Are lnml files required to remain with the Niagara G3 station?
  • Are lnml files required to remain with the Niagara G3 station?
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 10:13 AM
The LON XML tool was used to create a lnml file.  Does it need to remain with the station at all times?
Niagara G3
General database housekeeping
Once the LON controller has been imported, the lnml file is no longer required and can be removed.
Note:  If the LON controller's profile changes slightly (i.e. one or two SNVTs), a Learn Nv is sufficient to update the device in the station.  The Learn Nv command will not execute unless the reference to the lnml file is removed.