Issue
A huge number of BACnet Alarms stating Duplicate network identifier are being generated
Environment
BACnet
Cause
This has been seen when two Continuum bCX1-4040 units were inadvertantly connected together on to a single MSTP network
Resolution
Correct the wiring, restart the Enterprise Server and the alarms stop