Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 414
    • 415
    • 416
    • …
    • 509
  • Next »

Broken Vista IV (Vista 2000) dongle (PSU) replacement.

Issue Over the years, a few dongles (both LPT and USB) has broken for various reasons. Sometimes its internally, other issues has been that they have been exposed to violence (dropped laptops...) and to be able to run the Vista software, the dongles needs to be replaced. Environment Vista IV LPT dongle Enduser 000878560 USB dongle Enduser 000878570 LPT dongle Inhouse, Engineering 000879310 USB dongle Inhouse, Engineering 000879320 Cause Broken dongle (PSU) hardware.  Resolution The Vista IV product portfolio was withdrawn in 2011-12-31, and support is now very limited. It is strongly recommended to upgrade the Vista system to latest possible version in order to secure support possibilities onwards.
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • TAC Vista
1052 Views

When "Exporting Data" from a multi-history chart there are many nan's in the data

Issue When "Exporting Data" from a multi-history chart there are many nan's in the data. Environment I/A Series G3 (Niagara) Cause The timestamp in the history data has a millisecond component that is not shown on the data displays.  When the Export data is displayed history values are provided with the timestamp.  If the timestamps for all the histories samples are exactly the same (to the millisecond) the data value is displayed, if not "nan" is displayed.  Resolution This condition occurs only when the "rollup" for the chart is left at the default of none.  Changing the "rollup" to a value other than none will bring the data into order.  Setting the rollup to the sample interval of the histories gives the best results in the Export data.
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • TAC IA Series
1224 Views

Alarm printer is printing one alarm per page.

Issue Even though the "Suppress form feeds when printing alarms" option is selected in the Workstation Preferences, alarm printer is printing only one alarm per page. Environment CyberStation Alarms Printer Cause The alarm printer is issuing a form feed at the end of every alarm message. Resolution If the "Suppress form feeds when printing alarms" option is set to true in the Workstation Preferences, this issue has to be handled at the printers internal settings by adjusting the page length and other settings. 
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Andover Continuum
1323 Views

"Improper Use of Operand error" in a Plain English Program.

Issue A program turns on an output based on a comparison of a door's forced entry attribute and the value of a schedule numeric.  The program is disabling and throws an error. Environment AC1 AC1 Plus Plain English CyberStation Continuum Cause An Infinity Numeric and the Forced Entry attribute of a Continuum door object are incompatible value types.  Resolution Use an If/Then/Else expression to evaluate the value of the doors Forced Entry attribute, and the Infinity Numeric's value separately.  Then Switch the state of the output based on the result of the evaluation. Original Code   If (AHCASECACC100A ForcedEntry and PerimeterDoors) then Goto AlarmOutputOn Corrected Code   If (AHCASECACC100A ForcedEntry = True) and (PerimeterDoors = On) then Goto AlarmOutputOn
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Andover Continuum
1496 Views

Maximum Import Export entries in Infinet or a CX controller

Issue How many IE entries can Continuum controllers have? Environment CX controllers Infinet controllers Cause Limitations of IE entries in Continuum controllers Resolution Infinet controllers = 255 CX level controllers = 65535
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Andover Continuum
892 Views

The error message "BACnet is not enabled!" is displayed in the Standard Output Window of the UNC when a whoIs is performed in BACnetService.

Issue The error message "BACnet is not enabled!" is displayed in the Standard Output Window of the UNC when a whoIs is performed in BACnetService. No devices are displayed. Environment Niagara R2, UNC-410, UNC-520 Cause The BACnet instance number in the UNC was set at its default of -1. It must be configured with an unique number between 0 - 4,194,302 Resolution Assign the unique instance number for the UNC. Open the UNC’s station and expand its Services container Right-click BACnetService and select Properties Open the General and Config tab Enter a unique number in the Instance Number property and then click Apply The BACnet devices will be populated when a whoIs is performed.
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • TAC IA Series
999 Views

Neuron ID has been lost from Vista System Plug-In

Issue When re-entering the Neuron ID of a controller, an  error appears indicating that this Neuron ID already in use. Environment Vista 4.4.2 Cause If the System Plug-In fails at the time a Xenta controller is being worked on sometimes a default controller is created using the Neuron ID of the controller you were working on. Resolution In the Network management tool look for a device that has a name that does not make sense or follow the site naming convention. When you find this device check the neuron ID to ensure this is the device that has been assigned the Neuron ID of the Xenta device you were working on. When this is confirmed delete this device from the LNS network. Then refresh the LNS side of the System Plug-in and assign the Neuron ID to the Xenta controller you were working on at the time of the crash.
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • TAC Vista
1069 Views

Actuator selection for VTRE valves

Issue Selecting the correct actuator for the VTRE valves. Environment VTRE M9B EM9 Cause The data sheet for VTRE is currently listing the following suitable actuators: M9B-24:  860-1010-000 M9B-230:  860-1020-000 EM9:  860-1110-000 Also, it states the following: "NOTE! The VTRE valves require that the  actuators be adjusted for 90° rotational travel." However, the EM9 listed in the data sheet is 180° rotational. Resolution The correct actuators should be the following: M9B-24:  860-1010-000 M9B-230:  860-1020-000 EM9:  860-1100-000
View full article
Picard Product_Support
‎2018-09-06 12:35 PM

Labels:
  • Field Devices
1061 Views

This alarm is trigged every day "trendlog object...log point can not be read" how do I get rid of it?

Issue This alarm is trigged every day "trendlog object...log point can not be read" how do I get rid of it? The trendlog is a Vista server trendlog logging a point in a Xenta 400 Environment Vista 5.1.6 Cause When a Vista server trendlog is started Vista reads the chosen value according to the log interval, if one reading is missed you will see this alarm. The missed reading could have several reasons but the most common is a bad Lon network or high traffic on the Lon network.  Resolution Investigate why the logged value can't be read, check the Lon network with a analyzer.  
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • TAC Vista
991 Views

Unable to override an ASD point from a Niagara G3 Enterprise Server.

Issue Unable to override an ASD point from a Niagara G3 Enterprise Server. . Environment Niagara G3 Cause TAC/ASD module is missing from Enterprise Server Niagara Modules folder. Resolution Download TAC/ASD module from The Exchange Download Center Download the matching revision module and copy the file in the Niagara Modules folder. Restart the Niagara Service and Workbench to register the module.
View full article
Picard Product_Support
‎2018-09-10 08:56 AM

Labels:
  • TAC IA Series
1371 Views

Rehosting licenses; can both new and old PCs run simultaneously after rehosting?

Issue After the rehost process, is it possible to use both the old and new licenses (PCs) at the same time? Environment TAC Vista 5 Cause After rehosting a license, nothing prevents you from using both the original and new license file at the same time, since there is no feedback from the system that synchronizes the usage of licenses from the same Entitlement. Resolution It is strictly against the license agreement, and should not be used at any time. If a temporary license is required, use the existing demo license files or contact PSS for other temporary solution. 
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • TAC Vista
1081 Views

Is there anything we can do to eliminate the unsolicited messages the UNC is receiving from the attached GCM?

Issue Frequently see Java.lang.Exception errors in the UNC error log or Standard output window that reads, in part,      "At tridiumx.gcm.GcmUnsolicitedReceive.run (bytecode xxx)" Environment I/A Series R2 UNC I/A Series GCM 84xxx or GCM 86xxx connected to UNC Cause The GCM does send unsolicited messages all the time, more or less depending on how you have the logging configured in the GCM. Depending on the source of the message, some will simply be reported to the Standard Output Window as "Unsolicited GCM message received" or "Processing Unsolicited Message"'. Other messages will be reported as a part of an error message written to the Standard Output Window and / or the Error log. Resolution You can minimize these messages by insuring that none of the print groups in the GCM are configured to use the serial port to which the UNC is connected. You also need to confirm that all of the Exception Print Flags in the GCM are set to NO. The remaining messages that cannot be eliminated are almost always GCM Network communications protocol messages that have no meaning to the UNC.  
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • TAC IA Series
1126 Views

Does Niagara R2 use SSL (Secure Sockets Layer)?

Issue An end customer wants to use SSL on his Niagara R2 control system.  Is it supported? Environment Niagara R2 Cause Security policy changes by end customer's IT department Resolution SSL is not supported in the Niagara R2 environment.
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • TAC IA Series
1215 Views

How to install / add WebClient to existing SU installation of Continuum.

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue How to install / add WebClient to existing SU installation of Continuum. Environment Continuum WebClient Cause Existing Continuum SU Cyberstation installed and site is being upgraded with WebClient support. Resolution Perform the following steps to install WebClient on your Single-User installation. Backup the ContinuumDB, Graphics files, and Menus to a safe location. (For detailed steps on how to backup / restore your ContinuumDB see here.) Upgrade security key to allow WebClient. (from supplied serialized upgrade code from Repairs) Uninstall Continuum. Install WebClient from scratch following the Planning and Installation Guide. (IIS then WebClient) Restore your ContinuumDB, graphics files and Menus. Test
View full article
Picard Product_Support
‎2018-09-10 07:47 AM

Labels:
  • Andover Continuum
1560 Views

Get energy consumption based on user input.

Issue The customer have some rooms with consumption logs. The customer wants to easily select from and to date, and then be presented with the total consumption in this period. Is this possible in Vista? Environment TAC Vista 5.1.7 Cause You can't do any programming in any objects in Vista(except java script) which you need here. There is no standard object in Vista doing what the customer want.   Resolution It would be possible to do using a report but then the customer need to create a new report where the trendlog and the input dates is specified every time he need the energy consumption for a certain period. This is not really what the customer requests so no this is not possible in Vista today.  
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • TAC Vista
1292 Views

Sigma - Logging off one user, logs another user on.

Issue Logging off one user, logs another user on. Environment Sigma Users Logon Logoff Cause When a specific user logs off  the Sigma system, another user is logged onto the system. Resolution This issue is caused by corruption of the GenCNF.rec and user files, there are two options available. Locate a backup of the system files that was taken before the corruption occurred. Shutdown the Sigma server and all clients. Copy the GenCNF.rec file and the User folder from the system backup. Paste the copied files into the Data folder. Restart the Sigma server and clients. Test the user access operation. Rename the corrupted user. System users cannot be deleted, they can only be re-named. In the Sigma SSM / Users, highlight the User name and select to rename it Rename the user to an appropriate name. Create a new user to replace the old user, allocate the correct access levels. Test the user access operation.
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • Satchwell BAS & Sigma
898 Views

When changing name of a trendlog in Vista will the name of the trendlog in the SQL server also change?

Issue When changing name of a trendlog in Vista will the name of the trendlog in the SQL server also change? This is when using Vista 5.1.7 and have upgraded the SQL database. Environment TAC Vista 5.1.7 Cause The name of the trendlog in the SQL database will change when the next value for that trendlog is written in to the SQL database. Resolution The name of the trendlog in the SQL database will change when the next value for that trendlog is written in to the SQL database
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • TAC Vista
908 Views

SPD310/SPD360, value outside of selected measurement range

Issue What happens with the output VDC value if the measured value goes outside of the specified range?  Environment SPD310 SPD360 Cause The selected value is specified by the position of the jumper. Signal output is set to 0-10V. Resolution If jumper is set to 500Pa and read value exceeds this value, the output signal will still show 10VDC. Any control signal above 10VDC is marginal, and should not be used as a measurement reference.
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • Field Devices
876 Views

Sigma - Remote client will not start and generates an error.

Issue When to  Sigma Remote Client is started a Runtime Error is reported, the error is as follows; Programme c:\Sigma\Bin\Sigop.exe - Application requested runtime to terminate in an unusual way. When OK is selected, the following is returned Software exception 0x40000015 occurred in this application at location 0x7857bb47   Environment Sigma Remote Client Error Cause The incorrect Sigma Client software has been installed onto the remote client PC. Resolution The site has Sigma 4.05 SEB software installed, but the Remote Client had been loaded with Sigma 4.06. Note - Sigma software releases cannot be mixed across Sigma Client/Servers and Remote Clients, therefore before adding a new Remote Client to a system, the existing site software must be established. To establish the current release of software, go to the Sigma System Manager, select "Help" and "About Sigma", there you will find the Sigma build number.  
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • Satchwell BAS & Sigma
1083 Views

Vista Workstation crashes when the content of a column in any View exceeds 259 characters.

Issue Vista Workstation crashes when the content of a column in any View (Alarms, Events, Search Results etc.) exceeds 259 characters. Environment Vista 5.1.7 Cause In the unlikely event that the content of a column in a Vista View exceeds a limit of 259 characters, Vista Workstation crashes and must be restarted.  Vista Server is not affected. The problem was discovered while doing a search for TGML graphics, with the property "Bindings" selected.  The search returns one graphic on each row and all the bindings for that graphic are displayed in the property column on that row.  Resolution Upgrade to Vista 5.1.8, when available.  The issue is fixed by truncating the contents of any View column to 259 characters. The issue is highly unlikely to occur in normal use.  In the case of the Bindings search, the workaround is to use the "Change Reference" tool instead
View full article
Picard Product_Support
‎2018-09-06 12:34 PM

Labels:
  • TAC Vista
832 Views
  • « Previous
    • 1
    • …
    • 414
    • 415
    • 416
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of