Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,825
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1849 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 53
    • 54
    • 55
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

"Authentication Failed. Could not connect to ES." when setting the password for the "SystemReportsService" user.

Issue Getting authentication failure when trying to set to password for "SystemReportsService" through "Building Operation WebReports Administrator" Environment Web Reports 1.6.0 RC and above Cause The Reports Agent can't check the password with the ES. This is dues to one of the three causes below: [1] The Enterprise Server path is not correct [2] The HTTP port entered for the reports agent is not correct [3] The ES is not started [4] The password entered is not correct [5] The reports agent is not started [6] The "Local System" account does not have high enough privileges to communicate out of the server Resolution [1] Enter the right ES server path e.g. using "SBO Reports Agent Config" [2] Enter the same port in HTTP in the ES Software Adminsitrator and the reports agent e.g. using "SBO Reports Agent Config" [3] Start the ES [4] Enter the correct password (you can change the defined password for the "SystemReportsService" through Workstation) Be sure to use the SystemReportsService account in the local domain of the ES [5] Start the reports agent [6] Change the report agent service to run under a local administrator account
View full article
Picard Product_Support
‎2018-09-11 01:07 PM

Labels:
  • EcoStruxure Building Operation
1744 Views

Testing SNMP alarms

Issue There is no full end to end description on how to test SNMP alarms in SmartStruxure 1.6.1 and later Product Line EcoStruxure Building Operation Environment SNMP Alarms Cause Only a guide on how to create the SNMP alarms is available, but there is no guide available on how to test them. For general information regarding SNMP traps, refer to the following Web Help links: Versions 1.6 and 1.7 SNMP Notification Properties Create SNMP Notification Wizard – SNMP Notification Page SNMP Notification View Version 1.8 and later SNMP Notification Distribution Method Create Notification Wizard - Configure SNMP Page Resolution Download and install "MIB Browser" from iReasoning Download the mib file for SmartStruxure Load the SmartStruxure mib file into the MIB Browser through "File"-->"Load MIBs", and select the SmartStruxure mib file Create a simple alarm in SmartStruxure and make it trigger on a digital point Create a SNMP notification with the following settings. To get to the conditions/filter, open (double click on it or hit enter) the SNMP notification. Only showing the properties of it will not show the filter settings. "Address" is the address of the SNMP manager that receives the SNMP notification, in this test "localhost" since the SNMP manager is installed locally. "User name" is the user name of the user on the SNMP manager that receives the notification. In filter settings, select normal and alarm state, and add "Source server = *" as a condition In the MIB browser, select "Tools"-->"Trap Receiver" Trigger the alarm in SmartStruxure An alarm will now be seen in the MIB browsers trap receiver window
View full article
Picard Product_Support
‎2018-09-11 01:04 PM

Labels:
  • EcoStruxure Building Operation
6536 Views

Export special does not save output bindings

Issue After performing an Export special of an object in SmartStruxure and then importing it into a database, the output bindings of the object are no longer there. Environment Export and Import Workstation Automation Server Enterprise Server Cause Performing an export special and then importing that xml file into another database or the same database after the object has been deleted will no longer have the output bindings of that object. Resolution This behavior functions as designed. See Section 20.31 of the StruxureWare Building Operation: Technical Reference Guide. The documentation states that: "Objects or properties with bindings where the bound objects are in separate import files. To preserve bindings during an import, import the references objects to the targeted server prior to importing the actual objects or programs that refer to these objects. For example, import any referenced I/O points before importing the programs that read and write the I/O points. No matter what order of import is used, the import process will restore the bindings if they are valid at the time of import."
View full article
Picard Product_Support
‎2018-09-11 01:03 PM

Labels:
  • EcoStruxure Building Operation
1649 Views

Web page is not displayed when trying to access Webstation using HTTP

Issue When trying to access Webstation, even on the local PC, using HTTP, the web page is not displayed. You get one of the following messages Internet Explorer 8 Internet Explorer 11 Chrome FireFox Environment Webstation Cause HTTP can be disabled so only HTTPS will work Resolution Make sure to untick the checkbox in security settings for the ES or AS in question SmartStruxure 1.5 SmartStruxure 1.6
View full article
Picard Product_Support
‎2018-09-11 01:15 PM

Labels:
  • EcoStruxure Building Operation
1271 Views

What is the Default Output Value on an IO Output

Issue When is the Default Output Value applied to an IO Output? Environment AS IO Modules Cause When the AS is disconnected it does not appear to go straight to the Default value. Resolution When an IO Module becomes disconnected from its AS or the AS is unplugged, after 255 Seconds (4.25 Minutes) the IO Outputs will change from the last controlled value to the Default Output Value. When the AS is reconnected (and starts up) the outputs will revert to normal control. "Default Output Value" is an attribute of the output point and is found in the: "Properties, Configuration Settings", this is where you can define its value.
View full article
Picard Product_Support
‎2018-09-11 01:15 PM

Labels:
  • EcoStruxure Building Operation
1247 Views

When trying to select meters in Building Operation QT Administrator a 'User is not authorised to access' message appears and a log list cannot be retrieved.

Issue When trying to select meters in Building Operation QT Administrator a 'User is not authorised to access' message appears and a log list cannot be retrieved. Environment StruxureWare Building Operation Building Operation QT Administrator Cause This is most likely caused by an incorrect trend log configuration.  Either: - One or more extended trend logs are not configured with a trend log. or - One or more trend logs are not monitoring a point. Resolution Correct the configuration and retry.
View full article
Picard Product_Support
‎2018-09-11 01:13 PM

Labels:
  • EcoStruxure Building Operation
1182 Views

Binding in Script program disappear

Issue If a binding variable is commended out in the program when the line is put back the binding is gone. Consider the following program... TheOUT3 binding variable is commented out... If the comment is removed and the line restored, the corresponding binding is NOT restored. Environment Workstation Script Cause Documentation Resolution This is functioning as designed, if the binding variable is removed in the program code, the associated binding is removed to avoid leaving an orphan binding. When the comment is removed and the binding variable is put back, you will need to re-bind it as SBO does not keep track of deleted bindings and can't automatically restore it.
View full article
Picard Product_Support
‎2018-09-11 01:34 PM

Labels:
  • EcoStruxure Building Operation
1671 Views

Schedule Exception in SmartStruxure not functioning.

Issue Necessary settings must be made to enable the SBO Exception Shedule Environment Exceptions in an SBO Schedule Cause Incorect settings on the Exeption Schedule Resolution   Adding a "Holiday Calendar" reference as an Exception to a schedule, an initial value of zero and "no end time" must be checked by editing the green area shown in the example below.
View full article
Picard Product_Support
‎2018-09-11 01:39 PM

Labels:
  • EcoStruxure Building Operation
1242 Views

How to use the HTML5 Viewer in SmartStruxure WebStation

Issue How to enable and use the HTML5 Viewer instead of the Java Viewer in SmartStruxure WebStation Product Line EcoStruxure Building Operation Environment WebStation Cause Starting with SmartStruxure WebStation 1.6.0 there are HTML5 viewers available for both graphics and trends. However, the Java viewer is the default so the HTML5 viewer must be enabled. Resolution Note: As of WebStation version 1.6.0, the HTML5 viewers are still in beta and still have some compatibility issues. To use the HTML5 viewers take the following steps: Log into WebStation On the upper right-hand side click on Settings Check the Use HTML5 viewers option
View full article
Picard Product_Support
‎2018-09-06 09:16 AM

Labels:
  • EcoStruxure Building Operation
1398 Views

How to search for all b3 analog inputs that are Out of Service.

Issue Need a quick way to find all the analog inputs under all the b3s in the system that are out of service. Environment Workstation Enterprise Server Automation Server b3s Cause Documentation Resolution Create a Search object at the ES or AS level and configure as follows...   In this example the search object is in the ES and it will search for b3 inputs in all of the Automation Servers under the ES.   The search can easily be modified to search for other types of objects that are out of service by changing the class filter.
View full article
Picard Product_Support
‎2018-09-11 01:50 PM

Labels:
  • EcoStruxure Building Operation
1149 Views

A huge number of BACnet Alarms stating Duplicate network identifier are being generated

Issue A huge number of BACnet Alarms stating Duplicate network identifier are being generated Environment BACnet Cause This has been seen when two Continuum bCX1-4040 units were inadvertantly connected together on to a single MSTP network Resolution Correct the wiring, restart the Enterprise Server and the alarms stop
View full article
Picard Product_Support
‎2018-09-06 09:16 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1529 Views

WorkPlace Tech Editor list of applications is empty or some are missing

Issue When opening the WorkPlace Tech Editor in Workstation the list of Applications is empty or some of the applications are missing. Product Line EcoStruxure Building Operation Environment WorkStation 1.5.0 and up Cause Buffer overflow condition Resolution When this condition occurs; with the Application list displayed hold down the ALT key and click on the refresh icon This will bring up the following information message. Due to a buffer overflow, the System Tree has been collapsed and your unsaved changes have been reverted back to what is currently saved in the server. To navigate to objects again, expand the tree as needed. Click OK and the Application list will be reloaded from the AS and all existing application files will be displayed .
View full article
Picard Product_Support
‎2018-09-11 01:34 PM

Labels:
  • EcoStruxure Building Operation
1419 Views

Untranslated infinity error when creating object in b3 or i2 device.

Issue Untranslated infinity error when creating object in b3 or i2 device. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Infinet i2 Controller BACnet b3 Controller Cause b3/i2 devices do not support certain characters in their objects name. Resolution b3/i2 devices do not support certain characters in their objects name. For example, creating an analog input using the name AI-1 will cause the error is the BACnet field is left blank, the EBO name AI-1 can be used but a name needs to be specified in the BACnet name field that is consistent with the b3 naming convention such as AI_1.
View full article
Picard Product_Support
‎2018-09-11 01:39 PM

Labels:
  • EcoStruxure Building Operation
3043 Views

Understanding IO Sourcing versus Sinking

Issue What are the sourcing and sinking specifications of the analog voltage outputs on the different controllers? Product Line Andover Continuum, EcoStruxure Building Operation Environment i2 b3 XP IO modules Cause Sourcing and sinking refer to the ability of a DC circuit to PUSH or PULL a direct current through the circuit. Resolution Voltage Sourcing In a controller's voltage sourcing output, the output provides a voltage source that PUSHES a direct current through the load as indicated in the illustration below. The current flows from the output's positive (V/+) terminal through the load to the output's negative terminal (-/ RTN). Current Sinking In the illustration below, a controller's voltage output is sinking a current from the load. Note the voltage source in the load's circuit which is at 15 VDC. Because current always flows from positive to negative, the voltage coming from the controller's output (0 - 10 VDC) will ALWAYS be more negative than the load's source of 15VDC, thus a current will flow from the load's voltage source through the controller's output circuit to reach the negative (RTN) side of the output's circuit. The lower the voltage coming out of the controller's output the more negative it will be as compared to the load's voltage source, thus the output will be sinking the most current when it has a value of 0 volts. It is extremely important when using a controller's voltage output in a way that will make it sink current to know the maximum amount of current the output will be sinking and to ensure it does not exceed the current sinking capacity of the controller's output. The following table shows the sourcing and sinking capabilities of the voltage outputs of the different controllers. CONTROLLER VOLTAGE SOURCING CURRENT SINKING COMMENT i2/b3 814 Voltage output 0-10 V @5 ma max 1 ma max Exceeding the 1 mA sink limit will cause the IO readings to be incorrect. ie, inputs may read 999.99
View full article
Picard Product_Support
‎2018-09-11 01:37 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
3228 Views

Warning when importing XIF file generated by XBuilder

Issue When importing a XIF file generated by XBuilder a warning (that might look like it's an error) is shown regarding missing file name and generated date Environment SmartStruxure Xenta Server XBuilder Cause The XIF file generated by XBuilder doesn't completely follow the LONMARK Device Interface File Reference Guide Resolution The warning can be disregarded, but the XIF file can easily be altered to avoid getting the warning if desired Open the XIF in notepad or similar editor, and change the following. Note the colon before the filename. Original XIF header File generated by TAC XBuilder version 5.1.9, XIF Version 4 Copyright (c) 2000 by TAC AB All Rights Reserved. Run on 0000-00-00 00:00 Changed XIF header File: X913.xif generated by TAC XBuilder version 5.1.9, XIF Version 4 Copyright (c) 2000 by TAC AB All Rights Reserved. Run on Mon Nov 03 08:00:00 2014 File generated by TAC XBuilder version 5.1.9, XIF Version 4 Copyright (c) 2000 by TAC AB All Rights Reserved. Run on 0000-00-00 00:00File generated by TAC XBuilder version 5.1.9, XIF Version 4 Copyright (c) 2000 by TAC AB All Rights Reserved. Run on 0000-00-00 00:00
View full article
Picard Product_Support
‎2018-09-11 01:54 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1286 Views

How to use the set point functionality of the ETR50x temperature sensor

Issue Need help configuring ETR501/ETR503 setpoint feature. Product Line EcoStruxure Building Operation Environment AS IO b3 Cause The ETR50x Series sensors support a slider that can be used by the occupants to change the temperature setpoint of the controlled space. Resolution SENSOR CONNECTED TO AS IO MODULE Create a resistive input on an IO module such as the UI16 and wire the slider from the ETR50x unit to the resistive input on the IO module. Move the slider all the way to the left and take note of the value reading at the input. Move the slider all the way to the right and take note of the value reading at the input. Configure the input's conversion using the values noted from steps 2 and 3 as the bottom and top of the electrical scale (see screen shot below) Use desired setpoint values for the top and bottom of the engineering scale, in the example below the slider will allow changing the setpoint between 68 and 78, note that the units has been set to degrees F for readability. Heating/cooling application such as a PE Script can now use the value of the input as the setpoint. SENSOR CONNECTED TO b3 INPUT Same as above except that the input should be configured for VOLTAGE since the b3s do not support resistive inputs.
View full article
Picard Product_Support
‎2018-09-11 01:48 PM

Labels:
  • EcoStruxure Building Operation
1536 Views

Change the subnet/node and domain for an AS?

Issue Is it possible to change the subnet/node and domain for the Lon network in an AS? Environment StruxureWare Building Operation 1.5 and previous Cause The subnet/node for an AS is hardcoded Resolution No Subnet/node is not possible to change for an AS. But the Domain is possible to change.
View full article
Picard Product_Support
‎2018-09-11 01:47 PM

Labels:
  • EcoStruxure Building Operation
1310 Views

Difference in SmartStruxure Backplanes for Power Supply and Automation Server Modules

Issue In rare occurrences, technicians may remove the bottom terminal from the AS or I/O Baseplate so that a power supply can fit. The backplanes inside the baseplates are not all the same and this will not work. Visually determine which baseplate is for each module. Product Line EcoStruxure Building Operation Environment SmartStruxure Power Supply SmartStruxure Automation Server SmartStruxure I/O module Cause Incorrect baseplate will not work on the SmartStruxure modules. Resolution See picture for representation of Power Supply backplane, the other configuration is for Automation Server (and I/O modules). For more detailed information please see the Hardware Reference Guide.
View full article
Picard Product_Support
‎2018-09-11 01:48 PM

Labels:
  • EcoStruxure Building Operation
1241 Views

Unknown Exception when opening a project in Workstation for Projects

Issue When opening a project in Workstation for Projects, Unkown Exception error will pop up Environment SmartStruxure 1.5 Workstation for Project PCS Cause This is a defect for SmartStruxure 1.5. When there is no Internet connection on this computer, this error will happen. Resolution This issue will be fixed in SmartStruxure 1.6. Currently the workaround is to obtain the Internet connection for this computer, at least when opening the project. It should be OK to remove the Internet connection after the project is opened.
View full article
Picard Product_Support
‎2018-09-11 01:46 PM

Labels:
  • EcoStruxure Building Operation
1406 Views

STR-150 Calibration Feature

Issue In the past there was no way to calibrate the space temperature from a STR-150 when used with a Xenta 121 FC/HP.  Environment STR-150 Xenta 104A Xenta 120 Xenta Programmables Cause Any calibration applied to the temperature of a STR-150 had to be done downstream of the stat in the controller. In the past when the STR-150 room stat was wired up to a Xenta 121 there was no way to calibrate the space temperature as the Xenta 121 FC/HP had no kind of Temp Offset in the controller. Resolution Starting with version 1.4 (released September 2013) of the STR-150, there is a calibration feature built into the stat. This feature allows the calibration to be applied before the temperature is sent down to the controller (Example: Xenta 121 controller). Below you can find out how to check the version number of the stat and how to perform the calibration. There is not a way to upgrade older versions of the STR-150 to 1.4 or greater. Checking the STR-150 version number The version number of the stat can be found as parameter P0. View version: Push the fan and bypass button simultaneously for 2 seconds to display P0. The version number will be displayed here. Using the STR-150 Calibration Feature Enter Configuration: Push the fan and bypass button simultaneously for 2 seconds to enter P0.   In P0, hold down the bypass button and push the fan button three times to enter configuration mode. Note: the wrench symbol is lit when the STR-150 is in configuration mode.   In Configuration Mode: Press the fan button repeatedly until you reach parameter F0. Note: The two digits farthest to the left on the display show the parameter, while the two digits farthest to the right show the value.   Use the increase or decrease button to adjust the value. The offset scale ranges from 0-99 which corresponds to -5.0 to +4.9 degrees. If the STR-150 is setup for degrees C, then the offset is exact. If the STR-150 is setup for degrees F, then the offset is recalculated to a corresponding value.   Exit Configuration Mode: Push the fan and bypass button simultaneously for 2 seconds or allow the idle timeout to exit configuration mode on its own.
View full article
Picard Product_Support
‎2018-09-11 01:53 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2167 Views
  • « Previous
    • 1
    • …
    • 53
    • 54
    • 55
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of