Issue
Untranslated infinity error when creating object in b3 or i2 device.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Workstation
- Infinet i2 Controller
- BACnet b3 Controller
Cause
b3/i2 devices do not support certain characters in their objects name.
Resolution
b3/i2 devices do not support certain characters in their objects name.
For example, creating an analog input using the name AI-1 will cause the error is the BACnet field is left blank, the EBO name AI-1 can be used but a name needs to be specified in the BACnet name field that is consistent with the b3 naming convention such as AI_1.