Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,840
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 329
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1838 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 83
    • 84
    • 85
    • …
    • 92
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Using the Download function with a BACnet controller.

Issue When a download is performed on a BACnet controller does SmartStruxure overwrite the entire contents of the controller? Environment SmartStruxure 1.4 Download Cause Wish to replace the entire contents of a BACnet controller Resolution When downloading a BACnet controller from an Enterprise Server or an Automation Server the following takes place... StruxureWare downloads the configuration properties of the device proxy to the BACnet device. StruxureWare updates the object list of the BACnet device with the object list of the device proxy. StruxureWare writes the properties of the object proxies to the objects in the BACnet device. Following the download the contents of the BACnet device match the contents of the device proxy.  If there are objects in an external BACnet device that do not have corresponding object proxies in StruxureWare, the Download operation deletes those objects in the device.  The Download command does not delete vendor proprietary BACnet objects or properties as described by the ASHREA standard.
View full article
Picard Product_Support
‎2018-09-06 09:59 AM

Labels:
  • EcoStruxure Building Operation
1176 Views

Upgrade to 1.4 side effect with Central IO temperature inputs defaulting to Deg C in PE script programs

Issue After an upgrades to 1.4, units for temperature inputs on Central IO are not configurable. Affected programs no longer work correctly. When there is no client activity to convert to the locale of the client (there is not with the Script engine), the input is assumed to have the number that corresponds to degrees Centigrade. Product Line EcoStruxure Building Operation Environment SmartStruxure 1.4 Central IO Inputs PE Script Cause Units must be set  in the variables window of the affected script program. Resolution The following program would work fine in 1.3 if the temperature that is bound to the SpaceT input was configured to have units of Deg. F. When the user of this program upgrades to 1.4, this program will no longer work correctly. The input is assumed to have the number that corresponds to Deg. C. You can see it in the variable value listing block: 22.4°C is compared to the setpoint of 70°F and it does not work right. The units MUST be set within the Script program as below: Now it will work.
View full article
Picard Product_Support
‎2018-09-11 06:14 AM

Labels:
  • EcoStruxure Building Operation
998 Views

Can not import lon Lon Device template.

Issue Cannot import lon Lon Device template. Field stays red after browsing in the correct XIF file. Import button does still grayed out after browsing the correct XIF file. Environment StruxureWare Building Operation 1.3 and earlier Cause There is a problem with some regional settings. We have seen this using Turkish regional settings so far but the are probably other languages that will also cause the issue. Resolution Stop Workstation Open control panel Go to Regional and Language Options Change standards and formats to English. Click ok Start workstation again and import the file. Add your devices Close workstation Open Regional and Language settings and change back to your language Open workstation
View full article
Picard Product_Support
‎2018-09-06 09:59 AM

Labels:
  • EcoStruxure Building Operation
1921 Views

Eventlist fills with message "Modbus group re-factorized".

Issue Eventlist in StruxureWare workstation is filled very rapidly with the following messages: - * Modbus group re-factorized - * Modbus group factorized - * Modbus illegal data address Environment StruxureWare Building Operation 1.4.818 Cause The problem is that it is illegal registers in the Modbus register group or groups. Modbus is trying to resolve this by refactoring the factoring and refactoring but is not successful. Resolution The possible solutions are: Identify the illegal Modbus point in SmartStruxure and remove from the subscription. Solution Split the group in to two so that the illegal Modbus point is left out of the groups. Disable group poll and Force individual point polling by setting incorrect function code for the group.   If it is difficult to identify the illegal Modbus point then you can use solution 3 to do this.
View full article
Picard Product_Support
‎2018-09-06 09:59 AM

Labels:
  • EcoStruxure Building Operation
977 Views

Creating a Counter input in b3 controllers.

Issue b3 controllers in StruxureWare Building Operation do not seem to support Counter inputs. Environment Counter Inputs b3 Cause SmartStruxure does support the creation of Counter inputs within b3 controllers. Resolution Counter inputs are Analog Inputs.  When the Object Creation wizard is used to create an Analog input the user is prompted to select the electric type.  At this point select Counter.
View full article
Picard Product_Support
‎2018-09-06 09:57 AM

Labels:
  • EcoStruxure Building Operation
1166 Views

Federal Information Processing Standard (FIPS) Compliance

Issue Federal Information Processing Standard (FIPS) Compliance Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation Cause Is the Automation Server or Enterprise Server FIPS compliant? Resolution There is not Federal Information Processing Standard (FIPS) Compliance with the current release of Building Operation.
View full article
Picard Product_Support
‎2018-09-07 11:12 AM

Labels:
  • EcoStruxure Building Operation
1369 Views

StruxureWare Building Operation Runtime Compatibility available during Upgrades

Issue Is it supported to access an Automation Server 1.4.0 with the Workstation 1.4.1? Are there any problems and what features are supported when accessing a 1.4.0 Automation Server with WorkStation 1.4.1? Environment Enterprise Server / Workstation 1.4.1 Automation Servers 1.4.0, 1.3 with SP1 and SP2 Cause Understanding of the new Runtime Compatibility mode available in 1.4.1 available during system upgrades Resolution Building Operation supports runtime compatibility between servers running two versions on a single system, during an upgrade process. Version 1.4.1 servers are runtime compatible with version 1.3 SP1 and 1.3 SP2 servers. The system is able to exchange runtime information between 1.4.1 servers and 1.3 SP1 or 1.3 SP2 servers. However, configuration changes cannot be made from an upgraded WorkStation via an upgraded Enterprise Server to a non upgraded Automation Server, such as creating, configuring, and deleting objects. There is also no runtime compatibility for WebStation. Runtime compatibility means you can delay the upgrade of some Automation Servers running version 1.3 SP1 or 1.3 SP2 while upgrading the Enterprise Server, WorkStation, Reports Server, and some Automation Servers to version 1.4.1. You cannot make any configuration changes on an Automation Server running the 1.3 SP1 or 1.3 SP2 version with WorkStation and Enterprise Server running the 1.4.1 version. However, you can make the changes using a parallel WorkStation running a 1.3 SP1 or 1.3 SP2 version that is connected to the Automation Server running the 1.3 SP1 or 1.3 SP2 version. Full compatibility is supported on Automation Servers running the 1.4.0 version   Additional detail is available on the Online Help http://help.sbo.schneider-electric.com/topics/show.castle?id=9807&locale=en-US&productversion=1.4&a=1 Supported Features: Navigate You can navigate in the system tree of an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, object and property types removed in the 1.4.1 version compared to the 1.3 SP1 or 1.3 SP2 version are not be displayed in the system tree. Search You can perform an object or property search on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, object and property types removed in the 1.4.1 version compared to the 1.3 SP1 or 1.3 SP2 version are not be displayed in the search list. View Events You can view detailed information and perform commands on events on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. The 1.4.1 Enterprise Server will also store events from an Automation Server running 1.3 SP1 or 1.3 SP2 version. View Trend Logs and Trend Charts You can view trend log lists and trend charts on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. Extended trend log lists in the server running 1.4.1 version are functional and be able to retrieve values from a server running the 1.3 SP1 or 1.3 SP2 version. View Graphics You can navigate to and view a graphic on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server at 1.4.1 version. Graphic variable values can be changed with Graphics Editor, but configuration data cannot be changed. View Alarms You can view detailed alarm information from an Automation Server running the 1.3 SP1 and 1.3 SP2 version, with WorkStation and Enterprise Server at 1.4.1 version. Also actions on alarms can be performed, such as assigning or disabling an alarm and enabling a Change-state logging. View Dynamic Values You can navigate to and view dynamic values in the Watch pane from an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. However, because there is no way to navigate to and view objects or properties that have been removed in the 1.4.1 version, such dynamic values cannot be viewed. Transfer Values You can transfer values from an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with an Enterprise Server or Automation Server running the 1.4.1 version and the other way around. Change and Force Variables You can change and force variables using properties on an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. Lead and Shadow relationships Lead and Shadow relationships work for all objects with the runtime compatibility support. Backup You can make a backup of an Automation Server running the 1.3 SP1 or 1.3 SP2 version, with WorkStation and Enterprise Server running the 1.4.1 version. Log on to the Enterprise Server and then make a backup of the Automation Server running the 1.3 SP1 or 1.3 SP2 version. You can also log on directly to the Automation Server running the 1.3 SP1 or 1.3 SP2 version with WorkStation running the same 1.3 SP1 or 1.3 SP2 version, and then make a backup of the Automation Server.
View full article
Picard Product_Support
‎2018-09-11 08:32 AM

Labels:
  • EcoStruxure Building Operation
2379 Views

The Triac (V) outputs on the TAC Xenta 120-FC device goes ON, but never OFF

Issue The Triac (V) outputs on the TAC Xenta 120-FC device goes ON, but never OFF. In this case, it can open the valve, but the device could not close the valve. Environment TAC Xenta 121-FC TAC Xenta 121-HP Cause If the device is powered with 24 VDC, the Triac will not work properly. According to the datasheet, the TAC Xenta 121-device should always be powered by AC, not DC. Triac is an acronym for Triode for Alternating Current, and could only be working with AC power supply. Resolution Correct the power supply to the device to use AC, not DC.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1369 Views

Error 0x00001402 (Reached end of the list).

Issue A Plain English program is becoming disabled.  The controller error log logs the following error. 0x01402 (Reached end of the list). Environment Continuum Plain English Error b3 i2 Cause 0x00001402 (Reached end of the list) is a Plain English error.  This error most often occurs when a program is calling a Plain English Function that contains no byte code.. Resolution Edit each InfinityFunction in the controller to determine which function is empty (contains no programming).
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1702 Views

Why aren't the MSTP Devices coming in to SBO when upgrading site from Continuum?

Issue Some MSTP Devices show up when learned but other are not coming in. They worked fine on the Continuum install with the same MSTP network. Environment Automation Server Cause The AS has a maximum of 50 MSTP nodes and the b3 controllers that are not coming in are above this NodeId. Resolution Change the b3's NodeId's to a value below 50. 1. Use the Continuum system to change the Id by deleting the device object from the database, recreating it with the new NodeId. 2. Clear the controller to factory default.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • EcoStruxure Building Operation
908 Views

Bindings to PVB and PVR blocks are lost when upgrading AS.

Issue Bindings to PVB and PVR blocks in function block programs are lost after upgrading from 1.3 to 1.4.1. Environment StruxureWare Building Operation 1.4.1 Cause Text from Release notes for 1.4.1, page 38 10.2.2 Bindings to Public Variables and Public Constants in Function Blocks Bindings to Public Constants and Public Variables will be lost after upgrade from 1.3 to 1.4.1. The names of these Public Constants and Public Variables will be listed in the Conversion log produced by the 1.4.1 Device Administrator at the upgrade. Resolution After upgrade to 1.4.1 do the following: Locate the Public Constants and the Public Variables listed in the Conversion log. Select the Function Block Program that includes Public Constants or the Public Variables listed in the Conversion log and open the Edit Bindings View. Lost bindings will be displayed with: "Invalid- Variable not allowed to have a reference" Make a note of these bindings. Quit the Bindings View. Select and Edit the Function Block Program(s) that include the Public Constants or Public Variables, move a Function Block slightly to enable an insignificant change of the program to be discovered by the compiler. Save the Function Block program (the program then compiles again). Open the Binding View and re-bind the lost bindings. You will now also be able to select in which direction the value should be transferred. Save the bindings.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • EcoStruxure Building Operation
1280 Views

Function Block Editor does not open

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Function Block Editor does not open. Product Line EcoStruxure Building Operation Environment SmartStruxure Function Block Editor Cause There could be many reasons but in one of the case we found a malware called "sprotector.dll" somehow trying to hook into the Function Block Editor dll's. This malware is then crashing and prevents Function Block Editor from starting. SProtector.exe is typically added when you install another free software (video recording/streaming, download-managers or PDF creators) that had bundled into their installation this program. Resolution Reinstall this computer's Operating System completely, if that's not an option you can read more about how to remove "sprotector" here: http://malwaretips.com/blogs/sprotector-exe-virus-removal/
View full article
Picard Product_Support
‎2018-09-07 10:22 AM

Labels:
  • EcoStruxure Building Operation
1625 Views

What is the maximum number of pulses per minute a Xenta 411 I/O module can detect?

Issue How does the documented minimum pulse width translate into maximum pulses per minute? Environment All software/ firmware versions Cause The documentation defines the minimum pulse duration, not the number of pulses per minute. Resolution The documented 20ms min pulse duration for the Xenta 411 applies to both On and Off states. A complete min pulse cycle would be 20ms On + 20ms Off (50% Duty cycle), which equals 40ms. Therefore the max number of pulses per minute is 1000*60/40 = 1500 pulses/min or 25 pulses/ Second (25Hz).  
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1087 Views

All graphics are blank when opened on some PC's

Issue When a graphic is opened in WorkStation, the graphic work area is just white. If the mouse cursor is moved over the white area, it is possible that some objects will show. Environment Detected in SmartStruxure version 1.4.1 WorkStation Cause This is caused by an issue in the graphics card display driver. Resolution Update the graphics card display driver to the newest version. Sometimes you will need to refer to the manufacturer of the card, and not the manufacturer of the PC.
View full article
Picard Product_Support
‎2018-09-06 09:53 AM

Labels:
  • EcoStruxure Building Operation
1130 Views

Download option unavailable on MNL-800 controller in StruxureWare Building Operation

Issue The option to download the application to a MNL-800 controller is not available in StruxureWare Building Operation Workstation. Environment StruxureWare 1.1 or higher Cause For the download option to be available the MNL-800 version must be 2.0. Resolution There are two options to handle this issue: Upgrade the controller board to version 2.0 Treat the controller as a 3rd party LON device by importing the XIF file and handling the program in an external version of WorkPlace Tech.
View full article
Picard Product_Support
‎2018-09-06 09:53 AM

Labels:
  • EcoStruxure Building Operation
927 Views

I/NET to Building Operation Bindings

Issue Trouble with I/NET to Building Operation bindings. Site can bind an internal I/Net AO to a analogue value in Building Operation but the value won't update. Value appears with a blue triangle that says "unresolved".  Environment I/NET Seven together with StruxureWare Building Operation Cause I/NET points are integrated into Building Operation as points. When you upload the device configuration to the Enterprise Server, the configuration and point information are created in the System Tree pane. You edit and command the points as needed, using WorkStation and I/NET Seven editors. There are ten possible point types available in I/NET: Analog input (AI) Analog output (AO) Discrete input (DI) Discrete output (DO) Discrete alarm (DA) Discrete monitor (DM) Discrete control (DC) Digital input (GI) Digital output (GO) Pulsed input (PI) Resolution For any I/NET inputs (AI, DI, DM, GI and PI) it is only possible for operator changes to be made via the Building Operation Properties. It is not possible to programmatically control I/NET inputs and therefore not to be able to bind an output to an I/NET input point. It is also not possible to programmatically change any points Test state, any outputs (AO, DC, DO and GO) Manual state. And finally it is not possible to programmatically acknowledge an alarm. Therefore it is not possible to bind any script, schedule, FB, etc to any I/NET Points Test, Manual, Alarm Acknowledge or input point.
View full article
Picard Product_Support
‎2018-09-06 09:52 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1396 Views

Is it possible to acknowledge an alarm from a TGML graphic?

Issue Is it possible to acknowledge an alarm from a TGML graphic? Environment TGML graphics in StruxureWare Building Operation workstation and webstation. Cause Customers may wish to simplify the user interface and have a TGML graphic as the interface for all user operations. Resolution It is not possible to bind to an "acknowledge" attribute of an alarm from TGML, as this is not exposed. Our recommendation would be to use a panel and have an alarm pane in the panel as well as the graphic.
View full article
Picard Product_Support
‎2018-09-06 09:52 AM

Labels:
  • EcoStruxure Building Operation
1127 Views

DMO and SMO from SQL

Issue DMO and SMO from SQL Environment DMO and SMO from SQL Cause A site which was running I/NET and StruxureWare Building Operation, and as required, I/NET is running as a service. The SQL DMO caused an issue with I/NET running as a service and interrupted the INET service. What is SMO and DMO DMO is part of SQL 2005 backwards compatibility. Which has to be installed when going to SQL 2008 to allow the old I/NET database to be imported. With SQL 2008 they now use SMO instead of DMO. You cannot remove DMO without creating a new data base.  Resolution I/NET SQL interface is based on DMO (Distributed Management Objects) so it will not work with SMO (Server Management Objects). That is the reason the backward compatibility must be installed.  Sites that are using a 64 Bit Workstation and 64 bit SQL then there is a 64 bit backward compatibility that should be installed. The 64 bit BCM is in the Support folder on the original install CD called SQLBCM_64Bit.
View full article
Picard Product_Support
‎2018-09-06 09:51 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1337 Views

Unable to find Modbus device on RS-485 line under an Automation Server.

Issue Unable to find Modbus device on RS-485 line under an Automation Server. Environment Automation Server (AS) Modbus over serial line Cause Common wire is missing. Resolution Connect a common wire to the Shield connection on the COM port terminal
View full article
Picard Product_Support
‎2018-09-06 09:51 AM

Labels:
  • EcoStruxure Building Operation
1116 Views

Number of events in ES version 1.4.1?

Issue How many events can be saved in the Enterprise server version 1.4.1? Environment StruxureWare 1.4.1. Cause The number of events which could be saved in 1.4.0 was 200 000 which some customers have thought is too few. Resolution The number of events which can be saved in the ES version 1.4.1 is increased to 1,5 million.
View full article
Picard Product_Support
‎2018-09-06 09:51 AM

Labels:
  • EcoStruxure Building Operation
981 Views
  • « Previous
    • 1
    • …
    • 83
    • 84
    • 85
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of