Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2208 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 92
    • 93
    • 94
    • …
    • 111
  • Next »
Label: "Andover Continuum" Show all articles

BACnet error reloading Infinity controller

Issue Error reads....BACnet Device for this Infinity controller is not created, please perform a ‘Find new BACnet devices’. Site does not have any BACnet devices Environment CyberStation CX Infinity controllers Cause Some how Event Notification objects are configured under the infinity controllers in the database Resolution Delete non applicable BACnet only objects that some how got configured under the infinity controllers
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Labels:
  • Andover Continuum
1465 Views

Tablet PCs and webclient screen resolution

Issue Screen resolutions may be distorted on a tablet PC Environment Webclient Tablet PC Windows 7 Cause Screens, graphics displays and drivers on Tablet PCs are very specific hardware for that device and can cause distortion when rendered in Continuum Resolution No QA testing has been done with any Tablet PC so results may vary as to how the screens are displayed on these devices
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Labels:
  • Andover Continuum
1293 Views

Where is a list of all Continuum Keywords held?

Issue What are all of the Key and Reserved works used in Plain English and object naming? Environment Names and Alias used in Plain English programming and object creation. Cause Keyword list required. Resolution Reserved Words are split into different types: Statements (used in Plain English) Functions Operators Local Variables System Variables System Constants A full list of all reserved and keywords are in the Plain English Language Reference, see Chapter 7: Keywords also Appendix B: Reserved Words.
View full article
Picard Product_Support
‎2018-09-06 12:02 PM

Labels:
  • Andover Continuum
1189 Views

Improper object references appearing in Occupancy Point field of Infinity Schedule object in Continuum 1.74.

Issue An Infinity Program object appears In the Occupancy Point field of the schedule editor. When an attempt is made to browse, select apply the proper occupancy numeric, the same Infinity Program object reference reappears. Environment Continuum 1.74 Schedules Occupancy Point Database Cause This behavior was related to the behavior described in TPA-BOST-08-0005.00.  Resolution Apply the Cyber 1.74 SP2 HotFix For TPA-BOST-08-0005.00.
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • Andover Continuum
1083 Views

Are the LCX898 and ACX781 supported in the current (1.94) version of Continuum?

Issue These Infinet controllers either in limited production or no longer manufactured, but are they supported? Environment CyberStation Cause Upgrade from Continuum 1.62 is desired. Are LCX898 and ACX781 still supported? Resolution Yes, they are supported in all CyberStation versions from v1.62 to 1.94 with no chip change required  
View full article
Picard Product_Support
‎2018-09-06 11:03 AM

Labels:
  • Andover Continuum
932 Views

After a power reset, bCX1 comes back online with its comm2 set to a different baud rate than before it went offline, no longer communicating with the connected b3 MSTP controllers.

Issue After a power reset, bCX1 comes back online with its comm2 set to a different baud rate than before it went offline, no longer communicating with the connected b3 MSTP controllers. Environment bCX4000 bCX4040 bCX9640 CX9680 CX9900 Cause Controller comes back from power fail and does not have the correct baudrate set which results in loss of communications to all field controllers. Resolution 4.500076 should correct this issue. If not get the controller error log and see if the controller is cold starting. On those controllers that have come back from power fail and have their comm port set to 9600, you can try setting the defaultbaud attribute of that comm port to the desired speed. For this to be saved to the controllers EEPROM you will need to do this from the command line, see the syntax for this below. (replace baud19200 with your desired baudrate) comm2 defaultbaud = baud19200   Or   Write a PE program to detect the baud condition and change the baud to the desired rate
View full article
Picard Product_Support
‎2018-09-06 11:03 AM

Labels:
  • Andover Continuum
1406 Views

Once working access cards now produce invalid read when presented to card reader.

Issue Once working access cards now produce invalid read when presented to card reader. Environment Card reader Invalid read Cause Reader power supply was no longer supplying power to the reader. Battery backup had been depleted and was not supplying sufficient voltage to the reader.   Resolution Repair or replace card reader power supply.
View full article
Picard Product_Support
‎2018-09-06 11:03 AM

Labels:
  • Andover Continuum
757 Views

What might cause IOU modules to randomly drop off-line and on-line.

Issue IOU modules connected to an NC2 and powered by Continuum PS are randomly dropping off-line and returning on-line. Environment NC2, AC-1, DO4 Cause IOU modules randomly dropping off-line and on-line Resolution In this case the maximum power output of the Continuum PS was exceeded once the card readers powered by the AC-1's were taken into consideration. The problem is exacerbated when cards are presented as the reader power spikes at this time. The 28 AC1-Plus's were grouped together in several panels. The voltage at the end of the line was measured to be under 21VDC. When a second PS was inserted to power the last 18 AC1Plus's, the voltages at the ends of both runs came up to above 22.5VDC and the offline issues stopped. Note: There are other conditions that could cause this behavior like grounding, comm bus that does not meet specs, poor terminations, induced voltages, etc)
View full article
Picard Product_Support
‎2018-09-06 11:03 AM

Labels:
  • Andover Continuum
947 Views

Alarm Viewer at Workstation displays only the name of the object in alarm instead of the full path.

Issue Alarm Viewer at one WS displays only the name of the object in alarm instead of the full path. Environment CyberStation Windows Cause Windows issue Resolution Windows service pack was found to be incorrectly installed or corrupt, re-installing the Windows OS service pack solved the problem.
View full article
Picard Product_Support
‎2018-09-06 11:03 AM

Labels:
  • Andover Continuum
917 Views

Pinpoints crashes when selecting object properties of an Active Animation.

Issue Pinpoints crashes when selecting object properties of an Active Animation. Environment Continuum Pinpoint v1.93 Cause Image files used in the Active Animation do not exist or mapped through to the wrong path. Resolution Check that the Image Files used in your Active Animation are actually located at the path indicated. If the image files have been moved from the initial location used when creating the graphics then this could be the cause of the error. Copy the files back to the original location, now you should be able to edit the Active Animations and change the Image Files paths to the correct graphic location. This problem was found in Continuum v1.93 Pinpoint after an upgrade from an undetermined version and the cause able to be identified after importing those graphics into a v1.94 system. Presumably v1.94 does not have the same problem when attempting to view the Active Animation Image Files.
View full article
Picard Product_Support
‎2018-09-06 11:02 AM

Labels:
  • Andover Continuum
976 Views

Can an xdriver be run on Comm 4 of a CX9200 with it the comm port set to AutoSet?

Issue Must add XDriver to a CX9200 where all other ports are being used.  Environment xdriver Comm Port CX9200 CX9300 Cause As soon as the port mode switches from xdriver to some other mode the xdriver file is detached and must be reattached to the comm port for the xdriver to work. Resolution The default mode of a comm port that is being used with an xdriver must be hard set to xdriver.
View full article
Picard Product_Support
‎2018-09-06 11:02 AM

Labels:
  • Andover Continuum
1253 Views

When logging in Web Client, are the User Name and Password encrypted when sent to the server?

Issue When logging in Web Client, are the User Name and Password encrypted when sent to the server? Environment Web Client CyberStation Cause Documentation Resolution Both the User Name and the Password are encrypted by default when sent on the wire, this is true even when the system has not been configured to use Secure Sockets Layer (SSL). To have ALL communications encrypted configure SSL per the instructions in chapter 3 of the Web Client Installation and Configuration document. (Establishing SSL Support for Confidential Information)
View full article
Picard Product_Support
‎2018-09-06 11:02 AM

Labels:
  • Andover Continuum
1334 Views

Creating an alarm to show when a controller output HOA is not in the Auto position.

Issue Can an alarm be created to notify an operator when the HOA switch on a controller is no longer in the Auto position? Is it possible to show on a graphic when a controller output is not in the Auto position? Environment Output Override Alarm Cause Controller HOA switch security. Resolution Each output has an Override attribute which is set to True when controllers corresponding HOA switch is not in the Auto position. The Override attribute can be used for alarming and for a visual indication on a Pinpoint graphic.
View full article
Picard Product_Support
‎2018-09-06 11:02 AM

Labels:
  • Andover Continuum
1031 Views

Unable to bring an existing CX9200 onto a rebuilt workstation.

Issue Following a workstation crash and subsequent replacement of the workstation PC, cannot bring the existing CX9200 online with the new Continuum Installation. Environment Cyberstation 1.6 CX9200 Windows XP SP3 Cause Continuum 1.62 does not support Windows XP with Service Pack 3. Resolution Install Continuum 1.62 on a Windows XP SP2 platform.
View full article
Picard Product_Support
‎2018-09-06 11:02 AM

Labels:
  • Andover Continuum
1475 Views

Can an Infinity Controller with a Modbus xdriver operate as a slave node to a third party Modbus device that is set up as the master node?

Issue Can an Infinity Controller with a Modbus xdriver operate as a slave node to a third party Modbus device that is set up as the master node? Environment Modbus RTU Modbus TCP/IP xdriver Cause Third party modbus Master has to poll data from a CX or BCX controller that is set up as a slave node. Resolution The Modbus TCP/IP xdriver can be configured to operate as a slave node. The Modbus RTU xdriver must be the Master node whatever MODbus network it is attached to.
View full article
Picard Product_Support
‎2018-09-06 11:02 AM

Labels:
  • Andover Continuum
1255 Views

Bacnet loop object direct acting and reverse acting inverted

Issue The bacnet loop no longer works correctly after upgrading to 4.500064 firmware Environment BCX B3 Continuum Cause The action property of the loop object was reversed in prior versions. This has now been corrected in firmware version 4.500064. Direct is now Reverse and Reverse is now Direct.   Resolution If the loop was being used in prior versions you will need to correct your configuration to use this version. An accumulating error will now get cleared when the loop object is put "out of service"
View full article
Picard Product_Support
‎2018-09-06 11:02 AM

Labels:
  • Andover Continuum
1097 Views

Getting error FiringOrder error when sending data to a controller

Issue Getting error FiringOrder error when sending data to a controller "Unable to reload object Network\Controller\FiringOrder.           You do not have sufficient access to do the requested operation" Environment Continuum Cause Firing Order is a Group Object, so if Group Objects are not open to the user then they can not be sent to a controller. Resolution Firing Order is a Group Object thus when reloading a controller (send to controller) the user requires security rights for Groups.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
997 Views

How can a deleted Pinpoint graphic be restored?

Issue How can a deleted Pinpoint graphic be restored that was mistakenly deleted. Environment Pinpoint Graphic Cause A Pinpoint graphic was mistakenly deleted. Resolution In order to restore a deleted graphic and hope to have it restored with all the points from the database attached, in addition to the PIN file and background being in the correct drive and folder, you will need either a text export (.dmp) of the graphic file (which you would import) or you would need to restore the database from before the deletion. The PIN file has all the control objects but no link to the points that were attached on a certain graphic file. The database has the links to the points in the ObjectList of the Panel table. This is how you could have just one VAV.pin file and use it for hundreds of VAV boxes in a building. If you cannot restore a backup of the database and you do not have a text export of the graphic you will need to use the PIN file and background (if applicable) and manually attach the points to the control objects in the graphic.  To do this create a New >> Graphics in the location of your choice in ContinuumExplorer. Then using the menus go to File >> Import Panel File... and navigate to the PIN file and import it. This will bring in all the control objects in the locations they were before the deletion. Then add the background to the graphic by going to File >> Configuration and the Canvas tab. You then have to attach the points to the controls.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
995 Views

How to create personnel on a webClient user's PC

Issue On the webClient interface, it is not easy to find a way to create personnel. Environment Continuum webClient Cause No manuals describe how to create personnel via webClient user PC Resolution Log onto webClient Click "Search" on the top of the interface. From the left side of the interface click "All Objects" From the drop down list, select "Personnel" On the top of the new window, click "New Personnel", A personnel editor appears Following the same steps required for creating personnel objects in CyberStation, completing the necessary items. Click "Save " at the bottom of the editor Note: webClient does not support adding or editing photos for personnel objects. Go to CyberStation to do this.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
996 Views

B4920 does not have the Send to Database option.

Issue While rebuilding a database by bringing controllers online then initiating a Send to Database we find that the B4920 controllers do not offer a send to database option. Environment B4920 Send to Database Cause Send to database option was never added to the B4920. Resolution The controller will have to be rebuilt manually.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Labels:
  • Andover Continuum
1226 Views
  • « Previous
    • 1
    • …
    • 92
    • 93
    • 94
    • …
    • 111
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of