Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1827 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 42
    • 43
    • 44
    • …
    • 92
  • Next »
Label: "TAC IA Series" Show all articles

Upgraded a UNC-510 to Niagara version 522 and when trying to run the station, the following error appears: "Cannot load BACnet MSTP Driver"

Issue Upgraded a UNC-510 to Niagara version 522 and when trying to run the station, the following error appears: "Cannot load BACnet MSTP Driver" Environment Niagara version 522 UNC-510 Cause The upgrade process does NOT change the drivers.properties file. Resolution The error indicates the line: driver.mstp=tridium.nre.vxworks.mstp.VxWorksMstpDriver is missing from the driver.properties file. Copy the drivers.properties file from a UNC-520 running version 522 or higher or manually add this line into the drivers.properties file. Note that the UNC-510-2 has a maximum baud rate of 19.2 k for a BACnet MS/TP network.
View full article
Picard Product_Support
‎2018-09-06 02:48 PM

Labels:
  • TAC IA Series
841 Views

Upon starting the Lon App Tunneling program, a window displays a critical error message: "Exception occurred when attempting to run C:\windows\system32\shell32.dll, contro...

Issue Upon starting the Lon App Tunneling program, a window displays a critical error message: "Exception occurred when attempting to run C:\windows\system32\shell32.dll, control_run.dll natconfig.cpl" Environment Lon App Tunneling Program Google Desktop Cause Google desktop interferes with the Niagara LON App Tunneling service. Resolution Uninstall the Google desktop Uninstall the Lon App Tunneling program from the Windows Control Panel > Add/Remove Programs Re-install the Lon App Tunneling program Re-boot the computer
View full article
Picard Product_Support
‎2018-09-06 02:47 PM

Labels:
  • TAC IA Series
1018 Views

Erie T200 series thermostats, display is blank, or thermostat will not hold setpoint, or thermostat function buttons do not work.

Issue Erie T200 series thermostats, display is blank, or thermostat will not hold setpoint, or thermostat function buttons do not work. Environment Erie T200 Series Cause Bad or missing thermostat battery. Resolution Replace the bad or missing thermostat battery p/n Energizer 357 or equal. Confirm voltage is between 20 and 32 VAC with 75mA to 1.2A of power is available. If the battery is good and voltage and current is within specification then replace the thermostat. Symptoms Display fades away after 1 minute then goes BLANK. No function with up/down buttons. SETPOINT will default to 70°F (21.1°C) in Heat mode and 76°F (24.4°C) in Cool mode when power is restored. If the thermostat was manufactured before 2000, the default was 75°F (23.8°C) for both Heat and Cool mode. With a good battery, the display will indicate space temperature. There are no functions with the up/down buttons. The last setpoint is maintained when power is restored.
View full article
Picard Product_Support
‎2018-09-06 02:47 PM

Labels:
  • TAC IA Series
1812 Views

Niagara R2 UNCs using the bacnet-2.305.523b.v1 (or newer) jar file may need have the bacnet.properties file modified in order to work properly.

Issue Niagara R2 UNCs using the bacnet-2.305.523b.v1 (or newer) jar file may need  have the bacnet.properties file modified in order to work properly. Environment Niagara R2 UNC with bacnet-2.305.523b.v1 will need the bacnet.properties file modified in order to work properly. If the station is upgraded to bacnet-2.305.527i.v1, -2.305.529.v1, or -2.305.232.v1, the bacnet.properties file modified in order to work properly. New stations created with bacnet-2.305.527i.v1, -2.305.529.v1, or -2.305.232.v1 will have the correct bacnet.properties file  by default. (revised 9-23-2011) Cause Upgrading bacnet jar files. Resolution Two lines near the end of the file must be un-commented by removing the leading # sign. The two lines are: pollHeartbeatCheck=true PollRestartEnabled=true No other modifications to the file are recommended. The UNC must be rebooted to utilize the revised settings. (revised 9-23-2011)
View full article
Picard Product_Support
‎2018-09-06 02:46 PM

Labels:
  • TAC IA Series
976 Views

Lon Tunneling does not function with Workplace Tech 5.7.

Issue Lon Tunneling does not function with Workplace Tech 5.7. Environment Workplace Tech 5.7 Cause In order for Lon Tunneling to work, the Echelon OpenLDV Network Driver, version 3.4 is a requirement. Resolution To determine what driver version is currently installed, follow the steps outlined on page 7 of the WPT 5.7 Installation Instructions (F-27367-4). If "Echelon OpenLDV 3.4" is not listed, install the Echelon OpenLDV Network Driver software. The installer file for this driver is provided on the WPT 5.7 CD or it can be downloaded from The Exchange Download Center: 153-0212-01A_OpenLDV340.exe. Alternatively, it can be downloaded from the Echelon website (www.echelon.com). In order to download from Echelon’s website, a (free) user account is required. Once it is created, proceed to “Recommended Downloads” and the LDV driver will be listed (towards the bottom):"OpenLDV 3.4 Network Drivers for Windows Vista/XP/2000/Server 2003 (includes drivers for i.LON 10/100/600 RNI, PCLTA-20/21, PCC-10, and U10/20".
View full article
Picard Product_Support
‎2018-09-07 03:18 AM

Labels:
  • TAC IA Series
1570 Views

Can a Master schedule in a Niagara R2 Enterprise server station trigger slave schedules residing in a PollOnDemand object in a UNC station?

Issue Can a Master schedule in a Niagara R2 Enterprise server station trigger slave schedules residing in a PollOnDemand object in a UNC station? Environment Niagara R2 Enterprise Server UNC station Cause To trigger slave schedule, be sure to link a slave calendar to the slave schedule. Resolution Schedule objects do not care that the folder is PollOnDemand. Only driver points (ie. shadow objects) will be affected by the fact that their parent is a PollOnDemand container. Be sure that there is a slave calendar linked to the slave schedule in the same station. Calendar to schedule links do not work across an external link.
View full article
Picard Product_Support
‎2018-09-06 02:46 PM

Labels:
  • TAC IA Series
942 Views

Remote I/O Module (RIO) programming: Can I/O tags (outputs) from two different RIO modules be connected to Dual-output objects?

Issue Remote I/O Module (RIO) programming: Can I/O tags (outputs) from two different RIO modules be connected to Dual-output objects? Environment MNB-1000 MNB-1000-15 Cause The object error will occur "Outputs must connect to the same remote module". Resolution Details: Dual-output objects are objects with two addressable outputs. There are three such objects: Momentary Start/Stop Object, Floating Actuator Object and Floating Actuator Priority Object. When connecting dual-output objects to I/O tags on an MNB-1000 application drawing where MNB-1000-15 remote I/O modules have been configured, be sure to connect both outputs to the same set of I/O, whether that be the MNB-1000 controller’s onboard I/O or a particular MNB-1000-15 module’s I/O. For more information, see the latest WorkPlace Tech Tool Engineering Guide Supplement (F-27356).
View full article
Picard Product_Support
‎2018-09-06 02:45 PM

Labels:
  • TAC IA Series
1136 Views

If a MNB-1000 application contains R-I/O programming, can it be successfully downloaded without the actual R-I/O hardware connected and communicating?

Issue If a MNB-1000 application contains R-I/O programming, can it be successfully downloaded without the actual R-I/O hardware connected and communicating? Environment MNB-1000 Remote I/O Module Cause Communication lost between MNB-1000 and Remote I/O module  Resolution Yes. The R-I/O modules (MNB-1000-15) are not controllers and do not have control applications within them. All processing is done at the MNB-1000 (except fallback). Lack of R-I/O or R-I/O communications or loss of R-I/O communications has no effect on or during a download. In fact, the MNB-1000 cannot communicate with or even determine if R-I/O exists until an application configured for R-I/O has been downloaded at least once. This is because the R-I/O configuration information is stored in the application and the MNB-1000 must rely on the application to know if R I/O modules even exist.
View full article
Picard Product_Support
‎2018-09-06 02:45 PM

Labels:
  • TAC IA Series
1100 Views

How can the instance number be changed in a Viconics BACnet thermostat?

Issue How can the instance number be changed in a Viconics BACnet thermostat? Environment Viconics BACnet thermostat Cause No visible button to enter configuration Resolution The ID or instance number is 7x000(x=series model)+ Mac address. The Mac address can be defined from the front of the unit. Press the white "config" button in the lower right hand corner of the circuit board once. Then keep hitting "no" until "Com Addr" is displayed and hit yes. Use up/down keys to set the address. For units with no white "config" button: VT7200 series press and hold the button (OVERRIDE) for 8 seconds VT7300 series press and hold the middle button (°C/F or OVERRIDE) for 8 seconds. VT7600 series press and hold the button (MENU) for 8 seconds Then press no until "com addr" displays, then press yes and use the up/down button to change it.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Labels:
  • TAC IA Series
1901 Views

The notification Servlet does not work in the Enterprise Server station

Issue The notification Servlet does not work in the Enterprise Server station Environment Enterprise Server station Cause NotificationServlet settings and SWID to the output object. Resolution Double check to make sure the SWID to the output object is correct. Set the NotificationServlet - properties - config - "activeCommand" to emergencyActive or manualActive and the "inactiveCommand" to emergencyInactive or manualInactive. The "activeInactiveText" for the BO can be modified to make that more meaningful.   Reboot the UNC to make these changes take effect.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Labels:
  • TAC IA Series
913 Views

Unable to use the "Put" command from the DB Admin tab of the Admin Tool in Workplace Pro. Cannot select file buttons.

Issue Unable to use the "Put" command from the DB Admin tab of the Admin Tool in Workplace Pro.  Cannot select file buttons. Environment Workplace Pro UNC series Cause UNC must be in idle. Resolution The "Put" command can only be used to import a database to an "idle" UNC. To idle a running UNC, uncheck it's "Auto Start" box and reboot.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Labels:
  • TAC IA Series
1129 Views

In Niagara R2, device objects are not updating. Bundles were used to speed the linking to graphics.

Issue In Niagara R2, device objects are not updating. Bundles were used to speed the linking to graphics. Environment Niagara R2 Cause The device objects are in bundles. Resolution Only native Niagara objects should be placed in bundles. This includes the Niagara AO, BO, AI, BI, and logic (if desired). Due to the nature of bundles they execute at their own rate. This interferes with the normal execution of BACnet, LON, GCM, ASD, DMS, MS and other hardware objects. For additional information on the use of bundles refer to The Standard Reference Manual pages 7-14 through 7-21 and pages 5-1 through 5-6 of the Web Solutions Guide.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Labels:
  • TAC IA Series
1083 Views

Does Windows XP Service Pack 3 (SP3) cause a problem with SIGNAL XP?

Issue Does Windows XP Service Pack 3 (SP3) cause a problem with SIGNAL XP? Environment SIGNAL XP computer Service Pack 3 Service Pack 2 Cause Any known issues with the SP3 helps if updating is necessary. Resolution The impact of SP3 on SIGNAL XP is not known. SIGNAL XP has been field-tested with Windows XP Service Pack 2 and the only issue identified was recognition of the Security Plug (see TA06-03). No other anomalies have been observed. There are no plans to validate SIGNAL XP with this new service pack. It is recommended that all SIGNAL XP computers maintain Windows XP at service pack 2.
View full article
Picard Product_Support
‎2018-09-07 04:08 AM

Labels:
  • TAC IA Series
1126 Views

Without a Niagara R2 UNC, Enterprise Server, or MNB-1000 on a BACnet/MSTP network, can the MNB controllers communicate reliably peer-to-peer (i.e. sharing outside air temperature b...

Issue Without a Niagara R2 UNC, Enterprise Server, or MNB-1000 on a BACnet/MSTP network, can the MNB controllers communicate reliably peer-to-peer (i.e. sharing outside air temperature between multiple MNB-300 controllers)? Environment MNB-300 controllers Cause Some site would like to avoid the use of Niagara R2 UNC, Enterprise Server, or MNB-1000. Resolution Yes. The implementation of COV subscriptions in the MNB controller line, with the 1.4x (or greater) firmware, allows for every MNB controller to function as both a COV server and a COV client. This allows peer-to-peer communications between all MNB controller models. To create peer-to-peer links, review Chapter 4 in the WorkPlace Commissioning Tool and Flow Balance Users Guide (F-27358) that details how to use Link Builder.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Labels:
  • TAC IA Series
874 Views

How can an existing Enterprise Server station be configured to run the Vykon Alarm Service (VAS)?

Issue How can an existing Enterprise Server station be configured to run the Vykon Alarm Service (VAS)? Environment Enterprise Server Vykon Alarm Service Cause For Enterprise Server to support VAS, check the Enterprise Server shipped date to determine if part number IA-ENT-AS is required. Resolution An Enterprise Server station is already licensed to support VAS. It also includes support for two VAS clients. If additional clients are required, order part number IA-ENT-AS-C for each additional client. If the Enterprise Server was shipped before November 1, 2002, it did not include support for VAS. It must be ordered separately using part number IA-ENT-AS (which will also include support for two VAS clients). The Enterprise Server must also be upgraded to, at minimum, build r2.301.330. For more information, review R2 Worksheet (xlt) tab "ENT SVR Estimator" for additional notes on various part numbers. VAS software can be downloaded from The Exchange. Download VAS v2.4 CD Image.zip and VasPatch.zip. Unzip the CD Image for the Installation Instruction Manual. The VasPatch is installed last.
View full article
Picard Product_Support
‎2018-09-07 04:16 AM

Labels:
  • TAC IA Series
1203 Views

A Liebert SiteLink panel is not communicating with the Niagara R2 UNC using BACnet/MSTP.

Issue A Liebert SiteLink panel is not communicating with the Niagara R2 UNC using BACnet/MSTP. Environment Liebert SiteLink panel Niagara R2 UNC BACnet/MSTP communication Cause Termination resistors Resolution When connecting a dedicated Liebert SiteLink module MSTP segment to the UNC, the EIA-485 trunk typically requires 120-ohm termination resistors at each end. Field testing has determined for Liebert Sitelink-4 and –12 modules that the termination resistors have a negative affect on communication even at a low baud rate of 9600. Removing the termination resistors resolved the communication issues.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Labels:
  • TAC IA Series
1430 Views

How can two MicroNet 2000 MN-FLO or MN-FLO3T VAV controllers share data?

Issue How can two MicroNet 2000 MN-FLO or MN-FLO3T VAV controllers share data? Environment MicroNet 2000 MN-FLO / MN-FLO3T Cause Sharing data between the devices require MicroNet Integrator. Resolution Sharing data between two (or more) MicroNet controllers requires a MicroNet Integrator. Even if the integrator is not communicating to a GCM/DMS, it is still required to facilitate data sharing on the U-bus. The only system configuration, not involving an integrator, is stand-alone mode. Peer-to-peer data sharing is not possible. See the MicroNet 2000 Family Fundamentals Guide (F-25711) and review the chapter on System Configurations.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Labels:
  • TAC IA Series
1302 Views

With Niagara R2 Status Type objects, what colors are used to represent their different real-time conditions?

Issue With Niagara R2 Status Type objects, what colors are used to represent their different real-time conditions? Environment Niagara R2 Cause Configure the status indicator to turn a different color of an off-normal condition. Resolution Status-variable type objects contain a 'statusInput' (sIn) and 'statusOutput' (sOut) property. These objects are: BooleanStatusType floatStatusType integerStatusType The sOut will change to a different color for the following conditions: orange (dark yellow) -> fault yellow -> down red -> inAlarm cyan (light blue) -> OutOfService magenta (purple) -> overridden clear (grey) -> normal These are the background colors as the real-time text remains black in all cases. These are also the default colors that can be changed by modifying the statusColors.properties file.
View full article
Picard Product_Support
‎2018-09-06 02:44 PM

Labels:
  • TAC IA Series
1374 Views

What is the preferred architecture with MNB MSTP controllers when an installation has a MNB-1000 and a Niagara R2 UNC? Hang the controllers on the MSTP bus of the MNB-1000 or the ...

Issue What is the preferred architecture with MNB MSTP controllers when an installation has a MNB-1000 and a Niagara R2 UNC?  Hang the controllers on the MSTP bus of the MNB-1000 or the UNC? Environment MNB-1000 Niagara R2 UNC MNB Controllers Cause Prevent any performance degradation by hooking up the MNB controllers in the correct location. Resolution Either way is OK.  If the MNB controllers are on the MSTP trunk under the MNB-1000, then the MNB-1000 acts as a router, and communication is a little slower than if they were directly connected to the UNC.
View full article
Picard Product_Support
‎2018-09-06 02:43 PM

Labels:
  • TAC IA Series
1277 Views

Can the profile in a MNL standard LonMark controller be changed in the field? For example, can a MNL-20RH3 (heat pump profile) be changed to a MNL-20RS3 (satellite 3 profile)?

Issue Can the profile in a MNL standard LonMark controller be changed in the field?  For example, can a MNL-20RH3 (heat pump profile) be changed to a MNL-20RS3 (satellite 3 profile)? Environment MNL standard LonMark controllers Cause The LonMark Profile is stored in the controller's firmware. Resolution No, the LonMark Profile cannot be modified.
View full article
Picard Product_Support
‎2018-09-06 02:43 PM

Labels:
  • TAC IA Series
1535 Views
  • « Previous
    • 1
    • …
    • 42
    • 43
    • 44
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of