Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,899
  • TAC IA Series 1,682
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 453
    • 454
    • 455
    • …
    • 500
  • Next »

How to change the domain on a lonworks network in classic scenario

Issue How to change the domain on a lonworks network in classic scenario Environment TAC Vista Cause want to change the domain on the network Resolution Right click on the network and select properties Click on the domain tab Change the domain and click ok, NOTE you have to use capital letters.
View full article
Picard Product_Support
‎2018-09-06 10:48 AM

Labels:
  • TAC Vista
1459 Views

Can't find my controller firmware version on the Exchange Online.

Issue Can't find my controller firmware version on the Exchange Online. Controller firmware version has a very high number (1.2009921 instead of 1.2000021) Environment All CX controllers All b3 devices All i2 Infinet controllers Cause Beta version R&D produces special beta versions of the firmware to address specific issues found in the field, these beta versions are identified by the insertion of a high digit in the drop part of the version number (typically a 5, 7 or 9). Typical beta version of NC2 might look like 2.009044 or 2.107033 Resolution Beta versions are sent out on a per case basis and are not posted to the Extranet. Any fix or fixes addressed in a beta version is then included in the next release of the firmware following rigorous regression testing by the SQA department.
View full article
Picard Product_Support
‎2018-09-06 10:48 AM

Labels:
  • Andover Continuum
1601 Views

Is there a limit to how much CPU power the graphics editor can utilise?

Issue Is there a limit to how much CPU power the graphics editor can utilise? Environment Tac Vista 5.1.X Graphics Editor TGML  Cause The graphics editor appears to be limited to a maximum of 25% CPU usage, which means that some heavy operations take a long time. Resolution There is no limit to how much CPU graphics editor can utilise. However each thread can only use 100% of each CPU core, so a quad-core CPU would allow for a maxim of 25% total CPU usage per thread.
View full article
Picard Product_Support
‎2018-09-06 10:48 AM

Labels:
  • TAC Vista
1392 Views

Is there any way to segregate the IP level BACnet devices under the 'BACnet Devices' folder in CyberStation?

Issue Site has many IP level BACnet devices from different vendors and want to separate them into different folders. Environment CyberStation Cause Documentation Resolution Unfortunately there is no way to segregate the IP level BACnet devices in CyberStation. The 'BACnet Devices' container is managed by the system and the user is not allowed to create or move  folders under it.
View full article
Picard Product_Support
‎2018-09-06 10:48 AM

Labels:
  • Andover Continuum
1215 Views

Continuum AlarmDelay operation

Issue Alarm generated before the specified alarm delay time. Product Line Andover Continuum Environment CyberStation All master CXs All field devices. Cause If at the end of the alarm delay time the point is still in alarm, Continuum will generate the alarm notification regardless of how many times the point has been in the "return to normal" (RTN) state during the delay period. Resolution Example: Alarm configured with a 60 second delay, point goes in to alarm and the delay timer starts. 45 seconds later the point goes to RTN and then 5 seconds later goes back into alarm. 10 seconds later when the alarm delay ends, the firmware checks the alarm status of the point and finds that it is in alarm. It then sends out an alarm notification to the CyberStation. On the contrary, if the point is not in alarm at the end of the delay period, then a new 60 second delay will be started next time the point goes in to alarm.
View full article
Picard Product_Support
‎2018-09-06 10:48 AM

Labels:
  • Andover Continuum
1435 Views

What XML tags can be used with the Email and Paging format files to customize the Alarm Email messages?

Issue What XML tags can be used with the Email and Paging format files to customize the Alarm Email messages? Environment Continuum Cause Not sure what attributes of the alarm can be used and displayed in the Alarm Email message being sent out. Resolution This can also be found in the Online Help file under the help Index topic "Preferences for Device Attributes". This shows the preference options to select the email format files and the XML tags that can be used in those files. The list of tags is below. XML Tag Description <\date> The date of the alarm. For example: Friday, October 9, 2009. <\time> The time of the alarm. For example: 4:37:59 pm. <\name> The name of the object that generated the alarm. <\value> The current value of the alarm. For example: 190.00 <\state> The state of the alarm. Values can be : Alarm, Return to Normal, Acknowledged, or Fault. <\priority> The current priority of the alarm. <\type> The type of alarm that was triggered. <\message> The text message of the alarm. This is the message that is entered in the Text Message field on the Feedback tab of the AlarmEnrollment Editor. <\eventnotification> The name of the event notification for this alarm. <\operatortext> The operator text for this alarm (set by those who acknowledged this event). <\useractions> The user actions for this event. <\acknowledgedby> The user name of the person who acknowledged this event. <\acknowledgeddatetime> The date and time of this acknowledgement. <\silencedby> The user name of the person who silenced this event. <\silenceddatetime> The date and time of this silence event.
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • Andover Continuum
1225 Views

Can't find third party (Carel) BACnet gateways

Issue Two Carel BACnet gateways, when connected to the MSTP one at a time then doing 'Find BACnet devices' they show up under the BACnet folder but if connected together they do not. Environment CyberStation bCX4040 Cause Continuum enhanced MSTP mode is interfering. Resolution Disable Continuum enhanced MSTP mode.
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • Andover Continuum
1658 Views

Does the I/A Series G3 Enterprise Network Server (ENS-1) software support clustering or able to interface with the SQL cluster?

Issue Does the I/A Series G3 Enterprise Network Server (ENS-1) software support clustering or able to interface with the SQL cluster? Environment I/A Series G3 Enterprise Network Server (ENS-1) Cause Clusters are a set of computers operating together as one unit.  Load-balancing clusters are configurations in which cluster-nodes share computational workload to provide better overall performance.  The activities of the computing nodes are orchestrated by clustering middleware, a software layer that sits atop the nodes and allows the users to treat the cluster as by and large one cohesive computing unit. Resolution The I/A Series G3 Enterprise Network Server (ENS-1) software does not support clustering.  The software does not provide capability for load balancing nor can it interface to a SQL cluster scenario.
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • TAC IA Series
1271 Views

CyberStation not getting BACnet alarms

Issue A CyberStation is getting Infinity alarms but not BACnet alarms. Environment CyberStation bCX4040 b3s Cause BACnet routing information not available due to missing or incorrect BBMD configuration Resolution Configure a BBMD in the sub-net where the workstation is located.
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • Andover Continuum
1418 Views

"Invalid card number" error when Importing custom format personnel records.

Issue When importing custom format card records, Continuum fails to create personnel objects for records where the card number has seven or more digits. Environment CSV Import Personnel records Custom Format Cause Continuum defaults to Infinity_37 When the card format is not specified in the import file.  While custom formats can accommodate larger card numbers, Infinity 37 cards only support card numbers up to 524287. Resolution Add a attribute column for cardtype. Under the card format column for each card, add Customwiegand.
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • Andover Continuum
1053 Views

SmartStruxure Building Operation - Is there a way to force ES web clients to use https only (instead of http)?

Issue Web Security. Environment http https Web Clients Cause http does not provide the same level of security as https. Resolution At SmartStruxure Building Operation 1.4, this is no way to force ES web clients to use https. The feature is supported from SmartStruxure 1.6.0 RC and up
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • EcoStruxure Building Operation
1035 Views

Changing configuration EM9 90 to 180?

Issue Is it possible to make the EM9 90° to a 180°? Environment EM9 8601100000 8601110000 Cause Due to large quantities of 90° version in stock but no demand, changing to 180° type would cover the requests of that model. Resolution No such method is known to us. Also, we strongly recommend not doing this since it will void warranties and the products will be delivered with the wrong part number.
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • Field Devices
1290 Views

SmartStruxure 1.3 user accounts - Can a user have access to change a value on a Graphic, without access to its other functions?

Issue Access which allows a value to be changed, also allows other changes to be made. Environment Users User accounts Cause A user account is created to have read only access, but this user must also have access to view Graphics, and on these graphics, be able to change values. How can this be achieved without allowing the user access to delete or edit these objects?   Resolution At StruxureWare Building Operation release 1.3 there are no available options that will achieve this configuration, the most appropriate configuration is to create a Workspace for the user, in which they will see only the Graphics, the user would have Read/Write access to the values they are allowed to change.
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • EcoStruxure Building Operation
927 Views

Replacement for old sensor EG2RL

Issue EG2RL is obsolete and needs to be replaced. Environment EG2RL 5552220000 Cause Replacement of old EG2RL sensor Resolution The EG2RL was used in pairs as Average temp sensors. Each unit contains 2 SPA (1.8kOhm) sensor elements in serial, that are then connected to the other unit in parallel. No direct replacement is available.  
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • Field Devices
985 Views

Unable to add a segment to a new project in Tree Tech 3.2 on a Windows 7, 32-bit computer.

Issue After installing Tree Tech 3.2 on a Windows 7, 32-bit computer and creating a new project, I am not able to Add an object or segment to it; in  the File, Add menu, Object and Segment are grayed-out. Environment Tree Tech 3.2 Windows 7, 32-bit computer Cause Not yet determined Resolution 1. Close Tree Tech 3.2 and any other running programs. 2. Shut down & restart the computer. 3. From the desktop icon, double-click on "Run Tree" to start Tree Tech. 4. Open the project created earlier. From the File, Add menu, the Object and Segment should no longer be grayed-out.
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • TAC IA Series
1062 Views

How to set time in LON devices

Issue LON devices have the ability to run stand alone schedules.  This capability requires continuous time updates.  Environment Niagara G3 Cause The LON Time object provides the ability to transmit the station's "System Time" to any LON device using an NVI SnvtTimeStamp type. Resolution The LON Time object provides the ability to transmit the station's "System Time" to any LON device using an NVI SnvtTimeStamp type. Install KitLon under Software Manager Open KitLon under Palette Drag or copy and paste the LonTime Object in the LonNetwork Link the LonTime Object time stamp to NVI Set Time
View full article
Picard Product_Support
‎2018-09-06 10:47 AM

Labels:
  • TAC IA Series
1284 Views

Webstation - TGML picture does not show special character as &aring;&auml;&ouml;

Issue Some web browsers can not show special extended ASCII letters like åäö  Environment Vista Webstation Cause When logging in to webstation from a PC and the TGML can not show special characters this is because a temp file has not been downloaded correctly. Resolution In the TGML window there should be a refresh button, click it and the temp file should be downloaded permanently, this should make special characters work again.
View full article
Picard Product_Support
‎2018-09-06 10:46 AM

Labels:
  • TAC Vista
1002 Views

What are the maximum view settings for the standard output window in Workplace Pro?

Issue What are the maximum view settings for the standard output window in Workplace Pro? Environment Niagara R2 Cause Trying to a capture a long error message Resolution In Admin Tool > Options > Output Window Size, change the numbers listed to the following: 2000 rows 50 visible rows 200 columns
View full article
Picard Product_Support
‎2018-09-06 10:46 AM

Labels:
  • TAC IA Series
1311 Views

Values under Xenta Server on Graphics in Webstation Show Offline in Chinese OS

Issue In Chinese OS, values under Xenta server on graphics in Webstation show offline. But in Workstation, it is fine. Environment Xenta 5/7/9 Vista Graphics Webstation Cause In Chinese OS, the characters contain space will show odd symbols. If the path of the value contains space, it will be fine in Workstation, but offline in Webstation. Resolution The solution of this issue is to avoid space in the path of the value. Use underline instead of space to separate characters. For these path that can’t avoid space(for example, the Public signal and Time schedule under Xenta server), create dummy variables to connect to them, and use these variables in graphics.
View full article
Picard Product_Support
‎2018-09-06 10:46 AM

Labels:
  • TAC INET
  • TAC Vista
1126 Views

Names on shortcuts?

Issue If creating a shortcut from an object the name of the shortcut does mirror the object. I can change the object name but the shortcuts does not reflect the change and the old name remains. Environment StruxureWare version 1.3 Cause The shortcut object doesn't need to have the same name as the original object. When the shortcut is created it gets the same name default but then you can change the names on booth the shortcut or the original object to anything you like. But the shortcut will still show the value from the original object. This is the same way as it working in Vista also Resolution That is the way it is designed to work.
View full article
Picard Product_Support
‎2018-09-06 10:46 AM

Labels:
  • EcoStruxure Building Operation
1051 Views
  • « Previous
    • 1
    • …
    • 453
    • 454
    • 455
    • …
    • 500
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore