Issue
Updating firmware from StruxureWare Building Operation and the still be usable with other BMS such as Continuum, I/A Series, I/NET, Sigma, and Vista
Environment
Site with more than one Building Management System
Cause
Implications of updating firmware on a controller from the StruxureWare Building Operation side and still compatible with existing
Resolution
For the controllers available on the StruxureWare Building Operation network that have been configured, take precaution when updating the firmware and still expect compatibility with other systems.
For example, at a Continuum site, with a b3 and the option to update of firmware from StruxureWare Building Operation, there are a couple of things to keep in mind. When selecting the b3, and the Update Firmware, it will ask you for the *.udp file. This can be downloaded from the extranet. The thing to keep in mind here is if you are using this controller in conjunction with Continuum, then pay particular attention to the Compatibility Matrix and the firmware which is compatible with the version of Continuum you are running. Updating a firmware that is not in line with the version of Continuum will create problems for the site. So when selecting the firmware *.udp, be sure of which firmware file you are selecting.
The operating system in the b3 controller is no different between StruxureWare Building Operation and Continuum. The PE code may be different though, so he should be able to learn these controllers into Continuum as long as they have their user memory cleared out.