A program turns on an output based on a comparison of a door's forced entry attribute and the value of a schedule numeric.  The program is disabling and throws an error.
  • AC1
  • AC1 Plus
  • Plain English
  • CyberStation
  • Continuum
An Infinity Numeric and the Forced Entry attribute of a Continuum door object are incompatible value types.
Use an If/Then/Else expression to evaluate the value of the doors Forced Entry attribute, and the Infinity Numeric's value separately.  Then Switch the state of the output based on the result of the evaluation.
Original Code
  If (AHCASECACC100A ForcedEntry and PerimeterDoors) then Goto AlarmOutputOn
Corrected Code
  If (AHCASECACC100A ForcedEntry = True) and (PerimeterDoors = On) then Goto AlarmOutputOn