Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Field Devices
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "field devices"

View in: "Building Automation Knowledge Base" | Community

721 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 35
    • 36
    • 37
  • Next »
Label: "Field Devices" Show all articles

SVT Controller will not operate plant under Auto control following Clock replacement due to lack of re-commissioning.

Issue SVT Controller will not operate plant under Auto control following Clock replacement Environment SVT 4201 Optimiser Controller  SVT 4251 Optimiser Controller  Cause SVT Controller will not operate plant under Auto control following Clock replacement due to lack of re-commissioning. Resolution Re-commission SVT Controller using Test method. The absence of plant control may normally be confirmed by lack of illumination of Burner L E D (bottom left corner of SVT)  Test method of re-commissioning may be undertaken as follows: Ensure SVT 4201 Analogue Clock override button is set to AUTO condition and Clock is in an ON period. Ensure SVT 4251 Digital Clock status is set to AUTO condition and Clock is in an ON period. Ensure SVT Manual Override Switch (lower left of SVT) is set to AUTO Note SVT Preheat Selector Switch (lower centre of SVT) setting (scaled 1,2,3,4,5,T) Turn Preheat Selector Switch fully clockwise from Preheat number setting to letter T Turn Manual Override Switch fully anti-clockwise from AUTO setting to O (Off)  Turn Manual Override Switch fully clockwise from O (Off) setting to + (ON) Burner L E D should illuminate and plant should start. Turn Manual Override Switch anti-clockwise from + (ON) setting to AUTO Burner L E D should remain illuminated and plant should continue to run. If plant continues to run then proceed to action L.  If plant remains OFF then return to action A. Turn Preheat Selector Switch anti-clockwise from T position to previously noted SVT Preheat Selector Switch setting.  
View full article
Picard Product_Support
‎2018-09-07 02:16 PM

on ‎2018-09-07 02:16 PM

Labels:
  • Field Devices
1600 Views

CSC 5 Series Climatronic Compensator Controller Battery missing when Controller supplied.

Issue CSC 5 Series Climatronic Compensator Controller Battery missing when Controller supplied. Environment CSC 5 Series Climatronic Compensator Controllers. Cause CSC 5 Series Climatronic Compensator Controllers - not all specifications require a Battery to be fitted.  CSC 5252 Climatronic Compensator Controller - has no Clock and therefore requires no Battery to be fitted. CSC 5352 Climatronic Compensator Controller - has a Clock and therefore requires a Battery to be fitted. CSC 5352 Climatronic Compensator Controller - Battery should be packed with Controller when new. The Battery (3.6V Lithium AA) is required to power the Clock whilst the Controller is powered OFF for a period of typically 1 year of continuous use. The typical shelf life of the Battery is 10 years. Resolution If CSC 5252 Climatronic Compensator Controller is to be installed then no Battery is required. If CSC 5352 Climatronic Compensator Controller is to be installed then Battery should be fitted. If CSC 5352 Climatronic Compensator Controller Battery is not packed with Controller then its absence should be reported to the supplier. Please check the catalog for current equipment
View full article
Picard Product_Support
‎2018-09-07 02:08 PM

on ‎2018-09-07 02:08 PM

Labels:
  • Field Devices
1167 Views

Satchwell FEU 4-port Unit Control Valve Open / Close status required relative to spindle position.

Issue Satchwell FEU 4-port Unit Control Valve Open / Close status required relative to spindle position.  Environment Satchwell FEU 2, 4, 5 and 6 Series 4-port Unit Control Valve installations. Cause Open / Close status of Satchwell FEU 4-port Unit Control Valve is not visually apparent  Resolution Observe Satchwell FEU 4-port Unit Control Valve spindle position. FEU 2 Series  =  Spindle UP OPEN / Spindle DOWN CLOSE FEU 4, 5 and 6 Series  =  Spindle DOWN OPEN / Spindle UP CLOSE
View full article
Picard Product_Support
‎2018-09-06 02:11 PM

Labels:
  • Field Devices
1626 Views

DC1100 / DC1400 displays identical temperatures for all connected Sensors. It is not uncommon for a temperature of 39 deg C to be displayed for each Sensor connected to the Controller

Issue DC1100 / DC1400 displays identical temperatures for all connected Sensors.  It is not uncommon for a temperature of 39 deg C to be displayed for each Sensor connected to the Controller. Environment DC1100 Stand Alone Optimiser / Compensator Controller DC1400 Stand Alone Optimiser / Compensator Controller Sensors compatible with DC1100 :- A701 Room Temperature Sensor A702 Outside Air Temperature Sensor A703 Pipe Temperature Sensor A704 Contact Temperature Sensor STC 600 D Contact Temperature Sensor           (Original Drayton Sensor = A704) STO 600 D Outside Air Temperature Sensor      (Original Drayton Sensor = A702) STP 600 D Pipe Temperature Sensor                 (Original Drayton Sensor = A703) STR 600 D Room Temperature Sensor              (Original Drayton Sensor = A701) Sensors compatible with DC1400 :- STC 600 Contact Temperature Sensor               (Original Satchwell Sensor = DST) STO 600 Outside Air Temperature Sensor          (Original Satchwell Sensor = DOT)    STP 660 Pipe Temperature Sensor                     (Original Satchwell Sensor = DWT) STR 600 Room Temperature Sensor                  (Original Satchwell Sensor = DRT) 39 deg C. Cause DC1100 / DC1400 displays identical temperatures for all connected Sensors.  A Sensor temperature of 39 deg C is a common value displayed. Resolution Check each Sensor is correctly connected to its appropriate "Common" Terminal of the DC1100 / DC1400 Wiring Base Check each Sensor Cable Screen is correctly connected to the Earth Terminal of the DC1100 / DC1400 Wiring Base Check that a good Earth connection exists between the Earth Terminal of the DC1100 / DC1400 Wiring Base and the site Earth Check that a good site Earth is available for connection to the DC1100 / DC1400 Wiring Base. N.B. In the event that the DC1100 / DC1400 continues to display identical temperatures for all connected Sensors following completion of the above checks then it is suggested that the Cold Start procedure is applied to the Controller and the result observed.
View full article
Picard Product_Support
‎2018-09-06 01:20 PM

Labels:
  • Field Devices
1528 Views

S-E VZ29 / VZ39 / VZ49 Valve Body produces excessive let by due to S-E MZ20 series Actuator Manual Override set to value other than ZERO.

Issue S-E VZ29 / VZ39 / VZ49 Valve Body produces excessive let-by.   Environment S-E VZ29 2-port Valve Body controlled by S-E MZ20 series Actuator. S-E VZ39 3-port Valve Body controlled by S-E MZ20 series Actuator. S-E VZ49 4-port Valve Body controlled by S-E MZ20 series Actuator. Cause S-E MZ20 series Actuator Manual Override set to value other than ZERO Resolution 1.  Check S-E MZ20 series Actuator Manual Override facility is set to ZERO. 2.  If S-E MZ20 series Actuator Manual Override facility is set to ZERO then investigate Valve Body condition / duty compatibility. Instances of excessive let-by experienced with S-E Valve Bodies from the VZ29 / VZ39 / VZ49 family may result from the setting of the Manual Override facility on the S-E MZ20 series Actuator controlling it, rather than the Valve Body itself. S-E MZ20A and MZ20B Actuators include a Manual Override facility, comprising a screw, accessed through a hole in the top of the Actuator, which may be raised and lowered by means of a 3mm Allen Key inserted through the hole in the top of the Actuator. The Manual Override position is required to be set to ZERO upon manufacture.  If the screw is not set to the ZERO position prior to dispatch however, then this may result in the Valve Spindle being depressed by the amount of Manual Override applied. Where a Valve Body is letting by excessively, then initially the Actuator Manual Override setting should be checked and reset to ZERO if necessary.  
View full article
Picard Product_Support
‎2018-09-06 02:37 PM

Labels:
  • Field Devices
1561 Views

Replacement of Satchwell VSF or VJF Valve Body controlled by Satchwell Spring Return Actuator due to obsolescence.

Issue Satchwell VSF or VJF Valve Body controlled by Satchwell Spring Return Actuator requires replacement. Environment Satchwell VSF or VJF Valve Body installed in Water or Steam Control Valve applications. Cause Obsolescence of Satchwell VSF or VJF Control Valve Body. Resolution STEAM APPLICATION 1.  Replace Satchwell VSF or VJF Valve Body with S-E Two-Port Flanged Valve Body. Where an existing Satchwell VSF or VJF Valve Body is utilised in a STEAM application, then the VSF or VJF Valve Body should be replaced by a suitably sized S-E VGS211F Valve Body, thus enabling steam having a steam inlet pressure up to 1300 kPa and a temperature up to 200 deg C to be controlled. It should be noted however that the face-to-face dimension and overall dimensions of each S-E Valve Body will differ to those of the Satchwell VSF or VJF Valve Body. It should also be noted that the operation of the VGS211F Valve Spindle is the reverse of that of the VSF or VJF Valve Spindle. When the VGS211F Valve Spindle is UP, or in the fully extended position, then the Valve is OPEN. Similarly, when the VGS211F Valve Spindle is DOWN, or in the fully retracted position, then the Valve is CLOSED This will therefore result in the need to replace the existing Satchwell Actuator with the correct model of S-E M700 Actuator, in order to ensure the correct operation of the Valve Body in the event of electrical power failure. It is important that the above limitations are recognised when replacing a Satchwell VSF or VJF Valve Body with a S-E VGS211F Valve Body in retrofit projects. Such limitations do not apply to new projects where a new S-E VGS211F Valve Body and a new S-E  M700 Actuator are being selected, providing of course that an Actuator having the correct spring action in the event of electrical power failure is selected. N.B. Steam Control Valves are normally required to CLOSE in the event of electrical power failure. In the case of the S-E VGS211F therefore the S-E M700 SRSD Actuator should be selected. WATER APPLICATION 1.  Replace Satchwell VSF or VJF Valve Body with S-E Two-Port Flanged Valve Body. A number of alternative models of S-E Two-Port Flanged Valve Bodies are available to replace existing Satchwell VSF or VJF Two-Port Flanged Valve Bodies. It should be noted however that the face-to-face dimension and overall dimensions of each S-E Valve Body will differ to those of the Satchwell VSF or VJF Valve Body.  
View full article
Picard Product_Support
‎2018-09-06 02:42 PM

on ‎2018-09-06 02:42 PM

Labels:
  • Field Devices
2006 Views

Replacement of Satchwell DRT3451 Adjustable Room Temperature Sensor by S-E STR612.

Issue Replacement of Satchwell DRT3451 Adjustable Room Temperature Sensor by S-E STR612. Environment Satchwell DRT3451 Adjustable Room Temperature Sensor installations. Cause Obsolescence of Satchwell DRT3451 Adjustable Room Temperature Sensor Resolution Replace Satchwell DRT3451 Adjustable Room Temperature Sensor with S-E STR612 The STR612 provides the same functionality as the DRT3451 differing only in its appearance, dimensions and terminal identification. Equivalent terminal identification is as follows STR612 Terminal 22 (A) = DRT3451 Terminal A STR612 Terminal 23 (C) = DRT3451 Terminal C Connection of STR612 to CZU Fan Coil Unit Temperature Controller STR612 Terminal 22 (A) – connect to CZU Terminal 9 STR612 Terminal 23 (C) – connect to CZU Terminal 10 (CZU Setpoint should be set to 10 deg C)
View full article
Picard Product_Support
‎2018-09-06 02:42 PM

on ‎2018-09-06 02:42 PM

Labels:
  • Field Devices
1588 Views

DC1100 & DC1400 Optimiser / Compensator Controller Cold Start .

Issue DC1100 & DC1400 Optimiser / Compensator Controller Cold Start malfunction. Environment DC1100 Optimiser / Compensator Controller. DC1400 Optimiser / Compensator Controller Cause DC1100 & DC1400 Optimiser / Compensator malfunction preventing Cold Start procedure being undertaken.. Resolution 1.  Repeat DC1100 & DC1400 Controller Cold Start procedure. A manufacturing problem experienced with the DC1100 and DC1400 may result in difficulty applying the Cold Start procedure. Faults have been reported in respect of a number of DC1100 Controllers in particular, where difficulty has been experienced when applying the Cold Start procedure. The fault appears in those Controllers where the Enter and Exit Keys foul their respective cut-outs in the Top Cover Panel, thus preventing Cold Start from being achieved. This is due to a conflict in assembly tolerances that can cause the Keys to remain depressed after they have been pressed in, due to their being trapped by the cut-outs they should pass through. In such instances it may be necessary to undertake the Cold Start procedure a number of times before any trapped Key is released sufficiently to enable resetting of the Controller to be achieved. Actions are currently in hand to rectify this matter and the positioning of the cut-outs in the Top Cover Panel relative to the Key positions has been addressed from a design point of view. Examples of the Top Cover Panel incorporating newly dimensioned cut-outs are not due to be available for inclusion in production assemblies until Week Number 2010 45 at the earliest however. Consequently current production assemblies incorporating the existing Top Cover Panel will continue to be utilised in all newly manufactured Controllers for the moment at least. Similarly an opportunity will not arise until Week 2010 45 for any Controllers currently held in stock in S-E Sweden to be re-worked to include the new Top Cover Panel prior to their sale.
View full article
Picard Product_Support
‎2018-09-06 02:41 PM

on ‎2018-09-06 02:41 PM

Labels:
  • Field Devices
2608 Views

S-E MD20 Actuator Clamp Drive Shaft Clip fouling LMD/AR-MBF Linkage Kit Mounting Platform inhibits Actuator rotation.

Issue S-E MD20 Actuator Clamp Drive Shaft Clip fouling LMD/AR-MBF Linkage Kit Mounting Platform inhibits Actuator rotation. Environment S-E MD20 Actuator installed on Satchwell MBF Valve Body. Cause S-E MD20 Actuator Clamp Drive Shaft Clip cut out undersized. Resolution Measure diameter of S-E MD20 Actuator Clamp Drive Shaft Clip cut out. S-E MD20 Actuator Clamp Drive Shaft Clip cut out diameter should be 47mm Replace S-E MD20 Actuator Clamp Drive Shaft Clip with another having modified cut out if dimension less than 47mm. The diameter of the cut out in the original LMD/AR-MBF Linkage Kit Mounting Platform was such that the MD20 Actuator Drive Shaft Clip could be prevented from turning freely with the Drive Shaft. The LMD/AR-MBF Mounting Platform was modified in August 2007, when the diameter of the cut out in the Mounting Platform was increased to 47mm, thus overcoming the fouling of the MD20 Actuator Drive Shaft Clip. It is possible to ascertain whether the LMD/AR-MBF Mounting Platform in use is of the original or modified design by measuring the diameter of the cut out in the Mounting Platform If the diameter of the LMD/AR-MBF Mounting Platform cut out is less than 47mm, then the MD20 Actuator Drive Shaft Clip will foul the LMD/AR-MBF Mounting Platform. The MD20 Actuator Drive Shaft Clip however is retained in a groove within the Drive Shaft and whilst the Clip may be prevented from turning freely with the Drive Shaft, the turning of the Drive Shaft itself will not be impeded.
View full article
Picard Product_Support
‎2018-09-06 02:37 PM

on ‎2018-09-06 02:37 PM

Labels:
  • Field Devices
1469 Views

TAC Valve Body published Cv values may differ markedly to equivalent Kv values due to use of Cv values based on US Gallons per minute rather than U.K. Gallons per minute.

Issue TAC Valve Body published Cv values may differ markedly to equivalent Kv values.  Environment TAC Valve Body published data utilised when sizing and selecting S-E / TAC Control Valves. Cause TAC Valve Body published Cv values based on flow rates measured in U.S. Gallons per minute rather that U.K.Gallons per minute., Resolution Check published Cv value relative to published Kv value stated for TAC Valve Body. If published Cv value is within 3% of published Kv value then Cv value may be used for sizing / selection of Valve Body. If published Cv value is up to 17% higher than Kv value then Cv value should not be used for sizing / selection of Valve Body. Cv values published in older TAC Valve Body Data Sheets should be checked before considering use in U.K. valve sizing formula. Numerous TAC Valve Body Data Sheets show that for a particular Kv value, the equivalent Cv value is approximately 17% higher than the Kv value. For example, where TAC Valve Body Data Sheet shows Kv = 10, then equivalent Cv = 11.7 or in other words Cv = Kv x 1.17 Cv values published in Satchwell Valve Body Data Sheets however show the relationship between Kv and Cv as:- Kv = Cv x 1.03 or in other words Cv = Kv x 0.97 This difference in equivalent values is due to Cv values stated in some TAC Data Sheets being based on flow rates measured in U.S. Gallons per minute, while those Cv values stated in Satchwell Data Sheets however are based on flow rates measured in U.K. Gallons per minute. If flow rates are measured in U.S. Gallons per minute, then the following conversion factor applies :- Kv = Cv x 0.86, as the U.S. Gallon is smaller than the U.K. Gallon. Taking published TAC Valve Body Data Sheet information therefore, where the Cv value is stated as 11.7 and the Kv value is stated as 10, confirms that the conversion factor Kv = Cv x 0.86 ( 11.7 x 0.86 = 10 ) has been applied, further confirming that published Cv values are in fact based on U.S. Gallons and not U.K. Gallons. Consequences of this are as follows : - If it is assumed that the published Cv value is a U.K. Cv value, when in fact it is a U.S. Cv value, and the published Cv value is then used as a basis for valve sizing and selection, then this will result in a smaller Valve Body being selected than would otherwise be the case. Consequently, once installed, the selected Valve Body will produce a much higher pressure drop and correspondingly higher authority for a given flow rate than would otherwise have been the case. In practice the installation of an undersized Control Valve can result in starvation of flow to the item of plant being controlled and the potentially costly replacement of the Valve Body for another of a larger size. Similarly, the installation of an undersized Control Valve will result in a greater pressure drop being applied to the hydraulic circuit than may be desirable and could lead to an adverse effect on the performance of the associated circulating pump. It is important to ensure therefore that where both Kv and Cv values are published for a given Valve Body, the Kv value is utilised when undertaking valve sizing and selection.  This should ensure that a Valve Body of the correct size is selected. Measures are currently in place to actively remove all references to Cv values from both S-E / TAC Data Sheets and all future editions of the S-E HVAC Valves and Actuators Catalogue.
View full article
Picard Product_Support
‎2018-09-06 02:37 PM

on ‎2018-09-06 02:37 PM

Labels:
  • Field Devices
1718 Views

Actuator not Tracking Control Signal

Issue Actuator not Tracking Control Signal. Environment Actuator typically controlling a damper or valve Cause This problem is usually traced to one of three common problems: Insufficient power to initialize actuator. Incorrect control signal. Actuator is bound. Resolution Verify the associated troubleshooting/resolutions with reference to the numbered causes above: Insufficient power to initialize actuator. Verify transformer capacity is above required power up inrush load. To determine if this is the problem, check published VA requirement. When multiple devices are powered from a common transformer, disconnect all other devices from transformer output or use isolated transformer. Incorrect control signal. Verify correct control signal is selected for the actuator. Verify actuator operation by using a Loop Calibrator such as the Fluke 789 to simulate the control signal. If the actuator tracks the simulated signal, the problem is at the controller or in the wiring. Actuator is bound. Verify actuator motion matches the controlled device. Is the actuator trying to close a valve or damper that is already closed?
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

on ‎2018-09-06 02:31 PM

Labels:
  • Field Devices
1711 Views

TS-57XX-85X and TS-67XX-85X 10K thermistor with 11 K shunt resistance table

Issue TS-57XX-85X and TS-67XX-85X 10K thermistor with 11 K shunt resistance table Environment Unknown Environment Cause Unknown Cause Resolution Temp (°C) Temp (°F) Ohms (11K shunt)   -40.0°     -40.0°   10,517   -39.0°     -38.2°   10,489   -38.0°     -36.4°   10,460   -37.0°     -34.6°   10,430   -36.0°     -32.8°   10,397   -35.0°     -31.0°   10,364   -34.0°     -29.2°   10,329   -33.0°     -27.4°   10,292   -32.0°     -25.6°   10,254   -31.0°     -23.8°   10,214   -30.0°     -22.0°   10,172   -29.0°     -20.2°   10,129   -28.0°     -18.4°   10,084   -27.0°     -16.6°   10,037   -26.0°     -14.8°   9,988   -25.0°     -13.0°   9,938   -24.0°     -11.2°   9,885   -23.0°     -9.4°   9,830   -22.0°     -7.6°   9,773   -21.0°     -5.8°   9,715   -20.0°     -4.0°   9,654   -19.0°     -2.2°   9,592   -18.0°     -0.4°   9,527   -17.0°     1.4°   9,460   -16.0°     3.2°   9,391   -15.0°     5.0°   9,320   -14.0°     6.8°   9,247   -13.0°     8.6°   9,171   -12.0°     10.4°   9,094   -11.0°     12.2°   9,015   -10.0°     14.0°   8,933   -9.0°     15.8°   8,850   -8.0°     17.6°   8,764   -7.0°     19.4°   8,677   -6.0°     21.2°   8,587   -5.0°     23.0°   8,495   -4.0°     24.8°   8,402   -3.0°     26.6°   8,307   -2.0°     28.4°   8,210   -1.0°     30.2°   8,111   0.0°     32.0°   8,012   1.0°     33.8°   7,910   2.0°     35.6°   7,807   3.0°     37.4°   7,702   4.0°     39.2°   7,595   5.0°     41.0°   7,489   6.0°     42.8°   7,380   7.0°     44.6°   7,270   8.0°     46.4°   7,160   9.0°     48.2°   7,048   10.0°     50.0°   6,937   11.0°     51.8°   6,825   12.0°     53.6°   6,711   13.0°     55.4°   6,597   14.0°     57.2°   6,483   15.0°     59.0°   6,369   16.0°     60.8°   6,255   17.0°     62.6°   6,141   18.0°     64.4°   6,027   19.0°     66.2°   5,912   20.0°     68.0°   5,798   21.0°     69.8°   5,686   22.0°     71.6°   5,572   23.0°     73.4°   5,460   24.0°     75.2°   5,348   25.0°     77.0°   5,238   26.0°     78.8°   5,127   27.0°     80.6°   5,018   28.0°     82.4°   4,909   29.0°     84.2°   4,802   30.0°     86.0°   4,696   31.0°     87.8°   4,591   32.0°     89.6°   4,487   33.0°     91.4°   4,385   34.0°     93.2°   4,284   35.0°     95.0°   4,184   36.0°     96.8°   4,086   37.0°     98.6°   3,989   38.0°     100.4°   3,894   39.0°     102.2°   3,800   40.0°     104.0°   3,707   41.0°     105.8°   3,617   42.0°     107.6°   3,528   43.0°     109.4°   3,441   44.0°     111.2°   3,355   45.0°     113.0°   3,271   46.0°     114.8°   3,189   47.0°     116.6°   3,107   48.0°     118.4°   3,028   49.0°     120.2°   2,951   50.0°     122.0°   2,875   51.0°     123.8°   2,801   52.0°     125.6°   2,729   53.0°     127.4°   2,658   54.0°     129.2°   2,588   55.0°     131.0°   2,521   56.0°     132.8°   2,455   57.0°     134.6°   2,390   58.0°     136.4°   2,327   59.0°     138.2°   2,266   60.0°     140.0°   2,206   61.0°     141.8°   2,148   62.0°     143.6°   2,091   63.0°     145.4°   2,036   64.0°     147.2°   1,982   65.0°     149.0°   1,929   66.0°     150.8°   1,878   67.0°     152.6°   1,827   68.0°     154.4°   1,779   69.0°     156.2°   1,732   70.0°     158.0°   1,685   71.0°     159.8°   1,640   72.0°     161.6°   1,597   73.0°     163.4°   1,554   74.0°     165.2°   1,513   75.0°     167.0°   1,472   76.0°     168.8°   1,433   77.0°     170.6°   1,395   78.0°     172.4°   1,359   79.0°     174.2°   1,322   80.0°     176.0°   1,287   81.0°     177.8°   1,253   82.0°     179.6°   1,220   83.0°     181.4°   1,188   84.0°     183.2°   1,157   85.0°     185.0°   1,126   86.0°     186.8°   1,097   87.0°     188.6°   1,068   88.0°     190.4°   1,040   89.0°     192.2°   1,013   90.0°     194.0°   987   91.0°     195.8°   961   92.0°     197.6°   936   93.0°     199.4°   912   94.0°     201.2°   888   95.0°     203.0°   865   96.0°     204.8°   843   97.0°     206.6°   821   98.0°     208.4°   800   99.0°     210.2°   780   100.0°     212.0°   760   101.0°     213.8°   741   102.0°     215.6°   722   103.0°     217.4°   704   104.0°     219.2°   686   105.0°     221.0°   669   106.0°     222.8°   652   107.0°     224.6°   636   108.0°     226.4°   620   109.0°     228.2°   605   110.0°     230.0°   590   111.0°     231.8°   576   112.0°     233.6°   561   113.0°     235.4°   548   114.0°     237.2°   534   115.0°     239.0°   521   116.0°     240.8°   509   117.0°     242.6°   496   118.0°     244.4°   484   119.0°     246.2°   473   120.0°     248.0°   462   121.0°     249.8°   451
View full article
Picard Product_Support
‎2018-09-06 02:31 PM

on ‎2018-09-06 02:31 PM

Labels:
  • Field Devices
2544 Views

Which NEMA 4 classed DuraDrive actuators can be used with the VB-7323 diverting valves

Issue NEMA 4 classed DuraDrive actuators cannot be used with the VB-7323 diverting valves Environment NEMA 4 DuraDrive actuators VB-7323 diverting valves Cause Which NEMA 4 classed DuraDrive actuators can be used with the VB-7323 diverting valves Resolution There are no NEMA 4 solutions available. Consider using the MA-318 or 481 for two position applications. No modulating spring return options are available but non-spring return gear train actuators with AV-391 (150 pound plungers) can be used when the AM-363 gasket is added.
View full article
Picard Product_Support
‎2018-09-06 02:30 PM

on ‎2018-09-06 02:30 PM

Labels:
  • Field Devices
1702 Views

Replacement of Satchwell ALX series Linear Actuator by S-E MV15B-24 Linear Actuator due to obsolescence. (Actuator Selection)

Issue Satchwell ALX series Linear Actuator requires replacement. Environment Satchwell ALX series Linear Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body. Cause Obsolescence of Satchwell ALX series Linear Actuator. Resolution Replace Satchwell ALX series Linear Actuator with MV15B-24 Linear Actuator and Linkage Kit :-  ALX = MV15B-24 + L7SV (880-0662-000). Note: this part no. is for both actuator and linkage kit.  N.B.  Should the Satchwell ALX series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the MV15B-24 Actuator as appropriate :-  S2 – MV15B = Two independent 250 volt 10 amp / 3 amp rated SPDT Auxiliary End Point Switches.    Particular care should be taken when selecting an S-E Forta MV15B-24 Actuator to replace an existing Satchwell ALX series Actuator. The S-E MV15B-24 Actuator may be used to replace an existing Satchwell ALX series Actuator but it should be noted that where an existing Satchwell ALX series Actuator has been connected directly to a Satchwell Controller, an independent Transformer rated to provide the greater level of power required by a single S-E MV15B -24 Actuator (12VA) will also be required. (e.g. S-E Transformer Type TR32)  Where an existing Satchwell ALX series Actuator has been connected via an independent Transformer, it is possible that the Transformer may have been rated to provide the level of power required by a single ALX series Actuator (3.5VA) only. In such circumstances the existing independent Transformer may also require replacement by another independent Transformer, rated to provide the greater level of power required by a single S-E MV15B-24 Actuator (12VA) (e.g. S-E Transformer Type TR32)
View full article
Picard Product_Support
‎2018-09-06 02:06 PM

on ‎2018-09-06 02:06 PM

Labels:
  • Field Devices
2175 Views

Replacement of Satchwell ALM series Linear Actuator by S-E MV15B-230 Linear Actuator due to obsolescence. (Actuator Selection)

Issue Satchwell ALM series Linear Actuator requires replacement. Environment Satchwell ALM series Linear Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF Series Plug and Seat Valve Body. Actuator type :- ALM series Cause Obsolescence of Satchwell ALM series Linear Actuator. Resolution Replace Satchwell ALM series Linear Actuator with MV15B-230 Linear Actuator and Linkage Kit :-  ALM = MV15B-230 + L7SV (880-0126-000) Linkage Kit N.B.  Should the Satchwell ALM series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the MV15B-230 Actuator as appropriate :-  S2 – MV15B = Two independent 250 volt 10 amp / 3 amp rated SPDT Auxiliary End Point Switches.
View full article
Picard Product_Support
‎2018-09-06 02:06 PM

on ‎2018-09-06 02:06 PM

Labels:
  • Field Devices
2122 Views

Replacement of Satchwell AR Series 1 or AR Series 2 Rotary Actuator by S-E MD Series Rotary Actuator due to obsolescence. (Actuator Wiring)

Issue Satchwell AR Series 1 or AR Series 2 Rotary Actuator requires replacement Environment Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MB Series or MBF Series Rotary Shoe Valve Bodies. Satchwell ARE ARM & ARX Series 1 and Series 2 Rotary Actuators Cause Obsolescence of Satchwell AR Series 1 or AR Series 2 Rotary Actuators Resolution Replace Satchwell AR Series 1 or AR Series 2 Rotary Actuators with appropriate S-E MD Series Rotary Actuators and wire as follows: Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MB Series Screwed Rotary Shoe Valve Bodies ARE ARE Series 1 & 2 Wire Colour BLUE  =  MD10A-24 or MD20A-24 Wire Number 2 ARE Series 1 & 2 Wire Colour RED  =  MD10A-24 or MD20A-24  Wire Number 3 ARE Series 1 & 2 Wire Colour BLACK  =  MD10A-24 or MD20A-24  Wire Number 1 ARE Series 2        Wire Colour WHITE  =  MD10A-24 or MD20A-24  Wire Number 5  ARX ARX Series 1 & 2 Wire Colour RED  =  MD10B-24 or MD20B-24 Wire Number 3 ARX Series 1 & 2 Wire Colour BLUE  =  MD10B-24 or MD20B-24  Wire Number 2 ARX Series 1 & 2 Wire Colour BLACK =  MD10B-24 or MD20B-24  Wire Number 1  ARM – UP TO MARCH 2006 ARM Series 1 & 2 Wire Colour RED  =  MD10B-230 or MD20B-230 Wire Number 3 ARM Series 1 & 2 Wire Colour BLUE  =  MD10B-230 or MD20B-230 Wire Number 2 ARM Series 1 & 2 Wire Colour BLACK  =  MD10B-23 or MD20B-230 Wire Number 1  ARM – SINCE MARCH 2006 ARM Series 1 & 2 Wire Colour BROWN  =  MD10B-230 or MD20B-230 Wire Number 3 ARM Series 1 & 2 Wire Colour BLACK  =  MD10B-230 or MD20B-230 Wire Number 2 ARM Series 1 & 2 Wire Colour BLUE  =  MD10B-230 or MD20B-230 Wire Number 1  Note: Should the Satchwell AR Series Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the S-E MD Actuator as follows: MD – S1  One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch  AR COMMON Wire Colour ORANGE  =  MD-S1 COMMON Wire Number S1 AR N/O contact Wire Colour BROWN  =  MD-S1 N/O contact Wire Number S3      AR N/C contact Wire Colour WHITE  =  MD-S1 N/C contact Wire Number S2  MD – S2  Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches  AR COMMON Wire Colour ORANGE  =  MD-S2 COMMON Wire Number S1 AR N/O contact Wire Colour BROWN  =  MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Colour WHITE  =  MD-S2 N/C contact Wire Number S2  AR COMMON Wire Colour BLACK  =  MD-S2 COMMON Wire Number S4 AR N/O contact Wire Colour RED  =  MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Colour BLUE  =  MD-S2 N/C contact Wire Number S5   Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MBF Series Flanged Rotary Shoe Valve Bodies ARE ARE Series 1 & 2 Wire Colour BLUE  =  MD20A-24 Wire Number 2 ARE Series 1 & 2 Wire Colour RED  =  MD20A-24 Wire Number 3 ARE Series 1 & 2 Wire Colour BLACK  =  MD20A-24 Wire Number 1 ARE Series 2        Wire Colour WHITE  =  MD20A-24 Wire Number 5  ARX ARX Series 1 & 2 Wire Colour RED  =  MD20B-24 Wire Number 3 ARX Series 1 & 2 Wire Colour BLUE  =  MD20B-24 Wire Number 2 ARX Series 1 & 2 Wire Colour BLACK =  MD20B-24 Wire Number 1  ARM – UP TO MARCH 2006 ARM Series 1 & 2 Wire Colour RED  =  MD20B-230 Wire Number 3 ARM Series 1 & 2 Wire Colour BLUE  =  MD20B-230 Wire Number 2 ARM Series 1 & 2 Wire Colour BLACK  =  MD20B-230 Wire Number 1  ARM – SINCE MARCH 2006 ARM Series 1 & 2 Wire Colour BROWN  =  MD20B-230 Wire Number 3 ARM Series 1 & 2 Wire Colour BLACK  =  MD20B-230 Wire Number 2 ARM Series 1 & 2 Wire Colour BLUE  =  MD20B-230 Wire Number 1  Note: Should the Satchwell AR Series Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the S-E MD Actuator as follows: MD – S1  One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch  AR COMMON Wire Colour ORANGE  =  MD-S1 COMMON Wire Number S1 AR N/O contact Wire Colour BROWN  =  MD-S1 N/O contact Wire Number S3 AR N/C contact Wire Colour WHITE  =  MD-S1 N/C contact Wire Number S2  MD – S2  Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches  AR COMMON Wire Colour ORANGE  =  MD-S2 COMMON Wire Number S1 AR N/O contact Wire Colour BROWN  =  MD-S2 N/O contact Wire Number S3 AR N/C contact Wire Colour WHITE  =  MD-S2 N/C contact Wire Number S2  AR COMMON Wire Colour BLACK  =  MD-S2 COMMON Wire Number S4 AR N/O contact Wire Colour RED  =  MD-S2 N/O contact Wire Number S6 AR N/C contact Wire Colour BLUE  =  MD-S2 N/C contact Wire Number S5
View full article
Picard Product_Support
‎2018-09-06 02:01 PM

on ‎2018-09-06 02:01 PM

Labels:
  • Field Devices
2032 Views

Replacement Digital Clock for Satchwell SVT4251 or CSC2726 and CSC2727 Controller.

Issue Need to replace Digital Clock for SVT4251 or CSC2726 and CSC2727 Controller. Environment SVT4251  CSC2726 CSC2727 Cause Faulty Clock Resolution Replacement Digital Clock for SVT4251 or CSC2726 and CSC2727 Controller is part number 561-9-261
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

on ‎2018-09-06 02:00 PM

Labels:
  • Field Devices
1318 Views

DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods

Issue DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods Environment DC1100 / DC1400 Discrete Controller installations. Cause DC1100 / DC1400 HWS time schedule is not Boiler Linked. Resolution Please check the catalog for current equipment Check Hot Water Link Option is set to Boiler Linked by following Controller access procedure :- Override Setting Switch :- select SET position. Display Screen / Navigation Buttons :- select parameters SYSTEMS MENU / ALTER SETTINGS / ENTER PASS No. (0112) HOT WATER / LINK OPTION Check LINK OPTION setting If LINK OPTION is set to INDEPENDENT then amend to BOILER LINKED If LINK OPTION is set to BOILER LINKED then PUMP RUN ON may be active If PUMP RUN ON  is active then Boiler outputs will be disabled until PUMP RUN time expires To amend PUMP RUN ON time :- select parameters SYSTEMS MENU / ALTER SETTINGS / ENTER PASS No. (0112) COMPENSATOR / SET-UP MENU / PUMP RUN-ON Amend Pump Run-On time period to 1 MINUTE and observe BOILER No.1 LED status should change from OFF to ON DC1100 / DC1400 Boiler No. 1 output (Terminal 10) should now be energised.
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

on ‎2018-09-06 01:55 PM

Labels:
  • Field Devices
1596 Views

SVT Optimiser Controller Time Switch settings should allow for selected Design Preheat Hours in order to enable the controlled space to recover to the required day temperature af...

Issue SVT Optimiser Controller does not enable the controlled space to recover to the required day temperature after an unoccupied period during which the inside air temperature has fallen to 12°C. Environment SVT4201 Optimiser Controller fitted with Analogue Time Switch. SVT4251 Optimiser Controller fitted with Digital Time Switch. Cause SVT Optimiser Controller Time Switch settings do not allow for selected Design Preheat Hours (DPH) Resolution SVT Optimiser Controller Time Switch settings should allow for selected Design Preheat Hours (DPH) SVT Optimiser Controller Time Switch settings should be carried out as follows :- Set Td to "Day" temperature required during occupancy. Set Tn to minimum "Night" temperature required during unoccupied periods. Set DPH to design preheat time. DPH is the maximum time required in order to enable the controlled space to recover to the required day temperature after an unoccupied period during which the inside air temperature has fallen to 12 deg. C. Select the approximate time in whole hours on the rotary switch (1 to 5 hours) Fine trim +/- 1/2 hour on the associated setting potentiometer. Note.  ALL "ON" times must be set earlier than the start of occupancy by the selected pre-heat time (DPH) set at (3) above. Example : DPH = 2 hours Occupancy time = 8.00 a.m. Set Time Switch "ON" time to 6.00 a.m. Setting the Time Switch "ON" time to 6.00 a.m. will enable the SVT Optimiser Controller to switch the plant ON at any time between 6.00 a.m. and 8.00 a.m. depending on the heating loss experienced in the controlled space during the preceding plant OFF period. N.B. The setting method detailed in the example above applies equally to both SVT4201 Analogue Time Switch and SVT4251 Digital Time Switch versions of the SVT Optimiser Controller.
View full article
Picard Product_Support
‎2018-09-06 01:46 PM

on ‎2018-09-06 01:46 PM

Labels:
  • Field Devices
1591 Views

Replacement Analogue Timeswitch for Satchwell SVT4201, CSC 1776, CSC 1777, CSC2776 or CSC2777 Controller.

Issue Need to replace Analogue Timeswitch for Satchwell SVT4201, CSC 1776, CSC 1777, CSC2776 or CSC2777 Controller. Environment SVT4201 CSC1776 CSC1777 CSC2776 CSC2777 Analogue Timeswitch. Cause Faulty Timeswitch requires replacement. Resolution Replacement Analogue Timeswitch for Satchwell SVT4201, CSC1776, CSC 1777, CSC2776 or CSC2777 Controller is part number 561-9-260.
View full article
Picard Product_Support
‎2018-09-06 01:22 PM

on ‎2018-09-06 01:22 PM

Labels:
  • Field Devices
1892 Views
  • « Previous
    • 1
    • …
    • 35
    • 36
    • 37
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore