Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,851
  • TAC IA Series 1,825
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 332
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 149
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2045 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 85
    • 86
    • 87
    • …
    • 103
  • Next »
Label: "TAC Vista" Show all articles

STR-250 functionality on Micro Regulators (MR).

Issue Does the STR-250 work on Micro Regulators (MR)? Environment I/NET Seven STR-250, I/STAT, M/STAT I/SITE Controller and Micro Regulators (MR) Cause The STR-250 Wall Module is the replacement for the commonly referred to I/STAT sensor, still referenced in I/NET documentation.  The I/STAT is no longer available.  Resolution The STR-250 sensor is the replacement for the I/NET I/STAT, so installation and configuration for the STR-250 is as per this I/STAT. There are two documents that will provide assistance with this TCON126 and TCON299 (Chapter 21). The STR-250 full functionality must be installed on the I/STAT port of any I/NET device and configured as detailed in the above documents. Only one I/STAT port exists per MR. The M/STAT is still available and is used as the hardware tool for configuring the controller settings on all supported I/STAT devices, such as, all Micro Regulators (MR) variants, I/Site LAN Controller (Model 7728) and Xenta 102-AX. 
View full article
Picard Product_Support
‎2018-09-10 05:32 AM

Labels:
  • TAC INET
  • TAC Vista
1613 Views

Vista is very slow after a TGML graphic is opened

Issue Vista is very slow after a TGML graphic is opened, it takes like 30 seconds to open a small folder. Environment Vista 5.1.6 Cause A Loytec NIC USB used as the Lon interface is not online because the engineers computer is not connected to the Lon network. But the Xentas and Lon network under the Lon interface are online in Vista for some reason. So Vista tries to read the values from the Xentas and this makes Vista hang for periods of time. Resolution Create a new Lon Network interface Drag and drop the Lon network to the newly created interface Drag and drop the Lon network back to the original interface Now the Xentas show up as offline
View full article
Picard Product_Support
‎2018-09-06 12:59 PM

Labels:
  • TAC Vista
911 Views

24 hour Vista log does not collect information.

Issue When a log is defined in Vista for a 24 hour log period no values are logged. Environment Vista 5.1.6. Windows 7 32 bit Cause There is a known issue with Vista 5.1.6 and time zones of the Vista server PC. 24 Hour logs do not start to collect information if the time zone is set to GMT +2 or greater. Resolution The only resolution currently is to change the log to 12 hourly. Then use Excel to add these together if this value is used in a Report. This problem has been fixed in the release of Vista 5.1.6. Upgrading to this version will fix the problem.
View full article
Picard Product_Support
‎2018-09-06 12:58 PM

Labels:
  • TAC Vista
944 Views

Is the Operators Panel TAC OP1500 still available?

Issue Is the Operators Panel TAC OP1500 still available? Environment TAC Vista 5.1.X Cause N/A Resolution The TAC OP1500 is no longer available from Schneider Electric Buildings Business. It may be available from other Schneider Electric branches. See Product Announcement PA-00138 for details.
View full article
Picard Product_Support
‎2018-09-10 05:04 AM

Labels:
  • TAC Vista
1283 Views

When copying a trend log in Xbuilder 5.1.6, the green arrows on the signals disappear.

Issue When copying a trend log in Xbuilder 5.1.6, the green arrows on the signals disappear. Environment TAC Xbuilder 5.1.6 Cause Bug in the code that appeared in v5.1.6 Resolution If you bind something to the signal or reload the project, the green arrows appears again. This issue will be fixed in version 5.1.7.
View full article
Picard Product_Support
‎2018-09-06 12:55 PM

Labels:
  • TAC Vista
844 Views

Get "service not implemented" message when downloading Menta application from Vista.

Issue Get "service not implemented" message when downloading Menta application from Vista. Environment TAC Vista 5.1.X Menta application downloaded via Vista Cause A programming error in the Menta application has occurred. Resolution Check the Menta application - start with the last added block and check for calculation errors etc, e.g. Division by 0 in a calculation.
View full article
Picard Product_Support
‎2018-09-06 12:55 PM

Labels:
  • TAC Vista
1579 Views

The heating and/or cooling outputs do not work when the TAC Xenta 121-HP is configured as a slave controller.

Issue The heating and/or cooling outputs do not work when the TAC Xenta 121-HP is configured as a slave controller. Environment TAC Xenta 121-HP versions up to 1.25 Cause If the device is configured as a slave, heating and cooling is dependent upon the isolation valve value. If there is no isolation valve configured, the heating and cooling outputs will be blocked. Resolution The isolation valve needs to be configured regardless of whether it exists or not in order to make the heating and cooling outputs work.
View full article
Picard Product_Support
‎2018-09-06 12:54 PM

Labels:
  • TAC Vista
991 Views

TAC Menta, Changing name on a HFB I/O-block in an HFB removes the connections

Issue TAC Menta, Changing name on a HFB I/O-block in a HFB removes the connections Environment TAC Menta Hierarchal Function Block (HFB) Cause Then a HFB IO-block is renamed, it loses its connection to other blocks. Resolution Disconnect the connections from the HFB IO-output Place the connection next to the HFB block Rename the output of the HFB Re-connect the HFB IO-output.
View full article
Picard Product_Support
‎2018-09-06 12:54 PM

Labels:
  • TAC Vista
1526 Views

Can not get the communication port in Vista online. Get error message: "Cannot open port:No 8250 present"

Issue Can not get the communication port in Vista online. Get error message: "Cannot open port:No 8250 present" Environment Vista 5.1.6 Windows 2008 server Cause This error message only say that Vista can not communicate with the chosen com port in the computer.   Resolution Try to verify that the chosen com port on the computer works. Use for example the device manager and check the status on the port.  If RSPD is used make sure the correct version of it is used, only the latest support 64 bit OS.
View full article
Picard Product_Support
‎2018-09-06 12:54 PM

Labels:
  • TAC Vista
1343 Views

What is Xenta 28x, 30x, 401 web and Xenta 28x, 30x, 401 TCP/IP

Issue What is Xenta 28x, 30x, 401 web and Xenta 28x, 30x, 401 TCP/IP Is there any documentation for  28x, 30x, 401 web and Xenta 28x,30x, 401  TCP/IP Environment Xenta 281 Web Xenta 282 Web Xenta 301 Web Xenta 302 Web Xenta 401 Web Xenta 281 TCP/IP Xenta 282 TCP/IP Xenta 301 TCP/IP Xenta 302 TCP/IP Xenta 401 TCP/IP Cause These are not products they are packages. Resolution The Xenta 280, 30x, 401  web and TCP/IP are not a controller type. It is just a packaging. The 280, 30x, 401  TCP/IP is sold with a Xenta 911 and the Xenta 280,30x, 401  Web are sold with a Xenta 511. So the documentation for "normal" Xenta 280 and Xenta 911/511 is used. This can be found on the Exchange Extranet.  
View full article
Picard Product_Support
‎2018-09-10 05:16 AM

Labels:
  • TAC Vista
1198 Views

Will the TRENDLOG ID change when upgrade the vista Database.

Issue Will upgrading a site make any changes to the TRENDLOG ID (not GUID) in the SQL database (DB). Environment Vista 5.1.X Vista 5.1.7 Cause Some third party software packages (such as energy monitoring packages) that rely on the "TRENDLOG ID" as a reference to obtain data from the Vista trend log database, will not work properly if the "TRENDLOG ID" changes. Resolution No, the "TRENDLOG ID" will not change when log database is upgraded from 5.1.X to 5.1.7.
View full article
Picard Product_Support
‎2018-09-06 12:52 PM

Labels:
  • TAC Vista
1222 Views

In Vista 4.5 it is not possible to acknowledge an alarm logged in as a Field user from Webstation, is this possible in Vista 5.1.6?

Issue In Vista 4.5 it is not possible to acknowledge a alarm logged in as a Field user from Webstation, is this possible in Vista 5.1.6? Environment Vista and Webstation 5.1.6 Cause In Vista 5.1.6 it is possible to acknowledge alarms even with a Field user. Resolution Upgrade from Vista 4.5 to Vista 5.1.6
View full article
Picard Product_Support
‎2018-09-06 12:52 PM

Labels:
  • TAC Vista
996 Views

Upgrading Webstation license.

Issue Currently has a 1CAL Webstation license, but wants to upgrade to 12CAL. Can the upg. license part be used? Environment Vista 5.1.X Cause  Upgrading number of Webstation licenses within the same version. Resolution The upgrade licenses are intended to be used only when upgrading from a previous version of Vista Webstation, and is not applicable for an increase of CALs.
View full article
Picard Product_Support
‎2018-09-06 12:52 PM

Labels:
  • TAC Vista
1000 Views

Upgrading Vista (and other modules such as Webstation) may require an upgraded license

Issue Depending on the initial version of Vista it may be necessary to order and use the "Upg" licenses when upgrading from an older version of Vista to the current version Environment TAC Vista versions within the same sub range: 5.0.x 5.1.x Cause License upgrade types Resolution The licenses are limited to the ranges of 5.0.x and 5.1.x. Upgrades within these ranges are free. Example: 5.0.1 to 5.0.3 is free of charge. 5.0.1 to 5.1.0 needs upgraded licenses. Use the "Upg" license package when ordering. 5.1.0 to 5.1.5 is free of charge.
View full article
Picard Product_Support
‎2018-09-06 12:52 PM

Labels:
  • TAC Vista
1006 Views

Remote Workstation crashes due to pagefile overflow

Issue Remote Workstation crashes due to pagefile overflow Environment Vista Workstation with Remote Vista Server Cause The minimum system requirements for Vista Workstation is 1 GB of RAM.  On a larger site or for machines with more programs running this should be increased.  This is especially true for machines that frequently run multiple graphic pages. Resolution Consult the documentation from you computers manufacturer to purchase and install additional RAM.
View full article
Picard Product_Support
‎2018-09-06 12:52 PM

Labels:
  • TAC Vista
1214 Views

Changing the Home Graphic in Workstation / Webstation.

Issue Customize the default graphic that opens after login. Environment Vista Workstation Vista Webstation Cause Vista defaults to a generic view which can be customized. Resolution The Home Graphic can be changed in any user profile, including the default Vista $UserProfile.  A user profile can be used by several users.  To create a User Profile In the folders pane, right-click the root object. Point to New, point to Object, and then click User Profile. Type the name of the object.  Browse the Home Graphic in the new User Profile and update each User properties to use the correct User Profile.
View full article
Picard Product_Support
‎2018-09-06 12:52 PM

Labels:
  • TAC Vista
2332 Views

TAC Vista User license settings in 2008 Server R2

Issue License settings for different users on Win2008 Server R2 differs from previous versions OS. The user that installs the license system (either with TAC  Vista or as a standalone) will make the initial license configuration in the .Default user in the registry. Next time a new user (that has never logged on to this server before) logs on to the PC, the default license settings are copied to this users profile. Then the user who has installed the license system logs in to the server, and changes the license settings. Now, when the second user logs in again, the license settings are the same as they were in the beginning. It seems that these settings are not stored in the general system settings, but actually in the domain users profile that are fetched upon login. So, all users that have logged in with wrong or not updated license settings, will have to login again and change their settings. Environment Windows 2008 Server R2 TAC Vista Cause Unable to access licenses when logging in with other account than used when changing license path. Resolution If changes are done to the license path ,every user has to manually change their settings to get the system to work. Or, a batch file or similar has to be run upon login to change settings in question.
View full article
Picard Product_Support
‎2018-09-06 12:51 PM

Labels:
  • TAC Vista
1262 Views

TAC Vista Report generator software

Issue Where to find the TAC Vista Report generator software for download.  Environment TAC Vista 5 Cause Specifically looking for the Report Generator software package. Resolution The Report generator software is included in the general TAC Vista software installation, and is not available separately.  
View full article
Picard Product_Support
‎2018-09-06 12:51 PM

Labels:
  • TAC Vista
1360 Views

Net-Point VAV Plug-In Compatibility with Windows OS

Issue Net-Point VAV Plug-In is not compatible with all Windows Operating Systems Environment Net-Point VAV Windows OS Cause Net-Point Plug-In is not registering or working in a Windows environment. The Net-Point VAV is a discontinued product of the former CSI company which was purchased by TAC. Resolution There has not been sufficient upgrades to the Plug-In software to allow compatibility above Windows XP. It will not function on Windows Vista, Windows Server 2008, or Windows 7 environments. There are no plans to upgrade this Plug-In therefore there is not a workaround.
View full article
Picard Product_Support
‎2018-09-06 12:51 PM

Labels:
  • TAC Vista
918 Views

Maximum value for an analog object in Vista

Issue How big of a number can a Vista analog object hold? Environment Vista all versions Cause In Vista, an analog value is of the type "float" and: Single precision, called "float" in the C language family, and "real" or "real*4" in Fortran. This is a binary format that occupies 32 bits (4 bytes) and its significand has a precision of 24 bits (about 7 decimal digits). Resolution A number with more than 6 digits in Vista will be shown as 1.23456*10e+006. If the value has more than 7 decimal digits, the digits over the 7th decimal will have poor precision.  
View full article
Picard Product_Support
‎2018-09-06 12:50 PM

Labels:
  • TAC Vista
917 Views
  • « Previous
    • 1
    • …
    • 85
    • 86
    • 87
    • …
    • 103
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of