The error message "BACnet is not enabled!" is displayed in the Standard Output Window of the UNC when a whoIs is performed in BACnetService.
  • The error message "BACnet is not enabled!" is displayed in the Standard Output Window of the UNC when a whoIs is performed in...
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 12:35 PM
The error message "BACnet is not enabled!" is displayed in the Standard Output Window of the UNC when a whoIs is performed in BACnetService. No devices are displayed.
Niagara R2, UNC-410, UNC-520
The BACnet instance number in the UNC was set at its default of -1. It must be configured with an unique number between 0 - 4,194,302
Assign the unique instance number for the UNC.
  1. Open the UNC’s station and expand its Services container
  2. Right-click BACnetService and select Properties
  3. Open the General and Config tab
  4. Enter a unique number in the Instance Number property and then click Apply
The BACnet devices will be populated when a whoIs is performed.