A Liebert SiteLink panel is not communicating with the Niagara R2 UNC using BACnet/MSTP.
  • A Liebert SiteLink panel is not communicating with the Niagara R2 UNC using BACnet/MSTP.
  • sesa119747
    sesa119747
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 02:44 PM
  • Liebert SiteLink panel
  • Niagara R2 UNC
  • BACnet/MSTP communication
Termination resistors
When connecting a dedicated Liebert SiteLink module MSTP segment to the UNC, the EIA-485 trunk typically requires 120-ohm termination resistors at each end. Field testing has determined for Liebert Sitelink-4 and –12 modules that the termination resistors have a negative affect on communication even at a low baud rate of 9600. Removing the termination resistors resolved the communication issues.