Will controller restore from flash if the ACCNetId is changed?
  • Will controller restore from flash if the ACCNetId is changed?
  • AbeMeran
    AbeMeran
‎2018-09-06 12:12 PM
Once a backup to flash is successfully performed, will the restore be successful if the acc net id changes?
bCX9640
CX9680
ACX5740
ACX5720
System design
Upon attempting to restore a backup of its DB from flash, the controller checks its acc net id against what is in the backup, if a mismatch is found the restore operation is aborted.
The error log will error 0x000014fb in the error code column and 0x1442000c in the Data1 column.