Integrated NPR Dial on a Xenta 527 (Web) failed to connect
  • Integrated NPR Dial on a Xenta 527 (Web) failed to connect
  • Tom_Poovey
    Tom_Poovey
‎2018-09-06 09:27 AM
I/Net Site with Integrated NPR Dial
There is a current issue with Xenta 527 (Web) and the Firmware load of 5.1.9-15 at the present time. This release will not support the Modem connection. This issue has been given to Engineering for Repair.
The "Work Around" is to go back a Firmware release. For the time being, until the 5.1.9-15 is fixed, load 5.1.8-10 in the Xenta 527 (Web) and the Modem will work in this load.
  • TAC INET
Tags (3)
  • 16651
  • Xenta 527 Web