Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

The Vykon Alarm Client will not connect to the Niagara R2 Enterprise Server station.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • The Vykon Alarm Client will not connect to the Niagara R2 Enterprise Server station.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • sesa116871
    sesa116871
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1558 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

The Vykon Alarm Client will not connect to the Niagara R2 Enterprise Server station.

Picard Product_Support
‎2018-09-06 02:57 PM

Issue

The Vykon Alarm Client will not connect to the Niagara R2 Enterprise Server station.

Environment

  • Vykon Alarm Client
  • Niagara R2 Enterprise Server station

Cause

The Vykon Alarm Client uses TCP port 4321 to communicate with the Enterprise Server. Many firewall, antivirus, and Internet security applications (e.g. Windows Firewall, antivirus & remote access software) block TCP port 4321 by default.

Resolution

Either disable the offending application, or create an exception policy in the application to open TCP port 4321.

To view active TCP connections, open a DOS window, and type: netstat -ano.

The output will look something like this:

Active Connections Proto Local Address Foreign Address State PID

TCP 0.0.0.0:13 0.0.0.0:0 LISTENING 956

TCP 0.0.0.0:37 0.0.0.0:0 LISTENING 956

TCP 0.0.0.0:135 0.0.0.0:0 LISTENING 1368

TCP 0.0.0.0:445 0.0.0.0:0 LISTENING 4

TCP 0.0.0.0:3011 0.0.0.0:0 LISTENING 756

TCP 0.0.0.0:6523 0.0.0.0:0 LISTENING 3752

TCP 0.0.0.0:27700 0.0.0.0:0 LISTENING 748

TCP 10.1.146.152:139 0.0.0.0:0 LISTENING 4

TCP 10.1.146.152:2531 72.247.127.34:80 CLOSE_WAIT 3616

TCP 10.1.146.152:2532 72.5.124.55:80 CLOSE_WAIT 3560

TCP 10.1.146.152:2533 72.247.127.11:80 CLOSE_WAIT 3560

TCP 10.1.146.152:4245 10.1.146.32:4321 ESTABLISHED 216

A successful connection to the Enterprise Server will have an entry similar to the last line, where the Foreign Address (e.g. 10.1.146.32:4321) will have a state of ESTABLISHED.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2675
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of