3rd Party Device Drops Off Line when Graphic Panel is Shut Down.
  • 3rd Party Device Drops Off Line when Graphic Panel is Shut Down.
  • JohnBoehmer
    JohnBoehmer
‎2018-09-06 11:10 AM
A graphic displays the values of 50 points from a Third party controller.
The graphic launches normally and all point values update normally while the graphic is running.
Once the graphic panel is shut down the controller drops offline.
  • 3rd Party Device
  • BACnet
  • Pinpoint
  • Graphic
  • While pinpoint graphics poll point values sequentially, when a graphic is shut down pinpoint will unsubscribe from all of the points at once.
  • While some 3rd party devices can handle large numbers of unsubscribe requests, other devices may overwhelmed when too many requests to unsubscribe occur in close succession.
  • Use Plain English to mirror points form the 3rd party device to local numerics.
  • Display mirrored points in the graphic panel rather than the actual points in the device.
  • 11022