Values under Xenta Server on Graphics in Webstation Show Offline in Chinese OS
  • Values under Xenta Server on Graphics in Webstation Show Offline in Chinese OS
  • sesa145087_brid
    sesa145087_brid
‎2018-09-06 10:46 AM
In Chinese OS, values under Xenta server on graphics in Webstation show offline. But in Workstation, it is fine.
Xenta 5/7/9
Vista Graphics
Webstation
In Chinese OS, the characters contain space will show odd symbols. If the path of the value contains space, it will be fine in Workstation, but offline in Webstation.
The solution of this issue is to avoid space in the path of the value. Use underline instead of space to separate characters. For these path that can’t avoid space(for example, the Public signal and Time schedule under Xenta server), create dummy variables to connect to them, and use these variables in graphics.