Controller Error Log shows error code 5128.
  • Controller Error Log shows error code 5128.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 11:13 AM
  • Error Log
  • Error Code
  • NetController
  • BCX
  • ACX
An Infinity Controller is dropping offline.
  • Controller error code 5128 (0x00001408) is an indication that the controllers network comm buffer is out of memory.
  • Normally the network transceiver will shut down when this happens to protect the controller.
  • This is generally an indication that the controllers comm buffer is being overtaxed.  This can happen when there is a data storm present on the network.