SPD310/SPD360, value outside of selected measurement range
  • SPD310/SPD360, value outside of selected measurement range
  • SESA150559
    SESA150559
‎2018-09-06 12:34 PM
What happens with the output VDC value if the measured value goes outside of the specified range?
SPD310
SPD360
The selected value is specified by the position of the jumper. Signal output is set to 0-10V.
If jumper is set to 500Pa and read value exceeds this value, the output signal will still show 10VDC. Any control signal above 10VDC is marginal, and should not be used as a measurement reference.
  • Field Devices
  • 7523