Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 486
    • 487
    • 488
    • …
    • 501
  • Next »

Wake-Up Interval and Redundant Transmission settings on the SED-THSU5045 thermostat.

Issue How do the Wake Up Time and Redundant Transmission settings affect the operation of the SED-THSU5045 thermostat? Environment SED-THSU5045 Enocean Cause The function of the Wake-Up interval and the Redundant Transmission switches is not described in the documentation that comes with the sensor.   Resolution DIP Switch 1 and 2 control the Wake-up Interval (in seconds) OFF OFF No cycling wake up ON OFF 1 OFF ON 10 ON ON 100 DIP Switch 2 and 3 control the Redundant Transmissions (in frequency of tx) OFF OFF Every wake up ON OFF 7 to 14 wake ups OFF ON 70 to 140 wake ups ON ON Never   The idea is that the stat will wake up when the wake-up interval is elapsed and verify if the temperature has changed by more than approximately 1°F. If it did, it will send a transmission, if not it will go back to sleep until the next interval. The second setting (redundant transmission) will govern how often the stat will send a value, even if the temperature has not changed (as some kind of ping or keepalive).
View full article
Picard Product_Support
‎2018-09-06 09:27 AM

Labels:
  • EcoStruxure Building Expert
1068 Views

Integrated NPR Dial on a Xenta 527 (Web) failed to connect

Issue Integrated NPR Dial on a Xenta 527 (Web) failed to connect Environment I/Net Site with Integrated NPR Dial Cause There is a current issue with Xenta 527 (Web) and the Firmware load of 5.1.9-15 at the present time. This release will not support the Modem connection. This issue has been given to Engineering for Repair. Resolution The "Work Around" is to go back a Firmware release. For the time being, until the 5.1.9-15 is fixed, load 5.1.8-10 in the Xenta 527 (Web) and the Modem will work in this load.
View full article
Picard Product_Support
‎2018-09-06 09:27 AM

Labels:
  • TAC INET
1576 Views

Smart Sensor will not display room temperature using a simple program on B3 controllers

Issue Configuring a Smart Sensor in a B3 controller in StruxureWare Building Operation using a simple script program to display temperature. The temperature does not display in the Smart Sensor LCD. Environment Automation Server with B3 controllers Cause SmartStruxure 1.4 attaches a _AV, _BI, etc. to the BACnet name Resolution Remove the _AV, _BI, etc. from the LCDDisplay BACnet name Download the controller again The display functions as suggested
View full article
Picard Product_Support
‎2018-09-06 09:27 AM

Labels:
  • EcoStruxure Building Operation
1382 Views

Moving Xenta devices in a Lonworks network and their Xenta group relationship

Issue When you drag and drop and Xenta programmable controller in to a new folder it remains in the existing Xenta group. Environment SmartStruxure 1.5 Cause The drag and drop feature is not designed to make new Xenta Group bindings. The controller will be moved but remain in the existing Xenta Group membership. Resolution Two options exist to move a controller into a different Xenta Group  Make a new Xenta Group, save the existing Menta application out of the database and then delete the device.  Add a new folder then add the Xenta device into that folder and select the previously saved Menta file.  A new Xenta Group will now be created .  Select the controller you wish to move, using right mouse click, select Copy. In the new location use the right mouse click Paste Special command.  When finished delete the original controller.
View full article
Picard Product_Support
‎2018-09-06 09:27 AM

Labels:
  • EcoStruxure Building Operation
1087 Views

What sensor element is used in STR300?

Issue What type of sensor element is used in the STR300? Environment STR300 Cause The HVAC European+Sensors+Catalogue.pdf on the Extranet, as well as the datasheet for the STR300 Series says that the sensor element is PT100 Class B. Resolution The actual sensor element for the STR300 that are made today is NTC Thermistor 10 kOhm. The output from the STR300 is 4-20 mA.   The documentation will be updated shortly.
View full article
Picard Product_Support
‎2018-09-06 09:27 AM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
  • TAC Vista
1487 Views

How to move a PCS project from one PCS server to another one.

Issue I have created a project in the Project Configuration Server (PCS) on my computer. Now I would like to move this to the customers computer how do I do that?  Environment StruxureWare Building Operation 1.5 and later versions. Cause You move a project database from an off-site computer to a customer site computer, when a project cannot be deployed from an off-site computer. Resolution On the source computer, in WorkStation for Projects, ensure that the project is backed up. For more information, see Checking the Backup Status of a Server . Close WorkStation for Projects. Wait 5 minutes to ensure that the project is closed. A project closes 5 minutes after the last user has logged off.    When multiple users are working with the Project Configuration Server, make sure a stop of the Project Configuration Server Windows service does not negatively affect your projects before closing.   In Software Administrator, in the Project Configuration Server tab, copy the path of the Projects folder. In Windows Explorer, in the Address box, paste the path of the Projects folder. Move the individual project folder to a USB drive or to another appropriate media. On the target computer, in Software Administrator, in the Project Configuration Server tab, copy the path of the Projects folder. In Windows Explorer, in the Address box, paste the path of the Projects folder. Move the individual project folder from the USB drive to the Projects folder. The project can now be opened in WorkStation for Projects on the target computer Make sure that the versions on both PCS servers is the same.
View full article
Picard Product_Support
‎2018-09-11 07:48 AM

Labels:
  • EcoStruxure Building Operation
1723 Views

Does the MNB-1000-15 Remote I/O Module supports pulse inputs?

Issue Does the MNB-1000-15 Remote I/O Module supports pulse inputs? Environment I/A Series MNB-1000-15 Remote I/O Module Cause How to use the MNB-1000-15 remote I/O module universal inputs to read pulse inputs. Resolution Standard pulse input is supported on the MNB-1000-15 universal inputs (UI1 to UI6).  Minimum Rate 1 pulse per 4 minutes   Maximum Rate 1 pulse per second Minimum Rate 1 pulse per 4 minutes. Maximum Rate 1 pulse per second.
View full article
Picard Product_Support
‎2018-09-06 09:26 AM

Labels:
  • TAC IA Series
1369 Views

b3885-V will not allow the restart mode to be set to warm start

Issue Manually selecting warm start on the restart variable or using a program to try to set it will not work Environment B3 SmartStruxure Continuum Cause Attempting to set the restart or accrestart system variable to work start will not work and may generate errors Resolution The b3885-V does not have an onboard battery, so the warm start option isn't available. Cool start or Cold start are the only options.  Programs that attempt to set warm start will need to be modified to do a cool start and use backup to flash.
View full article
Picard Product_Support
‎2018-09-06 09:26 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1426 Views

Enocean SED-THSU5045 thermostat super capacitor voltage test.

Issue The documentation for the SED-THSU5045 thermostat states that the super capacitor voltage can be measured across terminal strip TB1 terminals 1 and 2.  However, there is no mention of what an acceptable voltage reading would be.  Environment Super capacitor voltage specification is not published on the thermostat documentation. Cause A minimum voltage of 5.5 VDC should be present across TB1 terminals 1 & 2. Resolution If a 5.5 Volts DC charge cannot be maintained on the super capacitor, the device may require either an auxiliary light collector or external 24 VAC.  The Thermistat battery is not designed to run the thermostat for extended periods.
View full article
Picard Product_Support
‎2018-09-06 09:25 AM

Labels:
  • EcoStruxure Building Expert
1134 Views

Create an alarm when a Modbus point has a specific value

Issue An analog Modbus value has specific values when the system is in error. For example: 0 = No Error 1 = Over Current Acc 2 = Over Current DeAcc 3 = Over Current Constant Speed How could an alarm be defined to trigger when the object has Value = 2? Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation 1.5 Cause When using a Modbus analog value, it is not possible to create an alarm on a specific value. Resolution Instead of a Modbus Analog Value, create a Modbus Multistate Input. With a Modbus Multistate Input, it is possible to connect a multistate alarm which gives the option to create an alarm on a specific value.
View full article
Picard Product_Support
‎2018-09-06 09:25 AM

Labels:
  • EcoStruxure Building Operation
1631 Views

Is it possible to increase the cables to the sensors connected to a Multical device?

Issue According to the documentation the max cable lengths for the sensors connected to a Multical device are : Temperature sensors : 10m Flow Sensor : 2,5m Is it possible under any circumstances to extend the cable length up to 15m?   Environment Multical Cause The sensors come in pairs and are calibrated. They must never be extended. The longest length available is 10 metres. Resolution It is not possible to extend the cables to the sensors, as the devices are calibrated with the sensors delivered from the factory.
View full article
Picard Product_Support
‎2018-09-06 09:25 AM

Labels:
  • Field Devices
920 Views

Continuum controller compliance with the most recent BACnet standard.

Issue Are the BCX4040, BCX4000 and b3 line of controllers compliant with the most recent BACnet specification, ASHREA 135 2012? Environment Continuum Controllers Cause The consultant is requiring that all BACnet controllers be compliant with ASHREA 135 2012. Resolution As of August 27, 2014 the BCX1 and b3 family of controllers do not comply with ASHREA 135-2012. This is noted in the PICS statements as the Protocol Revision. The 2004 version of the spec correspond to Protocol Revisions 4, 5 & 6. The 2012 version is Protocol Revision 14 & 15. As of August 27, 2014 the BCX1 and b3 family of controllers comply with ASHREA 135-2004 spec revision.  
View full article
Picard Product_Support
‎2018-09-06 09:25 AM

Labels:
  • Andover Continuum
1478 Views

Integrating to Zigbee devices not available in Building Expert

Issue Integrating to Zigbee devices not available in Building Expert Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi Purpose Manager SmartStruxure Lite Building Expert Cause The Zigbee device is not available in Building Expert Resolution Zigbee devices are fairly complex to integrate when compared with EnOcean devices and requires development work from the engineers in R&D. Therefore, depending on the business case in your region, it has to be discussed with offer management on whether it could be part of the roadmap or not. You are reach out to the regional product managers to discuss about the opportunity. APAC - EMEA Dusan Janjic (dusan.janjic@schneider-electric.com) Ilda Metani (ilda.metani@schneider-electric.com)  North America Michael Sabinash (michael.sabinash@schneider-electric.com) South America Marcelo Varde (marcelo.varde@schneider-electric.com)   To be able to build a driver for a 3rd party Zigbee device, the following information are required. IEEE Address Endpoint(s) Cluster(s) Attributes Instead of waiting for R&D to build a driver though, you can always write your own script using the information above. However, no active support will be provided by our support teams.
View full article
Picard Product_Support
‎2018-09-11 10:19 AM

Labels:
  • EcoStruxure Building Expert
1872 Views

Replacement for Room humidity sensor SHR100-T with part# 006902350

Issue SHR100-T is obsolete and needs to be replaced Environment SHR100-T Room humidity sensor Cause Replacement of obsolete sensor Resolution The SHR100-T is replaced by SHR110-T with part# 006903115
View full article
Picard Product_Support
‎2018-09-06 09:24 AM

Labels:
  • Field Devices
1497 Views

Do the 902 MHz EnOcean and the 315 MHz EnOcean MPM's just have different antennas?

Issue Cannot learn EnOcean thermostats into the MPM. Environment MPM, EnOcean Cause Purchased the wrong EnOcean frequency MPM. Can the antennas just be changed?  Resolution No, just replacing the antennas will not resolve the problem. The MPM controller and antenna must be replaced to match the frequency of the Enocean thermostats. Note: the 315 MHz EnOcean MPM uses an antenna with green stripes; the 902 MHz EnOcean MPM uses an antenna with yellow stripes. 
View full article
Picard Product_Support
‎2018-09-06 09:24 AM

Labels:
  • EcoStruxure Building Expert
1062 Views

How many relay packs could be connected simultaneously to one SE7300 or SE8300?

Issue How many SC2300 could be connected to one SE7300 or 8300? Environment SC3000 SE7300 SE8300 Cause Inputs from the relay packs could not be connected in parallel. Resolution It is not possible to connect inputs in parallel, therefore you could only connect one relay pack to one device.
View full article
Picard Product_Support
‎2018-09-06 09:24 AM

Labels:
  • EcoStruxure Building Expert
2015 Views

Current line of a PE Script program in b3 displays incorrectly

Issue There is a display issue with PE programs running in a b3 device, depending on program code the current line shown maybe incorrect showing a line that is NOT the line the program is currently at, this issue exists in all versions of SBO. Note that program execution is not effected, the execution of the program iscorrect, it is only the CL shown that maybe incorrect. Issue will be fixed in SBO 1.6 Environment Workstation AS b3 Cause Firmware defect Resolution The defect has been corrected and the fix will be released in SBO 1.6 Currently there is not hot fix available for this issue.
View full article
Picard Product_Support
‎2018-09-06 09:24 AM

Labels:
  • EcoStruxure Building Operation
1455 Views

How to bring an MPM-VA online via ZigBee with the MPM Coordinator?

Issue How to bring an MPM-VA online over ZigBee to communicate with the ZigBee Coordinator (which is also the MPM you have your IP interface with). Environment MPM, MPM-VA, ZigBee Cause Cannot figure out how to get the MPM-VA to communicate over ZigBee to the Coordinator. Resolution Use web interface on the bench to set up ZigBee Pro Extended Configuration on the "remote MPM-VA" to match the Coordinator's Channel, PAN ID, Extended Network ID, Stack Profile, Security Profile and Trust Center Link. Save settings and save database to flash. You can now disconnect the IP connection to the remote MPM-VA. Re-discover controllers from the Coordinator MPM. It will appear as a "peer" below the coordinator, i.e., it will not be "under it" like a Room Controller (stat) or TE2.  
View full article
Picard Product_Support
‎2018-09-06 09:23 AM

Labels:
  • EcoStruxure Building Expert
2029 Views

Schneider Universal Plug-In is registered in StruxureWare but we got an error message saying, that no plug in matches the program ID.

Issue The Schneider Universal Plug-In 2.5.1 s registered in StruxureWare and the XIF file for the MTN880601 is imported into the StruxureWare database.. After adding the device and choosing Configure, the Plug-In is not launched. Instead comes an error message saying, that no plug in matches the program ID. Environment StruxureWare OpenLNS Cause XIF files that, during the installation, is not placed in the Import folder, may not be registered correctly in OpenLNS. Resolution In the StruxureWare Control Panel, under "LNS Plug-in Registration", you may have a selection "Import device templates in LNS." Select this to import the XIF file (device template) into OpenLNS database.
View full article
Picard Product_Support
‎2018-09-06 09:23 AM

Labels:
  • EcoStruxure Building Operation
1305 Views

Display true output status of Universal Outputs on a Xenta 102-AX

Issue How to display a binary on/off value for fan the following hardware outputs for a Xenta 102-AX graphic page: Fan command Heat 1 command Heat 2 command Damper open Damper close Environment Xenta 102-AX StruxureWare Building Operation TGML Graphics Cause Universal Outputs 1, 2, and 3 on a Xenta 102-AX are controlled via percent based values. Through hystereses, they will turn on and off. Without knowing the previous status of the output, values between 1% and 99% will be unclear as to the present value of the output. Note: due to this SNVT being of a user-defined type, TAC Vista Workstation is unable to display these values. This solution can only be applied to a SmartStruxure Solution. Resolution Navigate to the Xenta 102-AX object in Building Operation Drill down to Node Object [0] > nvoRawHwValues > Universal Outputs Current Value Use the following signals for a true/false status of each command: Damper Drive Down State Damper Drive Up State Universal Output1 state (fan) Universal Output2 state (heat 1) Universal Output3 state (heat 2)
View full article
Picard Product_Support
‎2018-09-06 09:23 AM

Labels:
  • EcoStruxure Building Operation
1308 Views
  • « Previous
    • 1
    • …
    • 486
    • 487
    • 488
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore