Soap error on launching graphics in WebClient.
  • Soap error on launching graphics in WebClient.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 11:14 AM
Unable to launch WebPinpoint graphics on client machines and/or at the webserver. Receiving the following errors when trying to launch a graphic in WebClient
  • Could not connect to server.  Cause: The remote server returned an error: (404) Not Found
  • Could not create ACWPPServerProxy Application on the remote server.
  • Server: http://0.0.0.0/DNWACServerFactory/WACServerFactory.soap.
IIS
WebClient
WebPinpoint
In IIS, the DNWACServerFactory authentication was failing when configured for Passthrough authentication.
  1. Deselect Passthrough Authentification.  (In Windows 7 you'll find this in IIS under DNWACServerFactory Basic Settings.
  2. Use Windows Authentication
  3. Enter the Windows User and Password. The connection should succeed.
  4. Reboot the IIS Server
  5. The accwppserverproxy process stays up and graphics launch properly.
  • 10865