Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 257
    • 258
    • 259
    • …
    • 507
  • Next »

What is the Date format that the ID Works supports?

Issue Is there a difference in the way Datacard (ID Works) handles the date format? What is the Date format that the ID Works supports? Environment I/NET Seven DataCard ID Works Cause Date format needs to be entered correctly when integrating ID Works with I/NET Seven Resolution Yes, the format is different. The only format that the Datacard ID Works system supports are YYYY/MM/DD.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1256 Views

In TCP/IP terms, what is a broadcast address used for?

Issue In TCP/IP terms, what is a broadcast address used for? Environment I/NET IP network Cause A broadcast address is used to simultaneously address every host on a network. Resolution The broadcast address for network 128.66 is 128.66.255.255. A datagram sent to this address is delivered to every individual on network 128.66.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1140 Views

What are some of the reasons why subnetting is used?

Issue What are some of the reasons why subnetting is used? Environment I/NET IP network Cause When considering network design, there are some reasons to consider subnetting. Resolution Overcoming distance limitations Interconnect dissimilar physical networks Filter traffic between networks
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1323 Views

What command displays the translation of the IP addresses to Ethernet addresses?

Issue What command displays the translation of the IP addresses to Ethernet addresses? Environment I/NET Cause This stands for Address Resolution Protocol (ARP). This command displays the table of translations between IP addresses and Ethernet Addresses. This table is built dynamically. When ARP receives a request to translate an IP address, it checks for the address in the (ARP) table. Resolution arp -a
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1115 Views

What situations may use Static Routing?

Issue What situations may use Static Routing? Environment I/NET Cause A network with a limited number of gateways to other TCP/IP networks may be configured with static routing. Static routing tables do not adjust to network changes, so they should be used only where routes do not change. But when remote destinations can only be reached through one route, a static route is the best choice. Resolution A static routing table is constructed manually by the system administrator using the "route" command.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1228 Views

Schedules behavior with Special Days and Temporary Time Schedule on a point

Issue If I have populated a Special Days and Temporary Time Schedule on a point, which schedule will control that point? Environment I/NET Time Schedule extension Cause There may be an overlap in scheduling that causes a Special day to fall on the same day as a Temporary Time Schedule. Resolution In the case of a point having a Special day defined and a Temporary schedule defined, the Temporary Time Schedule will override the Special Days schedule.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1126 Views

Possible Issues related to a large number of global and indirect points

Issue Possible Issues related to a large number of global and indirect points Environment I/NET CLAN network Cause Adding a large number of global and indirect points can adversely affect the system response time. Resolution Each globalization and request for globalization is a message from the DCU. A large number of global and indirect points an overload the DCU’s message capability. This can reduce the system performance, and may cause the system to discard messages.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1223 Views

Docutrend cells will not update

Issue A Docutrend setup has Docutrend cells that will not update. Environment Docutrend Cause Points storing information to docutrend cells (including Event cells) must have at least a priority of routine when attached to a direct connect host, or the cell will not receive the data. On a dial out Tap system, points storing information on Docutrend cells (including Event cells) must have at least a priority, or the tap will not send the data. Resolution Check the system settings to ensure that points storing information to Docutrend cells have a priority of at least routine.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
888 Views

UC, MR, and ASC controllers do not use the minimum trip and close command

Issue Which controllers do not use the minimum trip and close command? Environment UC, MR, or ASC Cause The editor lets you enter a value in the minimum trip and close field; however, the UCI, MRI, MCI, or I/Site Lan replaces the entered value with the default value of "0" when it is downloaded to the UC, MR, or ASC. Resolution The minimum trip and close parameters are not used for Unitary Controllers (UC), Micro Regulator (MR), or Application Specific Controllers (ASC) output commands.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
886 Views

Calculations may not be used on an indirect point

Issue Calculations may not be used on an indirect point Environment I/NET Seven Resident I/O calculation Cause Calculations may not be used on an indirect point Resolution Calculations may be used only with internals or external points. Indirect points may not use the calculation extension.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1257 Views

Special consideration for 08 and 09 DI\DA points on a 7910A and 7920 DPU

Issue Can I use the 08 & 09 DI\DA points on a 7910A and 7920 DPU as internal points? Environment 7910A DPU 7920 DPU Cause These points are dedicated points and cannot be used for any other purpose. Resolution The 08 & 09 DI\DA points on a 7910A and 7920 DPU: Cannot be used as internal points Cannot have calculation extensions
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
881 Views

File equalization quit working

Issue File equalization quit working. Troubleshooting steps to repair file equalization. Environment I/NET 2000 Cause Brdpend is a file equalization buffer, and should always be at 0KB.  Resolution Go to Windows Explorer Look in the Inet2000\data directory In this directory, look for a file called Brdpend. If this file is larger than 0KB, then delete this file. I/NET will make a new Brdpend file to replace the deleted one.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1324 Views

DPU restore does not work

Issue Cannot get a DPU restore to work. Environment I/NET 2000 DPU Cause Acsave.tmc is a file that buffers the DPU restore information. It should disappear after a restore. Having the file present could mean that there was a problem with the download. Resolution Go to Windows Explorer Look in the Inet2000\data directory In this directory, look for a file called Acsave.tmc. If this file is present, delete it.   After deleting the Acsave.tmc file, do another DPU restore.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1185 Views

A door DO is defined in the Resident I/O editor, but does not show up in the doors editor.

Issue A door DO is defined in the Resident I/O editor, but does not show up in the doors editor. Environment I/NET Resident I/O editor I/NET Doors Editor Cause  One of the causes is the doors are not saved in the NETCON file. Resolution Select Edit>Host Computer>Network Configuration Save any links with a "+" sign Select the link that contains the door and click Penetrate Save any controllers with "+" sign Select the controller that contains the door and click Penetrate Save any sub-Lan controllers with "+" sign Select the sub-Lan controller that contains the door and click Penetrate The door should have a "+" sign next to it.  Click Save All Close out of the Network Configuration Windows The door should now show up in the door editor.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
971 Views

Is an existing IMI video frame grabber supported by Datacard?

Issue Is an existing IMI video frame grabber supported by Datacard? Environment Video Badging conversion from IMI to Datacard Cause IMI and Datacard are two different platforms with a defined upgrade path between them. Resolution The Flashpoint and Flashpoint lite, as most of the TWAIN devices are supported by the Datacard system. However, if the grabber card you have is not supported, a new card can be purchased from Datacard.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1151 Views

Is a Magicard Video Badging printer supported by the Datacard system?

Issue Is a Magicard Video Badging printer supported by the Datacard system? Environment Video badging upgrade from IMI to Datacard Cause Depending on the existing printer, and upgrade from IMI to Datacard may require some steps to become operational. Resolution The magicard printer, used by the IMI System, can be used with the Datacard system. However, you will have to download a new printer driver from their Web Site (http://www.ultramagicard.com). If you have another type of printer, this printer may also have drivers on their web site as well.
View full article
Picard Product_Support
‎2018-09-07 12:21 AM

Labels:
  • TAC INET
1057 Views

Will CSI/TAC formatted mag-stripe encoded cards be encoded during the Badge printing process using a datacard printer?

Issue Will CSI/TAC formatted mag-stripe encoded cards be encoded during the Badge printing process using a datacard printer? Environment IDWorks Datacard printer Cause Event Handler ensures that the correct issue level is encoded on the card. Note: there are two version of the Event Handler. Resolution Yes you can, provided you add a plug-in called the "Event Handler" written by Datacard. 
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1258 Views

Does I/NET run on Windows 2000?

Issue Does I/NET run on Windows 2000? Environment I/NET rev 2.20 Windows 2000 Cause At the time of release of Windows 2000, there was concerns about compatibility with existing I/NET installations. Resolution There has been a modification in I/NET revision 2.20 for it to operate with Windows 2000 normally.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
1087 Views

Maximum character length for names in IDWorks

Issue What is the Maximum character length that ID Works software supports? Environment IDWorks video badging system Cause Limitations of the text input fields. Resolution The Maximum character length for the Last name, First name and Field names 1-16 is 50 characters. Any longer names will be truncated.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
913 Views

NPR flashing the LEDs from left to right, cannot open configuration editor

Issue My NPR is flashing the LEDs from left to right, and I cannot get into the configuration editor. Environment NPR Cause It means the NPR is ready for a software restore. Resolution Once you load a bin file, you will be able to configure it.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
841 Views
  • « Previous
    • 1
    • …
    • 257
    • 258
    • 259
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of