Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 298
    • 299
    • 300
    • …
    • 509
  • Next »

View the Personnel Object Picture and the Video of the person entering the area on the same PinPoint Graphic

Issue How to configure a PinPoint Graphic to show both the Personnel Object Picture and the Video of the person entering the area. Environment PinPoint Graphic Cause A dual view of the person's credentials as well as a live feed of them entering the area is a good view for security personnel. Resolution Assuming the personnel and door objects and the pinpoint Graphic were created, also create: Create A Video Server From the root click new Video server, add the ip address of the Video Server and account info. Create A Video Layout From the root click on new Video layout. Edit the door in the selected area and open the alarm tab. Add Root\Door access and click enable. In the graphic box add the assigned graphic. In the Video Box add the Video Layout object. Edit the Door access Notification Actions. Add desired actions. Display Video, Display Graphic. Open Pinpoint Graphic.Insert Active component Personnel Picture Assign attribute LastPersonentrd
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • Andover Continuum
1130 Views

Niagara R2 Enterprise Server Error: Invalid template: db/Bacnet522/BACnetTemp/Josh_Plant/JoshIndex. The file does not exist on the server.

Issue When logging into a Niagara R2 Enterprise Server station, the default web page displays the following error: ERROR: Invalid template: db/Bacnet522/BACnetTemp/Josh_Plant/JoshIndex. The file does not exist on the server. Environment Niagara R2 Enterprise Server Cause There must be a background HTML page specified in the WebUIservice default template URL field in order for the web pages to display correctly. Resolution Right click the WebUIservice > Properties > Config tab The default template that comes with a new station is /tridium/services/defaultTemplate.html Verify that this is correct For further information, refer to the Niagara Web Solutions Guide.
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • TAC IA Series
1361 Views

When attempting to open a Niagara R2 UNC station in Workplace Pro, a pop-up error explains that the station was "Not Found (404)".

Issue When attempting to open a Niagara R2 UNC station in Workplace Pro, a pop-up error explains that the station was "Not Found (404)". Environment Niagara R2 UNC Workplace Pro Cause Generally, this error indicates that TCP port 80 is blocked on the PC accessing the UNC. Resolution Most frequently, it is the Windows Firewall blocking the port, although there are other applications that can block the port (e.g. remote access software, antivirus software, Microsoft's IIS). The best way to resolve the issue is to disable the offending application while accessing the UNC. If this is not feasible, then create an exception policy in the application that will allow port 80 communications for the IP address of the UNC. Specific procedures vary from application to application.
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • TAC IA Series
1603 Views

Modems fail to connect with the USRobotics 5686 series V.92 modems

Issue Some older modems will successfully connect with the USRobotics 5686 series V.92 modems on the first call, but will fail to connect on subsequent attempts. Product Line TAC IA Series Environment USRobotics 5686 series V.92 modems Cause The V.92 protocol must be disabled when using these modems with older modems.  Resolution To disable the V.92 protocol on the USRobotics 5686 series modems, enter the following setup string in addition to the string specified in the referenced bulletin, before saving the settings: AT +PIG=1 +PMH=1 +PQC=3
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • TAC IA Series
1256 Views

Enabling MSTP bias resistors on a MNB-1000

Issue When should the MSTP bias resistors be enabled on a MNB-1000? Product Line TAC IA Series Environment BACnet /MSTP trunk under an MNB-1000 Cause RS-485 biasing rules apply to BACnet / MSTP Resolution An MSTP network requires at least one set of bias resistors but no more than two sets. If a UNC device exists on the network it will provide one set of resistors.  No others are needed. If one or more MNB-1000s are on the network, enable only one set of bias resistors.
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • TAC IA Series
1834 Views

A BACnet/MSTP network will run longer than 4000 feet. Can the ASD or MicroSmart repeater be used?

Issue A BACnet/MSTP network will run longer than 4000 feet. Can the ASD or MicroSmart repeater be used? Environment ASD repeater MicroSmart repeater BACnet/MSTP network Cause ASD or MicroSmart repeater won't extend communication distances on a BACnet/MSTP. Resolution Both repeaters were tested and neither worked on a MSTP network.
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • TAC IA Series
1064 Views

A Niagara R2 station won't open: Requestclient.handshake [serverSessionId=3] Station=josh [0] Station

Issue A Niagara R2 station listed under localhost won't open.  In the fui.exe console window, this message appears: Requestclient.handshake [serverSessionId=3] Station=josh [0] Station The station never opens. Environment Niagara R2 station Cause This behavior is caused by McAfee Security Centers Proxy Service. Resolution Disable the proxy service and reboot the computer. Follow the steps below to disable this service: Open the Windows services - (Click on Start - Run - then type service.msc) Scroll down to the McAfee Proxy service. Disable this service by right-clicking on the service - select properties - change the startup type to disabled. Reboot the computer. This should allow the station to run correctly on the localhost.
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • TAC IA Series
1228 Views

The Vykon Alarm Client will not connect to the Niagara R2 Enterprise Server station.

Issue The Vykon Alarm Client will not connect to the Niagara R2 Enterprise Server station. Environment Vykon Alarm Client Niagara R2 Enterprise Server station Cause The Vykon Alarm Client uses TCP port 4321 to communicate with the Enterprise Server. Many firewall, antivirus, and Internet security applications (e.g. Windows Firewall, antivirus & remote access software) block TCP port 4321 by default. Resolution Either disable the offending application, or create an exception policy in the application to open TCP port 4321. To view active TCP connections, open a DOS window, and type: netstat -ano. The output will look something like this: Active Connections Proto Local Address Foreign Address State PID TCP 0.0.0.0:13 0.0.0.0:0 LISTENING 956 TCP 0.0.0.0:37 0.0.0.0:0 LISTENING 956 TCP 0.0.0.0:135 0.0.0.0:0 LISTENING 1368 TCP 0.0.0.0:445 0.0.0.0:0 LISTENING 4 TCP 0.0.0.0:3011 0.0.0.0:0 LISTENING 756 TCP 0.0.0.0:6523 0.0.0.0:0 LISTENING 3752 TCP 0.0.0.0:27700 0.0.0.0:0 LISTENING 748 TCP 10.1.146.152:139 0.0.0.0:0 LISTENING 4 TCP 10.1.146.152:2531 72.247.127.34:80 CLOSE_WAIT 3616 TCP 10.1.146.152:2532 72.5.124.55:80 CLOSE_WAIT 3560 TCP 10.1.146.152:2533 72.247.127.11:80 CLOSE_WAIT 3560 TCP 10.1.146.152:4245 10.1.146.32:4321 ESTABLISHED 216 A successful connection to the Enterprise Server will have an entry similar to the last line, where the Foreign Address (e.g. 10.1.146.32:4321) will have a state of ESTABLISHED.
View full article
Picard Product_Support
‎2018-09-06 02:57 PM

Labels:
  • TAC IA Series
1558 Views

When using Workplace Tech, links won't create between two objects. No matter what type of objects, the link line remains red and the application will not link the two objects.

Issue When using Workplace Tech, links won't create between two objects.  No matter what type of objects, the link line remains red and the application will not link the two objects. Environment Workplace Tech Cause In Microsoft Visio, the Snap & Glue feature is disabled. Resolution  To enable Snap and Glue go to Tools > Snap & Glue, then check the Snap box and the Glue box.
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1135 Views

Can Signal XP run with a limited user account in Windows XP?

Issue Can Signal XP run with a limited user account in Windows XP? Environment Signal XP Limited local user account Cause The application will not run properly with limited local user account. Resolution In order to run Signal XP, the Windows user account must have local administrative privileges.
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
858 Views

Will Niagara R2 and G3 applications (ie: Workplace Pro, Workbench) run on a dual-processor/dual core/duo laptop?

Issue Will Niagara R2 and G3 applications (ie: Workplace Pro, Workbench) run on a dual-processor/dual core/duo laptop? Environment Niagara R2 Niagara G3 Workplace Pro Workbench Dual core processor PC Cause As per Tridium sales and technical support, both applications will run on dual processor computers, though they have not been specifically tested. For more information on Workplace Pro review document F-26999 and for more information on Workbench review document F-27426. Resolution Minimum hardware requirements for Niagara applications are as follows: R2 - Workplace Pro: Intel Pentium IV 1GHz processor, 512 MB RAM, 1GB hard disk space G3 - Workbench: Intel Pentium IV 2GHz processor, 1 GB RAM, 1GB hard disk space
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1537 Views

After manually changing all the COV increments in a Niagara R2 station, the COV increment values never update.

Issue After manually changing all the COV increments in a Niagara R2 station, the COV increment values never update. Environment Niagara R2 Cause The COV increment property is not fetched during a poll. To receive an update on this property use the Upload All command on the device object. Resolution Follow the steps below in WorkPlace Pro to perform an Upload All on the device object: Navigate to the workspace of the container where the BACnet device object exists. Right click the device object and select upload all. For further information on COV increment refer to the Niagara R2 BACnet Integration Reference manual 
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1613 Views

Is an additional license feature required for BACnet/MSTP in a Niagara R2 UNC or Niagara G3 ENC?

Issue Is an additional license feature required for BACnet/MSTP in a Niagara R2 UNC or Niagara G3 ENC? Environment Niagara R2 UNC Niagara G3 ENC BACnet/MSTP Cause Each COM port require a license to enable BACnet/MSTP Resolution Although the BACnet driver is included with all Niagara R2 and G3 controllers, only the UNC-510-2, UNC-520, and ENC-520 controllers support BACnet/MSTP communications. For the UNC-510-2 and UNC-520, BACnet/MSTP is a license feature that must be purchased separately per COM port desired for MSTP communications (part number: IA-DRV-MST-P). For the ENC-520, BACnet/MSTP is licensed for all COM ports by default.  No additional license purchase is necessary.
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1402 Views

Niagara R2/G3 UNC/JACE reboots every 15 minutes with "Battery test failed" logged

Issue A Niagara R2/G3 UNC/JACE is rebooting every 15 minutes and the standard output window indicates AC Power status failed and a "Battery test failed" gets logged as well. Product Line TAC IA Series Environment I/A Series UNC, ENC or JACE chassis with Gel-cell backup battery Cause Marginal or failed battery or bad battery charging fuse Resolution The UNC automatically performs a battery load test every 15 minutes. If the voltage drops below a predefined value, the battery test indicates "battery test failed". If the voltage is higher than the predefined value, the battery test indicates "battery test passed". This message is only reported once unless the detected battery condition changes. A station alarm is generated only when the new outcome is different that the previous test. If a battery is marginal, the test may alternate between "passed" and "failed." Additionally, a bad or marginal battery has been known to cause random UNC reboots. Begin troubleshooting by checking the battery fuse (field replaceable only in the UNC-500/510 controllers), connections and voltage level.  If the battery voltage is low (less than 12 Vdc), disconnect the battery and monitor the UNC for errors or rebooting. If the errors or rebooting stops install a new battery.  After installing the new battery, measure the battery charging voltage.  The voltage reading should be between 13 and 14.5 volts DC if a good battery is connected.  If the installed battery is partially discharged, the charging voltage reading may be as low as 12.5 volts. In release 2.301.522, a change was made to how embedded controllers (UNC-410 / 500 / 510 / 520) perform the backup battery test.  Formerly, a "marginal" battery might result in continuous reboots. Now, the battery test is better coordinated with the AC power test. This prevents the scenario of repeated AC power fail shutdowns upon boot up if the battery is bad or weak.
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
2311 Views

When opening an application file in Workplace Tech 5.x, the following error message appears: "AppXMLAddon error code: -##########" "unknown error."

Issue When opening an application file in Workplace Tech 5.x, the following error message appears:  "AppXMLAddon error code: -##########" "unknown error."  (where # = random numbers) Environment Workplace Tech 5.X Cause This error is caused by an illegal character in the application's nciLocation snvt. The character looks like a bold vertical line. WorkPlace Tech 4.0 did not have an issue with this character but WorkPlace Tech 5.x generates the above error. Resolution To eliminate the error: Open the application with WorkPlace Tech 5.x and continue to click OK until the drawing opens.  Locate the nciLocation snvt and check its initial value. Delete the unknown character from that entry field, and re-compile the application. 
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1005 Views

How can the Niagarad service for Niagara G3 be started?

Issue How can the Niagarad service for Niagara G3 be started? Environment Niagarad service Niagara G3 Cause There are three different ways to start the Niagarad service manually. Resolution From the Windows Start menu: click Programs > Vykon AX Supervisor 3.x.x > Install Platform Daemon Open a DOS window and type - cd\Niagara\Niagara-3.x.x\bin then type plat.exe installdaemon Create a desktop shortcut with the following: C:\niagara\niagara-3.x.x\bin\plat.exe installdaemon
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1669 Views

Daylight Savings Time changeover may not automatically occur on some Network 8000 controllers.

Issue Daylight Savings Time changeover may not automatically occur on some Network 8000 controllers. Environment Network 8000 Cause The controllers with the "Formula Date" option selected will use the "Formula Date" information to calculate a Spring and Fall fixed date which is used to determine when the daylight savings changeover should occur. The fixed dates calculated will be for the current calendar year. This means that if a "Formula Date" recalculation is triggered on April 15, 2007 in a NW8000 controller, the controller will generate fixed dates of March 11, 2007 and November 4, 2007 corresponding to the 2nd Sunday in March and the first Sunday in November. Once the fall back date of November 4, 2007 has been processed, the NW8000 controller will not recalculate the new fixed dates for year 2008 until there is a trigger event that occurs after January 1, 2008. If no trigger event occurs between January 1, 2008 and March 9, 2008, the "spring ahead changeover" does not occur since the controller is still using the fixed date of March 11, 2007. Resolution For the daylight savings time changeover to occur, a new fixed date must be calculated each calendar year before the Spring changeover date. The changeover date calculation is made following a pre-determined trigger event. The fixed changeover dates used for comparison in the "Formula Date" Daylight Savings option currently get recalculated when: The controller’s EEPROM is cleared, The controller is reset, Any information in the INSTALLATION DATA is modified. If the "Formula Date" option is selected in a controller, the only means to insure that a controller will process the daylight savings changeover is to either reset the controller or modify the installation data. If it is unknown that either of these events has occurred during the calendar year it will be necessary to manually initiate one of these events to guarantee that the daylight savings time changeover will occur. Refer to Bulletin 01-40
View full article
Picard Product_Support
‎2018-09-07 02:06 AM

Labels:
  • TAC IA Series
990 Views

Where can network bandwidth utilization statistics be found for the Niagara R2 product?

Issue Where can network bandwidth utilization statistics be found for the Niagara R2 product? Environment Niagara R2 Cause Concern of bandwidth usages over a connection. Resolution There are some scenarios in which IT Managers or Network Administrators are concerned with the impact of Niagara R2 systems on their network. Some testing has been done to determine bandwidth usages and is documented in the Niagara ITManagersFAQ document.
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1216 Views

How can the default HTTP port for a Niagara R2 UNC station be changed?

Issue How can the default HTTP port for a Niagara R2 UNC station be changed? Environment Niagara R2 UNC station Cause The station need to change the default port 80 to a non-standard HTTP port in the httpPort text box. Resolution Do the following:  In WorkPlace Pro, open the station offline In the tree view, right-click on the offline station and select Go - Properties On the Properties sheet, click the Config tab Edit the httpPort text box, removing the default port of 80 and replacing it with your chosen port number (e.g. 8081) Click Apply In the tree view, right-click on the offline station and select Close Open the Admin Tool, and log into the UNC Right-click the station name (not the host name or address) and select Edit - Properties. This opens the station.properties file Add the following line to the station.properties file:  httpPort=[newport] (newport = port number from step 4), example httpPort=8081 From the file menu, choose File - Close. The system will prompt you to save any changes. Choose Yes. In the Admin Tool, click the Installation tab On the Installation Sheet, click Install Station Select the station from step 4, then click OK In the Confirm dialog box, click Yes In the Select Database Format dialog box, select the DB radio button, then click OK The system will load the offline database to the UNC, then re-boot the station. When finished, the message box will display "Installation Complete"
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1194 Views

Niagara R2 UNC Standard Output Window Error: "Duplicate server sessions; kill! [station name]"

Issue The following error appears in a Niagara R2 UNC Standard Output Window: "Duplicate server sessions; kill! [station name]" Environment Niagara R2 UNC Cause This error message is usually indicative of another station running on the Enterprise Server having the same name as the UNC station. Resolution Stop the running station on the Enterprise Server via the Admin Tool.
View full article
Picard Product_Support
‎2018-09-06 02:56 PM

Labels:
  • TAC IA Series
1082 Views
  • « Previous
    • 1
    • …
    • 298
    • 299
    • 300
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of