Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2209 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 91
    • 92
    • 93
    • …
    • 111
  • Next »
Label: "Andover Continuum" Show all articles

Proper shielding where there is no cable shield termination point on a controllers comm terminal.

Issue Third party device does not provide a place to terminate the shield on the comm bus cable. Environment MSTP Infinet Cause Comm cable shielding is required for MSTP and Infinet buses but a controller does not provide a termination point for the shield. Resolution The shield on a comm cable works something like a drain, by redirecting any electrical interference to ground. rather than allowing it to degrade the data signal. If there is more than one grounding point on a shield conductor, often there is the potential that the two ground points have difference of electric potential.   Such a situation could cause the shield to actually introduce electrical interference as the current passes from the point of greatest potential, through the cable and to the point of lowest potential.  For this reason a shield should always be grounded on one end but never be grounded at both ends.  These days many field bus controllers include non grounded shield terminations that simply serve to connect all shield wires as one continuous conductor that are drained by the master controllers shield termination point which is grounded. Where there is no shield termination, simply make sure that the shields from two comm cables are connected together.  
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1232 Views

Methods to edit output files from the Report object to customize reports.

Issue Methods to edit output files from the Report object to customize reports. Environment Continuum Report Object Cause The Reports generate .PDF and .SVG files when configured as a chart. How can these files be modified to produce a tailored report? Resolution There are four file formats that can be produced with a Report object. Text HTML Easily editable with a text editor such as Notepad or Word. Text XML Easily editable with a text editor such as Notepad, Excel, or Word. Chart - PDF Typically, PDF files are not easily modified but you can use Adobe Acrobat Professional to add  simple text to your Report or export to a Microsoft Word format where you can then edit the report as much as you want. The downside to this is that Adobe Acrobat can be an expensive purchase and the end result from these conversions is that some text fields are cut off or displaced.  Chart - WEB (SVG) Another option is to use the Web format for your Report, configured from the Output tab of the Report object, to save the Report chart as a .SVG  (Scalable Vector Graphic) file. This format is very similar to XML and can be edited with a simple text editor. There are also SVG Editors available that allow creating / editing SVG files in a graphic canvas such as what Illustrator provides. One such application is Inkscape Open Source application available at the link below. http://inkscape.org Information on the SVG format can be found on the Wiki at the link below. http://en.wikipedia.org/wiki/Scalable_Vector_Graphics
View full article
Picard Product_Support
‎2018-09-10 12:45 PM

Labels:
  • Andover Continuum
1152 Views

Video Layout will not pop up when triggered from an alarm

Issue Video Layout will not pop up when triggered from an alarm Environment Windows Continuum 1.9x Cause Workstation Preferences not setup Resolution To fix this you need to go into the workstation, edit workstation, go to preferences, go to No.27 in the list where it say "Video on Alarm" change the value from None to ether Layout or Monitor, this will now allow your Video window to pop up on alarm
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • Andover Continuum
  • CCTV
1077 Views

Can Cat 6 cable be used with continuum network controllers?

Issue Network Question Environment Continuum 1.XX All controllers Cause Ethernet Cable question. Resolution Not only is Category 6 cable future-safe, it is also backward-compatible with any ... What is the difference between a CAT5 and CAT6 patch cable? Cat 6 will be overkill but will work fine. It has more stringent specs for crosstalk and noise than 5e and is designed to support 10GBASE-T.  
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • Andover Continuum
1060 Views

3rd Party Device Drops Off Line when Graphic Panel is Shut Down.

Issue A graphic displays the values of 50 points from a Third party controller. The graphic launches normally and all point values update normally while the graphic is running. Once the graphic panel is shut down the controller drops offline.  Environment 3rd Party Device BACnet Pinpoint Graphic Cause While pinpoint graphics poll point values sequentially, when a graphic is shut down pinpoint will unsubscribe from all of the points at once. While some 3rd party devices can handle large numbers of unsubscribe requests, other devices may overwhelmed when too many requests to unsubscribe occur in close succession. Resolution Use Plain English to mirror points form the 3rd party device to local numerics.  Display mirrored points in the graphic panel rather than the actual points in the device.
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • Andover Continuum
1012 Views

How long does it take to update the Continuum database.

Issue During the uprev of Continuum, the database initialization utility takes a while to update the database. Environment CyberStation SQL Cause Many factors will determine how long it will take for the database update process to complete. These include but are not limited to: - Size of the database - Server performance - Network performance Resolution The main factor determining the time it will take to update the database if its size. as a guideline a 6 GIG database will take about 30 minutes to update.
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • Andover Continuum
854 Views

High Resolution Counter Input Specifications

Issue Need to know if the counter input on a xPDI8 meets the 140 hz specification that is called out in the Project Specification.   Environment xPDI8 xPBD4 Counter input Cause Need to know if the high resolution counter input on a xPDI8 or an xPBD4 Resolution While the xPDI8 counter input is rated for 140 Hz. this spec is based on a 50% duty cycle rate.  In any case, the minimum pulse width we can read on a high resolution counter input is 3.57 ms.  Anything less than 3.57 ms cannot be read reliably by the XPDI8.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
1118 Views

Temperature sensor input is not changing.

Issue Temperature sensor input point is not updating. Sensor works fine on another input. Environment i2 controller Cause The threshold may be incorrectly set. For example, if it is set to 10 instead of 0.1. Resolution Check the threshold and make sure it is set to 0.1.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
1386 Views

Behavior of IOU modules when communication is lost with the main CPU.

Issue Do IOU modules retain their current state when they lose communication with the host NetController? (NC1, NC2) Environment CX9900 CX9400 CX9680 IOU Modules Cause Documentation Resolution Upon losing communication with the NetController, output modules (DO-4. AO-4 etc) start a 260 *** second timer (4 minutes and 20 seconds), if communication is not restored before the time expires the module turns off the outputs as a safety measure. For Digital outputs the outputs will be turned OFF. (Invert attribute is taken into account). For Analog outputs the output value will be set to zero. *** For access control modules (AC1, AC1A, AC1Plus) the timer is 10 seconds to avoid leaving a door unlocked for an extended period of time.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
900 Views

Product support for EasyLobby Visitor Management.

Issue Contact information for product support for EasyLobby Visitor Management. Environment CyberStation EasyLobby Visitor Management. Cause Documentation Resolution EasyLobby directly supports their software plus the Continuum - EasyLobby integration software. Please forward all EasyLobby support requests directly to them. support@easylobby.com 781-455-8558
View full article
Picard Product_Support
‎2018-09-06 11:28 AM

Labels:
  • Andover Continuum
1398 Views

Handle mismatch issues.

Issue Infinet controller could not see points on its parent controller (CX9680). When the parent controller was reloaded all references to point in the parent controller were broken.  Now none of the child infinet controllers can see points on the parent controller. Environment Infinet NetController BCX Handles LSX280 External references Cause The LSX280, which is the old SX8000 system service tool can be destructive to a Continuum based system. The LSX280 uses a very different process to calculate object handles.  Doing learns with the LSX280 can damage the object handle structure of a Continuum system in ways that may be hard to repair.    Resolution Ran the Import Export Fixup Utility.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1316 Views

Modbus RTU Communication is sluggish.

Issue Controller error log reports the following modbus error codes.  0x0000f806 0x0000f808 0x0000f80c   Environment Modbus RTU Stop Bits Cause Incorrect comm port configuration. Resolution Changed the comm port configuration from 1 stop bit to 2 stop bits.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1353 Views

Is it possible to dump objects to text from a PE program?

Issue How to dump object from a PE program Environment CyberStation Cause Documentation Resolution Use the DUMP keyword to dump objects from a PE program running in CyberStation. Example: Dump MyNetwork\MyController\MyObject to "C:\Temp\MyObject.txt" The object will be exported in DUMP format, there is no way to do the same in CSV format.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1026 Views

Scan time on a Netcontroller is high

Issue Performance of the Netcontroller could be slow because of the scan rate Environment All Netcontrollers Cause Programs and functions that are polling data frequently can drive up the scan time Resolution The scan cycle has the following components to evaluate and process: System variables, download schedules, update inputs, run programs, update outputs, process alarms. Any of these can drive up the scan, but typically there is a program that is requesting polling updates on child controllers (infinet, mstp, modbus) that is driving up the scan. To troubleshoot this, disable all of the programs and enable them one by one to determine which programs are driving up the scan. Once that is determined, focus on adjusting the program accordingly. Performance of the system can be affected by a slow scan time and normally as the scan rate goes up, the performance goes down. An extremely high scan rate would be 50 where the performance is unusable, but could still be working. A scan rate of less than 1 second is ideal, but the real measure of the acceptable rate would be determined by the end user. A scan time of 5 seconds may be acceptable. The scan rate is similar to CPU utilization on a PC, so that high utilization over long periods of time will be more taxing on the controller.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1369 Views

How to determine a controller's configuration options.

Issue Knowing just the serial number of a controller, how to determine the options configured. Environment CX, bcx Cause How to determine a controller's configured options when only knowing the serial number. Resolution When a controller is online with CyberStation simply run ContinuumExplorer, navigate to the controller, select and right-click on the controller and select Edit. Look at the Options tab. However, if the controller is non-functioning then contact the US Repair Dept at (978) 475-9600 Press 2 then 3 or via email at tacus.WLCrepair@schneider-electric and provide them with the serial number and controller type. They can look up the options that have been configured.
View full article
Picard Product_Support
‎2018-09-06 11:36 AM

Labels:
  • Andover Continuum
1047 Views

No Continuum icon in the notification area of Windows task bar.

Issue After installing Continuum, on launching Cyberstation Continuum does not display the logon dialogue box.  Cannot launch the logon dialogue manually because no Continuum icon appears in the notification area of Windows task bar. Environment Cyberstation Continuum Logon Cause Problem with the OS installation or the corporate image that was used to install the operating system. Resolution Following a reformat of the workstations hard drive and reinstallation of the operating system, Cyberstation installed properly. 
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1311 Views

Smart T-Stat Labels are not available in all languages

Issue Does Schneider Electric offer replacement labels to convert the Smart Thermostats to other languages? Environment Viconics T-Stats French, German, Italian, etc. Cause It is desired to have labels on the wall mounted thermostats that are in the native language of the installation site. Resolution Unfortunately, there is not an offering for labels for the sensors for any other languages.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
  • Field Devices
948 Views

How much future schedule data can be put into a BACnet Schedule and stored in the controller.

Issue How much future schedule data can be put into a BACnet Schedule and stored in the controller. Environment Continuum BACnet Cause Need to store a years worth of Exception events in a BACnet controller and unsure if the BACnet Schedule performs the same as the Infinet where it only stores 7 days of events going forward. Resolution Unlike Infinet controllers, BACnet controllers will store all the Exception events in there schedules. This includes past as well as future exception events. (It's important to clear out the past events to free up space on the controller.) The total number of exception events depends on the amount of memory available in the controller being used. In Continuum v1.94 with the latest build of v4.5 firmware, we find that a Schedule in a b3 controller has the following memory requirements. 1. Blank b3 had 46624 bytes available. 2. Each BACnet Schedule object will consume 416 bytes. 3. Each Exception Event will consume 60 bytes. 4. Each Time Value in the Exception Event will consume 12 bytes. 5. Exception Events can be created (and saved to the controller) up until 1-Jan-2105. These events, all the way up to 2105, were stored in the controller. In this example, and only using an ON/OFF time value pair for each Exception Event, you will (theoretically) be able to store a bit more than 535 Events in a single Schedule (If this was the only created object in the controller.)
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1069 Views

Continuum logs clear data when size or interval is changed.

Issue Continuum logs clear logged data when size or interval is changed. Environment All Continuum CXs i2 devices Cause Function as designed. Resolution Continuum logs automatically clear any existing logged data if the size of interval are changed.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • Andover Continuum
1161 Views

Modbus RTU enabled on controllers comm port, loaded with correct XDriver, and configured correctly but does not communicate.

Issue Modbus RTU enabled on controllers comm port, loaded with correct XDriver, and configured correctly but does not communicate. Environment bCX1 Netcontroller II Cause There is a rare occurrence where older implementations of Modbus RTU upgrade cookies may not be properly installed even after seeming to uprev properly. Enabling both the Modbus RTU and Modbus IP bits in the upgrade file seems to resolve this. The upgrade procedure has now been changed and all future implementations of Modbus will have both the Modbus RTU and Modbus IP options enabled on the comm port being upgraded. Resolution For existing controllers that have already had the Modbus RTU option added to the comm port but have not validated that it works and are now seeing this problem, obtain a new upgrade cookie from Repairs requesting that both the Modbus RTU and Modbus IP options be enabled. All new orders for Modbus RTU or Modbus IP will have both options enabled on the comm port so this problem does not occur in the future.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • Andover Continuum
969 Views
  • « Previous
    • 1
    • …
    • 91
    • 92
    • 93
    • …
    • 111
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of