Upgraded a UNC-510 to Niagara version 522 and when trying to run the station, the following error appears: "Cannot load BACnet MSTP Driver"
  • Upgraded a UNC-510 to Niagara version 522 and when trying to run the station, the following error appears: "Cannot load BACne...
  • sesa119747
    sesa119747
  • Kim_Baze
    Kim_Baze
‎2018-09-06 02:48 PM
  • Niagara version 522
  • UNC-510
The upgrade process does NOT change the drivers.properties file.
The error indicates the line: driver.mstp=tridium.nre.vxworks.mstp.VxWorksMstpDriver is missing from the driver.properties file.
Copy the drivers.properties file from a UNC-520 running version 522 or higher or manually add this line into the drivers.properties file.
Note that the UNC-510-2 has a maximum baud rate of 19.2 k for a BACnet MS/TP network.