Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 93
    • 94
    • 95
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

How long does it take to update the Continuum database.

Issue During the uprev of Continuum, the database initialization utility takes a while to update the database. Environment CyberStation SQL Cause Many factors will determine how long it will take for the database update process to complete. These include but are not limited to: - Size of the database - Server performance - Network performance Resolution The main factor determining the time it will take to update the database if its size. as a guideline a 6 GIG database will take about 30 minutes to update.
View full article
Picard Product_Support
‎2018-09-06 11:10 AM

Labels:
  • Andover Continuum
967 Views

High Resolution Counter Input Specifications

Issue Need to know if the counter input on a xPDI8 meets the 140 hz specification that is called out in the Project Specification.   Environment xPDI8 xPBD4 Counter input Cause Need to know if the high resolution counter input on a xPDI8 or an xPBD4 Resolution While the xPDI8 counter input is rated for 140 Hz. this spec is based on a 50% duty cycle rate.  In any case, the minimum pulse width we can read on a high resolution counter input is 3.57 ms.  Anything less than 3.57 ms cannot be read reliably by the XPDI8.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
1221 Views

Temperature sensor input is not changing.

Issue Temperature sensor input point is not updating. Sensor works fine on another input. Environment i2 controller Cause The threshold may be incorrectly set. For example, if it is set to 10 instead of 0.1. Resolution Check the threshold and make sure it is set to 0.1.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
1532 Views

Behavior of IOU modules when communication is lost with the main CPU.

Issue Do IOU modules retain their current state when they lose communication with the host NetController? (NC1, NC2) Environment CX9900 CX9400 CX9680 IOU Modules Cause Documentation Resolution Upon losing communication with the NetController, output modules (DO-4. AO-4 etc) start a 260 *** second timer (4 minutes and 20 seconds), if communication is not restored before the time expires the module turns off the outputs as a safety measure. For Digital outputs the outputs will be turned OFF. (Invert attribute is taken into account). For Analog outputs the output value will be set to zero. *** For access control modules (AC1, AC1A, AC1Plus) the timer is 10 seconds to avoid leaving a door unlocked for an extended period of time.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • Andover Continuum
985 Views

Product support for EasyLobby Visitor Management.

Issue Contact information for product support for EasyLobby Visitor Management. Environment CyberStation EasyLobby Visitor Management. Cause Documentation Resolution EasyLobby directly supports their software plus the Continuum - EasyLobby integration software. Please forward all EasyLobby support requests directly to them. support@easylobby.com 781-455-8558
View full article
Picard Product_Support
‎2018-09-06 11:28 AM

Labels:
  • Andover Continuum
1552 Views

Handle mismatch issues.

Issue Infinet controller could not see points on its parent controller (CX9680). When the parent controller was reloaded all references to point in the parent controller were broken.  Now none of the child infinet controllers can see points on the parent controller. Environment Infinet NetController BCX Handles LSX280 External references Cause The LSX280, which is the old SX8000 system service tool can be destructive to a Continuum based system. The LSX280 uses a very different process to calculate object handles.  Doing learns with the LSX280 can damage the object handle structure of a Continuum system in ways that may be hard to repair.    Resolution Ran the Import Export Fixup Utility.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1460 Views

Modbus RTU Communication is sluggish.

Issue Controller error log reports the following modbus error codes.  0x0000f806 0x0000f808 0x0000f80c   Environment Modbus RTU Stop Bits Cause Incorrect comm port configuration. Resolution Changed the comm port configuration from 1 stop bit to 2 stop bits.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1599 Views

Is it possible to dump objects to text from a PE program?

Issue How to dump object from a PE program Environment CyberStation Cause Documentation Resolution Use the DUMP keyword to dump objects from a PE program running in CyberStation. Example: Dump MyNetwork\MyController\MyObject to "C:\Temp\MyObject.txt" The object will be exported in DUMP format, there is no way to do the same in CSV format.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1162 Views

Scan time on a Netcontroller is high

Issue Performance of the Netcontroller could be slow because of the scan rate Environment All Netcontrollers Cause Programs and functions that are polling data frequently can drive up the scan time Resolution The scan cycle has the following components to evaluate and process: System variables, download schedules, update inputs, run programs, update outputs, process alarms. Any of these can drive up the scan, but typically there is a program that is requesting polling updates on child controllers (infinet, mstp, modbus) that is driving up the scan. To troubleshoot this, disable all of the programs and enable them one by one to determine which programs are driving up the scan. Once that is determined, focus on adjusting the program accordingly. Performance of the system can be affected by a slow scan time and normally as the scan rate goes up, the performance goes down. An extremely high scan rate would be 50 where the performance is unusable, but could still be working. A scan rate of less than 1 second is ideal, but the real measure of the acceptable rate would be determined by the end user. A scan time of 5 seconds may be acceptable. The scan rate is similar to CPU utilization on a PC, so that high utilization over long periods of time will be more taxing on the controller.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1577 Views

How to determine a controller's configuration options.

Issue Knowing just the serial number of a controller, how to determine the options configured. Environment CX, bcx Cause How to determine a controller's configured options when only knowing the serial number. Resolution When a controller is online with CyberStation simply run ContinuumExplorer, navigate to the controller, select and right-click on the controller and select Edit. Look at the Options tab. However, if the controller is non-functioning then contact the US Repair Dept at (978) 475-9600 Press 2 then 3 or via email at tacus.WLCrepair@schneider-electric and provide them with the serial number and controller type. They can look up the options that have been configured.
View full article
Picard Product_Support
‎2018-09-06 11:36 AM

Labels:
  • Andover Continuum
1252 Views

No Continuum icon in the notification area of Windows task bar.

Issue After installing Continuum, on launching Cyberstation Continuum does not display the logon dialogue box.  Cannot launch the logon dialogue manually because no Continuum icon appears in the notification area of Windows task bar. Environment Cyberstation Continuum Logon Cause Problem with the OS installation or the corporate image that was used to install the operating system. Resolution Following a reformat of the workstations hard drive and reinstallation of the operating system, Cyberstation installed properly. 
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1512 Views

Smart T-Stat Labels are not available in all languages

Issue Does Schneider Electric offer replacement labels to convert the Smart Thermostats to other languages? Environment Viconics T-Stats French, German, Italian, etc. Cause It is desired to have labels on the wall mounted thermostats that are in the native language of the installation site. Resolution Unfortunately, there is not an offering for labels for the sensors for any other languages.
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
  • Field Devices
1111 Views

How much future schedule data can be put into a BACnet Schedule and stored in the controller.

Issue How much future schedule data can be put into a BACnet Schedule and stored in the controller. Environment Continuum BACnet Cause Need to store a years worth of Exception events in a BACnet controller and unsure if the BACnet Schedule performs the same as the Infinet where it only stores 7 days of events going forward. Resolution Unlike Infinet controllers, BACnet controllers will store all the Exception events in there schedules. This includes past as well as future exception events. (It's important to clear out the past events to free up space on the controller.) The total number of exception events depends on the amount of memory available in the controller being used. In Continuum v1.94 with the latest build of v4.5 firmware, we find that a Schedule in a b3 controller has the following memory requirements. 1. Blank b3 had 46624 bytes available. 2. Each BACnet Schedule object will consume 416 bytes. 3. Each Exception Event will consume 60 bytes. 4. Each Time Value in the Exception Event will consume 12 bytes. 5. Exception Events can be created (and saved to the controller) up until 1-Jan-2105. These events, all the way up to 2105, were stored in the controller. In this example, and only using an ON/OFF time value pair for each Exception Event, you will (theoretically) be able to store a bit more than 535 Events in a single Schedule (If this was the only created object in the controller.)
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • Andover Continuum
1269 Views

Continuum logs clear data when size or interval is changed.

Issue Continuum logs clear logged data when size or interval is changed. Environment All Continuum CXs i2 devices Cause Function as designed. Resolution Continuum logs automatically clear any existing logged data if the size of interval are changed.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • Andover Continuum
1263 Views

Modbus RTU enabled on controllers comm port, loaded with correct XDriver, and configured correctly but does not communicate.

Issue Modbus RTU enabled on controllers comm port, loaded with correct XDriver, and configured correctly but does not communicate. Environment bCX1 Netcontroller II Cause There is a rare occurrence where older implementations of Modbus RTU upgrade cookies may not be properly installed even after seeming to uprev properly. Enabling both the Modbus RTU and Modbus IP bits in the upgrade file seems to resolve this. The upgrade procedure has now been changed and all future implementations of Modbus will have both the Modbus RTU and Modbus IP options enabled on the comm port being upgraded. Resolution For existing controllers that have already had the Modbus RTU option added to the comm port but have not validated that it works and are now seeing this problem, obtain a new upgrade cookie from Repairs requesting that both the Modbus RTU and Modbus IP options be enabled. All new orders for Modbus RTU or Modbus IP will have both options enabled on the comm port so this problem does not occur in the future.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • Andover Continuum
1166 Views

How to backup the database automatically to the specify path with Continuum Standalone system

Issue Continuum Standalone system use SQL Express without function of maintenance, So other method need to be implemented  to do this task Environment Cyberstation SQL Express Cause Require to backup the database with a record. Resolution Install SQL Server Management  Studio Tools for SQL Express Backup the database to specify path, such as "D:\backup\ContDB_Mon.bak" Run SQL Server Management Studio Express and create a new query Copy the following SQL syntax and paste in this new query then  run it EXEC Sp_Addumpdevice 'disk', 'ContinuumDB', 'D:\backup\ContDB_Mon.bak'   Create another new query called ContDB_BU_Mon.sql, copy the following SQL syntax and paste in the query  then run it Select getdate() as "ContDB backup startTime" go BACKUP DATABASE  [ContinuumDB]  TO [ContinuumDB] with Format, INIT,NAME= N'Contdb_Mon Database Backup', SKIP, Norewind, NOUNLOAD, STATS = 10 go select getdate() as "Contdb Backup Endtime" go  Close the query above and save it to D:\backup\ContDB_BU_Mon.sql Create a .txt file with the following command then save it as .bat file OSQL -S(Local)\SQLEXPRESS -E -i  "D:\backup\ContDB_BU_Mon.sql" -O  "D:\Backup\Contdb_BU_Mon.log"   From Windows Control panel > Performance and Maintenance > Scheduled Tasks, Add Scheduled Task, select the "Browse" button, find the .bat file you want to run, then set the time schedule you desired. After the scheduled task created successfully, the database backup will be executed scheduled with record. the record was written in the file Contdb_BU_Mon.log.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • Andover Continuum
1797 Views

Effect on a BACnet network if the Network Id - UDP setting in bCX40x0 have been set to different values

Issue What effect does it have on a BACnet network if the Network Id - UDP setting in bCX40x0's on the same BACnet IP network have been set to different values? Product Line Andover Continuum Environment Continuum BACnet bCX4000 bCX4040 Cause A site had it's routers configured with different Network Id - UDP values and communications between controllers were not reliable. Resolution In the scenario below, the routers have different Network Id's for the UDP network. They may still be able to talk with each other, but they will all think they are on different networks which could cause routing issues and much more traffic than is required.  Controller         UDP NET ID                                         UDP COMM2 1                                  1                                                            2701 2                                  2                                                            2702 3                                  3                                                            2703 4                                  4                                                            2704 5                                  5                                                            2705 6                                  6                                                            2706 7                                  7                                                            2707 If all of these bCX's are on the same IP network then they will need to have the same Network Id - UDP value. By default we (and most other BACnet vendors) use a Network Id of 1. Change all of the bCX's so they are on Network ID - UDP of 1, as below. Controller           UDP NET ID                                         UDP COMM2 1                                  1                                                            2701 2                                  1                                                            2702 3                                  1                                                            2703 4                                  1                                                            2704 5                                  1                                                            2705 6                                  1                                                            2706 7                                  1                                                            2707
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Labels:
  • Andover Continuum
1634 Views

BACnet error reloading Infinity controller

Issue Error reads....BACnet Device for this Infinity controller is not created, please perform a ‘Find new BACnet devices’. Site does not have any BACnet devices Environment CyberStation CX Infinity controllers Cause Some how Event Notification objects are configured under the infinity controllers in the database Resolution Delete non applicable BACnet only objects that some how got configured under the infinity controllers
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Labels:
  • Andover Continuum
1687 Views

Tablet PCs and webclient screen resolution

Issue Screen resolutions may be distorted on a tablet PC Environment Webclient Tablet PC Windows 7 Cause Screens, graphics displays and drivers on Tablet PCs are very specific hardware for that device and can cause distortion when rendered in Continuum Resolution No QA testing has been done with any Tablet PC so results may vary as to how the screens are displayed on these devices
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Labels:
  • Andover Continuum
1438 Views

After a power reset, bCX1 comes back online with its comm2 set to a different baud rate than before it went offline, no longer communicating with the connected b3 MSTP controllers.

Issue After a power reset, bCX1 comes back online with its comm2 set to a different baud rate than before it went offline, no longer communicating with the connected b3 MSTP controllers. Environment bCX4000 bCX4040 bCX9640 CX9680 CX9900 Cause Controller comes back from power fail and does not have the correct baudrate set which results in loss of communications to all field controllers. Resolution 4.500076 should correct this issue. If not get the controller error log and see if the controller is cold starting. On those controllers that have come back from power fail and have their comm port set to 9600, you can try setting the defaultbaud attribute of that comm port to the desired speed. For this to be saved to the controllers EEPROM you will need to do this from the command line, see the syntax for this below. (replace baud19200 with your desired baudrate) comm2 defaultbaud = baud19200   Or   Write a PE program to detect the baud condition and change the baud to the desired rate
View full article
Picard Product_Support
‎2018-09-06 11:03 AM

Labels:
  • Andover Continuum
1691 Views
  • « Previous
    • 1
    • …
    • 93
    • 94
    • 95
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore