was wired into a MNL controller's input. After some calibrating, the potentiometer drives past the "0 %open" position which displays as a negative value in the AI point. Is there a way to compensate in software for this negative reading? Environment WorkPlace Tech MNL and MNB controllers Cause It can be difficult to calibrate the feedback potentiometer accurately. Resolution Add a high selector block to the output of the AI block.  Connect the AI block's output and a constant set to a value of zero. Anytime the AI block's output drops below zero, the output of the high selector will display zero.  This can then be used for other logic or for graphical display.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • TAC IA Series
1135 Views

Can the manual override switches on the I/O modules still be used if the device is broken?

Issue We want to be able to control the outputs on an I/O even if the I/O module is broken. Environment StruxureWare Building Operation I/O Modules   Cause The switches for manual override on the I/O modules needs power to be able to operate. Resolution The switches on the I/O modules that are used for manual override internally controls relays, that need to be powered to be able to operate.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • EcoStruxure Building Operation
843 Views

Editing the Continuum security group export file outside of Continuum.

Issue Is there a way to edit the Continuum Security Group export file outside of Continuum? Environment Security Groups .sdf file format Cause The need for a more efficient method of editing Continuum user Security Groups. Resolution There is no method of editing the Security Groups export file outside of Continuum.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • Andover Continuum
931 Views

SBO user accounts not working as configured.

Issue Graphics are not displaying values under certain user accounts Environment User Accounts Domains Cause Although the user account configuration appeared to be correct, something in the user accounts was broken. Resolution Once the User Accounts were deleted and recreated with exactly the same configuration the graphics began displaying the values. 
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • EcoStruxure Building Operation
1056 Views

Continuum controller grounding requirements.

Issue The electrical contractor failed to pull an ground conductor with the controller power conductors.   Environment Controller installation. Controller Power. Cause Electrical contractor neglected to include a ground conductor when running power to the controller panel. Resolution All installation for the entire Continuum and Infinity controller product lines indicate that the controller power terminal must have a true earth ground connected to the ground terminal. Continuum controllers require a true earth ground connected to the ground terminal of the controller power strip.  Controller grounding is essential and impacts the controller in several ways including sensor bus communication, input accuracy, processor function and output performance. Improper grounding can also, in some cases, cause damage to the controllers.   The problem with grounding to the electrical enclosure or to the building structure is that each grounding point can have different  a ground potentials. This will especially cause issues with bus communication since all controller signals must be established with respect to the same ground reference. If each controller has a different ground reference the wave forms will be inconsistent.  
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • Andover Continuum
1114 Views

Is it possible to access the value of a doors ADA output for programming or reporting via graphics, listviews or reports?

Issue Is there a way to display the value of a doors ADA output or to use this value in a Plain English program? Environment ADA output Door attributes Cause Need to display and track the value of a doors ADA output. Resolution There is no sanctioned way to access or use the value of a doors ADA output.  While in some cases it may be possible to create a separate output object with the same channel number to track this value, this kind of configuration is known to have issues and it is not recommended.
View full article
Picard Product_Support
‎2018-09-06 09:34 AM

Labels:
  • Andover Continuum
986 Views

License Setup changes without user interaction and reverts to previous configuration

Issue The configuration in "License Setup" changes autonomously meaning that you open "License Setup", make a change, close "License Setup", open "License Setup" and the configuration has reverted to what is was before the change was made. It reverts back to what it was before making the change. Environment TAC Vista 5.1.9 Cause The cause of this is unknown. TAC Vista Server is supposed to set some values in the registry while running also regarding licensing, but not like described here. Resolution Make sure TAC Vista Server is stopped while changing the license setup: Stop TAC Vista Server Change the license setup Start TAC Vista Server
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • TAC Vista
1059 Views

Windows reports that RAM services do not start or stop in a timely manner

Issue Windows reports that RAM services do not start or stop in a timely manner Environment RAM 2.1.025 Cause Windows reports that RAM services do not start or stop in a timely manner. Re-installing RAM does not resolve the issue Resolution The issue may be with the RAM configuration file (setup.mdb). Note: If possible, record the RAM setup by opening the RAM console. Uninstall RAM and locate and delete or save the Remote Alarm Manager folder to a different location. Reinstall RAM. RAM will need to be re-configured with the site setup.
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • Satchwell BAS & Sigma
  • TAC Vista
1004 Views

Can the LON card for MULTICAL 601/602 be mounted on an older MULTICAL 66 type?

Issue On a MULTICAL 66, the Lon card is broken and needs to be replaced. Does the MALON BASE card fit the older heat meters? Environment MELON BASE MULTICAL Cause Unfortunately the LON card we have today for the newer MULTICAL 601/602 will not function with the old MULTICAL 66 meter types. Resolution Please contact local Kamstrup Service channel.
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • Field Devices
1027 Views

I/A Series G3 Enterprise Network Server output window displays the following error: java.io.IOException: Negative seek offset.

Issue I/A Series G3 Enterprise Network Server output window displays the following error: java.io.IOException: Negative seek offset. java.io.IOException: Negative seek offset at java.io.RandomAccessFile.seek(Native Method) at com.tridium.history.io.FileRandomAccess.seek(FileRandomAccess.java:118) at com.tridium.history.file.recstore.RecordStore.writePage(RecordStore.java:561) at com.tridium.history.file.recstore.RecordStore.newLastPage(RecordStore.java:631) at com.tridium.history.file.recstore.RecordStore.getWritePage(RecordStore.java:606) at com.tridium.history.file.recstore.RecordStore.append(RecordStore.java:222) at com.tridium.history.file.recstore.BRecordStoreHistoryTable.doAppend(BRecordStoreHistoryTable.java:175) at com.tridium.history.file.BFileHistoryTable.append(BFileHistoryTable.java:803) at com.tridium.history.db.TableHandle.append(TableHandle.java:203) at com.tridium.history.db.BLocalDbHistory.append(BLocalDbHistory.java:393) at com.tridium.driver.file.history.BDelimitedFileImport.appendToHistory(BDelimitedFileImport.java:796) at com.tridium.driver.file.history.BCsvFileImport.executeFileImport(BCsvFileImport.java:212) at javax.baja.driver.file.history.BFileHistoryImport.doExecute(BFileHistoryImport.java:90) at auto.com_tridium_driver_file_history_BExcelCsvFileImport.invoke(AutoGenerated) at com.tridium.sys.schema.ComponentSlotMap.invoke(ComponentSlotMap.java:1217) at com.tridium.sys.engine.EngineUtil.doInvoke(EngineUtil.java:49) at javax.baja.sys.BComponent.doInvoke(BComponent.java:1046) at javax.baja.util.Invocation.run(Invocation.java:46) at javax.baja.util.Worker.process(Worker.java:161) at javax.baja.util.Worker$Processor.run(Worker.java:134) at java.lang.Thread.run(Thread.java:619) Environment I/A Series G3 Enterprise Network Server (versions prior to 3.4.54) Cause The error indicates that a history has become too large where the source .hdb file has exceeded 2GB making the history become inaccessible.  Versions prior to 3.4.54 used a Java integer as the offset into the page file of a history and the negative seek offset error is caused by a math rollover calculating a negative number. Resolution Two options to correct: Review the current size of the audit histories, log histories and any string logs to see which one is at the 2GB limit and perform some history database maintenance to trim the size down. Upgrade to the latest maintenance build of I/A Series G3 (3.4.54 or higher) where Java long calculations are used for the offset.
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • TAC IA Series
1340 Views

When attempting to fax a WorkPlace Tech license request, the fax number is reported as no longer in service.

Issue The paper version of the WorkPlace Tech Tool license request form includes the 815-637-5331 fax number.  This number has been disconnected and is no longer in service. The Schneider Electric Park Plant Customer Care Center has been relocated and the 815-637-xxxx series phone numbers have been disconnected. Environment WorkPlace Tech License Request Fax and email information Cause Incoming faxes to the Schneider Electric Buildings Customer Care Center are now handled electronically. Resolution Use of email is the preferred method for submitting a WorkPlace Tech Tool license request form although a fax number is still available. The preferred email address is IASeries.License@schneider-electric.com If it is necessary to fax the license request please use +1 888-560-3636.
View full article
Picard Product_Support
‎2018-09-11 02:50 PM

Labels:
  • TAC IA Series
1091 Views

Sigma - When backing up User Names and Passwords, what files / folders need to be copied?

Issue When backing up user names and passwords, what files / folders need to be copied? Environment User Names Passwords Cause Replacing the Sigma server PC and upgrading at the same time, what files should be copied? Resolution The Passwords / User names are stored in two locations in the Sigma/Data folder.   The following files / folders should be copied; All files located in the User folder. GenCNF.rec
View full article
Picard Product_Support
‎2018-09-06 09:33 AM

Labels:
  • Satchwell BAS & Sigma
1095 Views

Schedule not work properly, especially the holiday events

Issue The customer reported the schedule not work properly randomly, especially the holiday events not executing correctly. One item of error log 1465 was logged every 10 minutes. Environment CX9900/9940 i2 controller with version 3.2x Cause Some controllers with special version contribute to error log 1465 significantly, possibly impacting on the schedule event downloading Some i2 controllers with lower version firmware cause the schedule not to work correctly. Resolution Upgrade the CX controller to the latest version firmware. Upgrade all the i2 field controller to the late version firmware 3.300008
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Labels:
  • Andover Continuum
1089 Views
  • « Previous
    • 1
    • …
    • 486
    • 487
    • 488
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of