Issue
In the past there was no way to calibrate the space temperature from a STR-150 when used with a Xenta 121 FC/HP.
Environment
- STR-150
- Xenta 104A
- Xenta 120
- Xenta Programmables
Cause
Any calibration applied to the temperature of a STR-150 had to be done downstream of the stat in the controller. In the past when the STR-150 room stat was wired up to a Xenta 121 there was no way to calibrate the space temperature as the Xenta 121 FC/HP had no kind of Temp Offset in the controller.
Resolution
Starting with version 1.4 (released September 2013) of the STR-150, there is a calibration feature built into the stat. This feature allows the calibration to be applied before the temperature is sent down to the controller (Example: Xenta 121 controller). Below you can find out how to check the version number of the stat and how to perform the calibration.
There is not a way to upgrade older versions of the STR-150 to 1.4 or greater.
Checking the STR-150 version number
The version number of the stat can be found as parameter P0.
-
View version:
-
Push the fan and bypass button simultaneously for 2 seconds to display P0.
- The version number will be displayed here.
-
Push the fan and bypass button simultaneously for 2 seconds to display P0.
Using the STR-150 Calibration Feature
-
Enter Configuration:
-
Push the fan and bypass button simultaneously for 2 seconds to enter P0.
-
In P0, hold down the bypass button and push the fan button three times to enter configuration mode.
Note: the wrench symbol is lit when the STR-150 is in configuration mode.
-
Push the fan and bypass button simultaneously for 2 seconds to enter P0.
-
In Configuration Mode:
-
Press the fan button repeatedly until you reach parameter F0.
Note: The two digits farthest to the left on the display show the parameter, while the two digits farthest to the right show the value.
-
Use the increase or decrease button to adjust the value. The offset scale ranges from 0-99 which corresponds to -5.0 to +4.9 degrees. If the STR-150 is setup for degrees C, then the offset is exact. If the STR-150 is setup for degrees F, then the offset is recalculated to a corresponding value.
-
Press the fan button repeatedly until you reach parameter F0.
-
Exit Configuration Mode:
- Push the fan and bypass button simultaneously for 2 seconds or allow the idle timeout to exit configuration mode on its own.