Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Daylight Savings Time changeover may not automatically occur on some Network 8000 controllers.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Daylight Savings Time changeover may not automatically occur on some Network 8000 controllers.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1050 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Daylight Savings Time changeover may not automatically occur on some Network 8000 controllers.

Picard Product_Support
‎2018-09-07 02:06 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:38 AM

Issue

Daylight Savings Time changeover may not automatically occur on some Network 8000 controllers.

Environment

Network 8000

Cause

The controllers with the "Formula Date" option selected will use the "Formula Date" information to calculate a Spring and Fall fixed date which is used to determine when the daylight savings changeover should occur. The fixed dates calculated will be for the current calendar year. This means that if a "Formula Date" recalculation is triggered on April 15, 2007 in a NW8000 controller, the controller will generate fixed dates of March 11, 2007 and November 4, 2007 corresponding to the 2nd Sunday in March and the first Sunday in November. Once the fall back date of November 4, 2007 has been processed, the NW8000 controller will not recalculate the new fixed dates for year 2008 until there is a trigger event that occurs after January 1, 2008. If no trigger event occurs between January 1, 2008 and March 9, 2008, the "spring ahead changeover" does not occur since the controller is still using the fixed date of March 11, 2007.

Resolution

For the daylight savings time changeover to occur, a new fixed date must be calculated each calendar year before the Spring changeover date. The changeover date calculation is made following a pre-determined trigger event. The fixed changeover dates used for comparison in the "Formula Date" Daylight Savings option currently get recalculated when:

  • The controller’s EEPROM is cleared,
  • The controller is reset,
  • Any information in the INSTALLATION DATA is modified.

If the "Formula Date" option is selected in a controller, the only means to insure that a controller will process the daylight savings changeover is to either reset the controller or modify the installation data. If it is unknown that either of these events has occurred during the calendar year it will be necessary to manually initiate one of these events to guarantee that the daylight savings time changeover will occur. Refer to Bulletin 01-40

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2684
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore