Niagara R2 UNCs using the bacnet-2.305.523b.v1 (or newer) jar file may need have the bacnet.properties file modified in order to work properly.
  • Niagara R2 UNCs using the bacnet-2.305.523b.v1 (or newer) jar file may need have the bacnet.properties file modified in order...
  • SESA113595
    SESA113595
‎2018-09-06 02:46 PM
Niagara R2 UNC with bacnet-2.305.523b.v1 will need the bacnet.properties file modified in order to work properly.
If the station is upgraded to bacnet-2.305.527i.v1, -2.305.529.v1, or -2.305.232.v1, the bacnet.properties file modified in order to work properly.
New stations created with bacnet-2.305.527i.v1, -2.305.529.v1, or -2.305.232.v1 will have the correct bacnet.properties file  by default.
(revised 9-23-2011)
Upgrading bacnet jar files.
Two lines near the end of the file must be un-commented by removing the leading # sign.
The two lines are:
  • pollHeartbeatCheck=true
  • PollRestartEnabled=true
No other modifications to the file are recommended. The UNC must be rebooted to utilize the revised settings.
(revised 9-23-2011)
  • TAC IA Series