Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1688 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 85
  • Next »
Label: "TAC IA Series" Show all articles

What is the difference between the MNL-V3RV3 and the MNL-V3RV3-A?

Issue What is the difference between the MNL-V3RV3 and the MNL-V3RV3-A? Environment  MNL-V3RV3 MNL-V3RV3-A Cause MNL-V3RV3-A is a new part number, and it isn't clear how it differs from the existing  MNL-V3RV3. Resolution The MNL-V3RV3-A meets the requirements of the Buy American Act (BAA).
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • TAC IA Series
1213 Views

The BDelay object from the LonWorks jar conversion library intermittently shows very large "remaining time" causing logic issues.

Issue The BDelay object from the LonWorks jar conversion library intermittently shows very large "remaining time" causing logic issues. Environment R2, UNC's Cause The BDelay object does not initialize the time remaining properly under some conditions. Resolution In the Lib jar - programObjects - hvac folder there is a program called DelayedOutput.sns.  This program can do the delayed on and off function but will need to be enhanced if the time remaining output is required.
View full article
Picard Product_Support
‎2018-09-06 10:20 AM

Labels:
  • TAC IA Series
929 Views

When the ENC is set up to pull weather data from the Enterprise Server the ENC's Application Director starts spewing out provisioning errors.

Issue When the ENC is set up to pull weather data from the Enterprise Server the ENC's Application Director starts spewing out provisioning errors. Environment I/A Series G3 Cause When set up to do this the ENC uses provisioningNiagara functionality and requires that module be present in the ENC Resolution Install the provisioningNiagara module in the ENC.
View full article
Picard Product_Support
‎2018-09-06 10:19 AM

Labels:
  • TAC IA Series
1241 Views

Is the Niagara G3 Floating License Repository (FLR) available for purchase?

Issue Is the Niagara G3 Floating License Repository (FLR) available for purchase? The FLR is a licensed feature that runs as a service in a Niagara station to provide licenses to other Niagara Runtime Environment (NRE) applications. Available licenses are 'leased' by authorized NRE applications at startup and 'returned' when the application shuts down. Environment Niagara G3 (version 3.5 and higher) Cause Field question Resolution The FLR was introduced with version 3.5 and discontinued shortly thereafter by Tridium. It is no longer available for purchase.
View full article
Picard Product_Support
‎2018-09-06 10:17 AM

Labels:
  • TAC IA Series
1005 Views

Which Modbus driver is required for I/A Series Niagara G3 ENC-520 to support Modbus TCP?

Issue Which Modbus driver is required for I/A Series Niagara G3 ENC-520 to support Modbus TCP? Environment I/A Series G3 ENC-520, JACE-645, JACE-6E, JACE-7, JACE-NXT, ENC-SW Cause Select the correct part number to enable the ENC to function as a Modbus TCP Client (Master) or Server (Slave).  Resolution ENC-DRV-MOD-T (ENC 520 acts as Modbus master (client) using Ethernet TCP) ENC-DRV-MOD-R (ENC 520 acts as Modbus server (slave) using Ethernet TCP) using Ethernet TCP master using Ethernet TCP
View full article
Picard Product_Support
‎2018-09-06 10:17 AM

Labels:
  • TAC IA Series
1379 Views

A MicroSmart controller is not communicating and the red watchdog timer (WDT) LED is on solid.

Issue A MicroSmart controller is not communicating and the red watchdog timer (WDT) LED is on solid. Environment DMS Cause Possible hardware issue or power issue Resolution Things to try: - Power cycle the controller - Verify it has a good earth ground and 24 Vac - Hardware clear the controller - Replace the line driver and disconnect the communications trunk - If it is a MSC-MPC, remove all modules.  If the WDT LED begins flashing normally, re-connect the modules one at a time until the WDT LED goes solid   On-board hardware issue.  Replace with another controller
View full article
Picard Product_Support
‎2018-09-06 10:16 AM

Labels:
  • TAC IA Series
1016 Views

Brought folders containing application drawings created in WPT 4.0 into a WorkPlace Tech 5.8 project and now getting two errors when opening drawings from a folder.

Issue Both errors indicate WorkPlace Tech cannot determine if the vsd file being opened is in the current project. Environment WorkPlace Tech Cause The names of the folders that were brought forward contained an apostrophe, i.e. Vav's, AHU's, etc. Resolution Rename the folders eliminating the apostrophe before bringing the folders\drawings into the new project and these errors will not occur.
View full article
Picard Product_Support
‎2018-09-06 10:16 AM

Labels:
  • TAC IA Series
854 Views

When a Niagara G3 server license gets de-activated (i.e. replaced), does the jobsite server station stop working?

Issue An existing Niagara G3 server is being replaced with new hardware.  The new server is being configured while the existing server continues to operate the station.  A replacement license has been provided for the new server with a new hostId.  The license for the existing server has been de-activated by Tridium.  Will the existing server continue to function even though its license has been de-activated?  Note:  The existing server has an Internet connection. Environment Niagara G3 Cause PC hardware replacement Resolution The existing server will continue to run the station.  The license remains active as long as there is no web-based license update performed.
View full article
Picard Product_Support
‎2018-09-06 10:15 AM

Labels:
  • TAC IA Series
1102 Views

Does the JACE-645 come with 128 MB or 256 MB like the ENC-520?

Issue Does the JACE-645 come with 128 MB or 256 MB like the ENC-520? Environment I/A Series, JACE-603/645 Cause Not sure what it comes with after reviewing announcement PA-251. Resolution A JACE-603 or JACE-645 comes standard with 128 MB of RAM with the option to upgrade to 256 MB.  The part number for the optional memory upgrade is TRD-NPM-256. This part number modifies the license which enables the factory-installed memory (license line:  maxHeap=true).
View full article
Picard Product_Support
‎2018-09-06 10:15 AM

Labels:
  • TAC IA Series
1087 Views

When moving files to a new PC user can no longer edit them

Issue User has a backup of my files that they have restored onto a new workstation PC but now they are unable to edit the files.  For example: A Continuum graphic needs to be edited and cannot save changes but can save as a new graphic. Environment Window OS Windows XP Windows 7 8 8.1 10 Windows Vista Cause This is caused by Microsoft Windows OS. Windows will automatically make a file "Read only" if it has been moved from another PC  Resolution The solution is to change the files back to read / write. Example: Open Windows Explorer and find the folder you want to change, for this example it is "Continuum graphics." Right click on the folder and select properties, which shows a tab that will be ticked next to "read only" deselect this tab and then select apply. Once windows has finished changing the folder and its contents to read/write the user will be able to go into continuum and edit graphics.
View full article
Picard Product_Support
‎2018-09-06 10:14 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1324 Views

Are lnml files required to remain with the Niagara G3 station?

Issue The LON XML tool was used to create a lnml file.  Does it need to remain with the station at all times? Environment Niagara G3 Cause General database housekeeping Resolution Once the LON controller has been imported, the lnml file is no longer required and can be removed. Note:  If the LON controller's profile changes slightly (i.e. one or two SNVTs), a Learn Nv is sufficient to update the device in the station.  The Learn Nv command will not execute unless the reference to the lnml file is removed.
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Labels:
  • TAC IA Series
1326 Views

Integration to CAN bus protocol

Issue Integration to CAN bus protocol Environment I/A Series R2 I/A Series G3 Cause There is a need to integrate to devices where the available communications protocol is CAN bus.  Resolution I/A Series does not have a driver for CAN bus protocol. A third party converter / gateway can be used to convert CAN bus to a standard protocol available in I/A Series.  The following company was found after a search on the Internet. They offer solution for CAN bus to various communications protocols. http://www.adfweb.com/home/default.asp http://www.adfweb.com/home/about/about.asp   Note: Please note Schneider Electric do not endorse this product but provide this option as a workable solution. All support issues related to these products should be sent directly to their support centers.
View full article
Picard Product_Support
‎2018-09-11 04:41 AM

Labels:
  • TAC IA Series
1819 Views

The suggested Belkin Bluetooth adapter is obsolete. Is there a suggested replacement for use with RoamIA?

Issue The suggested Belkin Bluetooth adapter is obsolete.  Is there a suggested replacement for use with RoamIA? Environment Roam IA BACnet MSTP communications Cause The suggested Belkin adapter is no longer available. Resolution Two alternates have been found to function well with the RoamIA; they are the AZIO BTD-V400 and SMK VP-6495.  Both of these devices are very compact and use Bluetooth v4.0 technology.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • TAC IA Series
1297 Views

How long will it take for a MNB controller to drop to 'Read-Only' mode when the AC power supply voltage drops below 20.4 Vac?

Issue How long will it take for a MNB controller to drop to 'Read-Only' mode when the AC power supply voltage drops below 20.4 Vac? Environment MNB controllers Cause Site installation using one AC transformer for multiple controllers.  Site is also suffering brownout conditions. Resolution Factory testing confirms that it takes only one AC cycle of power (i.e. one complete sine wave) of voltage below 20.4 Vac for the controller to drop into 'Read-Only' mode. It is difficult to view with a standard digital multimeter.  A scope may be required to capture the voltage dip.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Labels:
  • TAC IA Series
1068 Views

Do the Jace-6 or Jace-7 need multiple Modbus drivers if more than one port is used?

Issue The jobsite will eventually have 4 RS-485 trunks each communicating Modbus.  Two option cards have been ordered with the Jace (part# TRD-NPB-2X-485). Does each port on the option cards need a separate Modbus driver purchased for each? Environment Niagara G3 Cause Ordering/licensing clarification Resolution Purchasing one Modbus driver (part# ENC-DRV-MOD) will cover all ports used for Modbus on the Jace-6/7.
View full article
Picard Product_Support
‎2018-09-06 10:10 AM

Labels:
  • TAC IA Series
1362 Views

The error messages "LogService.archive: SQL Exception: Container 1,342,197,790,972 not found." and "Close pooled Connection" is displayed in the Standard ou...

Issue The Enterprise Server’s archives are not updating and the following message is displayed in the Standard Output Window:      ERROR: LogService.archive: SQL Exception: Container 1,342,197,790,972 not found.      ERROR: LogService.archive: Force close of Connection!      WARNING: Closed Pooled connection [ConnectionPool]      ERROR: XSCH1: Container 1,342,197,790,972 not found.   Environment Niagara R2 Enterprise Server – all versions Cause The “SQL Exception” error and “Closed pooled connection” warning appears to indicate a corruption within the Cloudscape SQL database. Resolution In this instance, the app folder became corrupt when copied between builds during an upgrade.  The original app folder was simply recopied. The second copy of the app folder copied without errors.   The following would apply in instances were the original app folder is corrupt:  First, try and recover the Cloudscape database and repair the corruption using the console and the dbadmin command.  After stopping the station, open the console and run the command at the prompt:            dbadmin >  recover  The software will search through the Cloudscape SQL database and attempt to clear the errors and recover the database.  If this is unsuccessful, you may have to remove the APP folder from the station and start over.    To remove the Enterprise Server’s app folder: Stop the server’s database and delete its app folder.  A new app folder will be created when the server is restarted.    Note: All archived information will be lost when the app folder is deleted.          
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • TAC IA Series
1339 Views

Is there a replacement RJ-11 to BACnet MSTP cable for I/A Series Roam IA?

Issue Is there a replacement RJ-11 to BACnet MSTP cable for I/A Series Roam IA? Environment Roam IA, MNB-ROAM-IA Cause Need to replace cable. Resolution The part number for the replacement RJ-11 to BACnet MSTP cable for Roam IA is MNB-ROAM-CBL.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • TAC IA Series
1088 Views

The message "Unsupported Unconfirmed service" is displayed in the Standard output Window of an UNC-520.

Issue The message “Unsupported Unconfirmed service” is displayed in the Standard output Window of an UNC-520. Environment Niagara G3, R2, UNC-520, ENC-520 Cause Some manufactures’ BACnet controllers use unconfirmed service which the UNC/ENC does not handle so they are ignored by the UNC/ENC. Resolution These are nuisance messages which cause no issues. The messages can be ignored.
View full article
Picard Product_Support
‎2018-09-06 10:08 AM

Labels:
  • TAC IA Series
1188 Views

Vykon Alarm Services client, no sound on alarm popup

Issue Using Vykon Alarm Services no sound is played on alarm popup, sound is enabled in both server and clients. Default sound is enabled and valid (operates in Windows when tested) and same for object level alarm sound. Have entered object level alarming parameters with pipe symbol, sc and tag in alarm text but even the default global sound doesn't work Environment Niagara R2 Vykon Alarm Client Cause The Vykon Alrm Client only supports wav files in standard PCM format, wav files that use compression codecs (e.g. mpeg3, etc.) do not work. Resolution Right click on the sound files and view the properties. The summary tab typically indicates the audio format. (for information on audio formats see http://en.wikipedia.org/wiki/Audio_file_format)  There are free utilities such as Moo0 Audio Converter that can be used to convert audio file formats
View full article
Picard Product_Support
‎2018-09-11 05:04 AM

Labels:
  • TAC IA Series
1477 Views

Getting Error: Class ID error when starting WorkPlace Tech.

Issue Getting Error: Class ID error when starting WorkPlace Tech. Environment WorkPlace Tech installation Cause The error indicates WorkPlace Tech is having problems working with RTMonitor. Resolution Remove the newest LDV driver first then the older ones and then uninstall and reinstall WPT. During the install WPT will load the LDV driver it requires.  
View full article
Picard Product_Support
‎2018-09-06 10:06 AM

Labels:
  • TAC IA Series
1371 Views
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 85
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore