Actuator selection for VTRE valves
  • Actuator selection for VTRE valves
  • SESA150559
    SESA150559
‎2018-09-06 12:35 PM
Selecting the correct actuator for the VTRE valves.
VTRE
M9B
EM9
The data sheet for VTRE is currently listing the following suitable actuators:
M9B-24:  860-1010-000
M9B-230:  860-1020-000
EM9:  860-1110-000
Also, it states the following:
"NOTE! The VTRE valves require that the
 actuators be adjusted for 90° rotational travel."
However, the EM9 listed in the data sheet is 180° rotational.
The correct actuators should be the following:
EM9:  860-1100-000
  • Field Devices
  • 7498