Replacement of Satchwell AR Series 1 or AR Series 2 Rotary Actuator by S-E MD Series Rotary Actuator due to obsolescence. (Actuator Wiring)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacement of Satchwell AR Series 1 or AR Series 2 Rotary Actuator by S-E MD Series Rotary Actuator due to obsolescence. (A...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2042 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacement of Satchwell AR Series 1 or AR Series 2 Rotary Actuator by S-E MD Series Rotary Actuator due to obsolescence. (Actuator Wiring)

Picard Product_Support
‎2018-09-06 02:01 PM

on ‎2018-09-06 02:01 PM

Issue

Satchwell AR Series 1 or AR Series 2 Rotary Actuator requires replacement

Environment

  • Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MB Series or MBF Series Rotary Shoe Valve Bodies.
  • Satchwell ARE ARM & ARX Series 1 and Series 2 Rotary Actuators

Cause

Obsolescence of Satchwell AR Series 1 or AR Series 2 Rotary Actuators

Resolution

Replace Satchwell AR Series 1 or AR Series 2 Rotary Actuators with appropriate S-E MD Series Rotary Actuators and wire as follows:

  1. Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MB Series Screwed Rotary Shoe Valve Bodies
    • ARE
      • ARE Series 1 & 2 Wire Colour BLUE  =  MD10A-24 or MD20A-24 Wire Number 2
      • ARE Series 1 & 2 Wire Colour RED  =  MD10A-24 or MD20A-24  Wire Number 3
      • ARE Series 1 & 2 Wire Colour BLACK  =  MD10A-24 or MD20A-24  Wire Number 1
      • ARE Series 2        Wire Colour WHITE  =  MD10A-24 or MD20A-24  Wire Number 5 
    • ARX
      • ARX Series 1 & 2 Wire Colour RED  =  MD10B-24 or MD20B-24 Wire Number 3
      • ARX Series 1 & 2 Wire Colour BLUE  =  MD10B-24 or MD20B-24  Wire Number 2
      • ARX Series 1 & 2 Wire Colour BLACK =  MD10B-24 or MD20B-24  Wire Number 1 
    • ARM – UP TO MARCH 2006
      • ARM Series 1 & 2 Wire Colour RED  =  MD10B-230 or MD20B-230 Wire Number 3
      • ARM Series 1 & 2 Wire Colour BLUE  =  MD10B-230 or MD20B-230 Wire Number 2
      • ARM Series 1 & 2 Wire Colour BLACK  =  MD10B-23 or MD20B-230 Wire Number 1 
    • ARM – SINCE MARCH 2006
      • ARM Series 1 & 2 Wire Colour BROWN  =  MD10B-230 or MD20B-230 Wire Number 3
      • ARM Series 1 & 2 Wire Colour BLACK  =  MD10B-230 or MD20B-230 Wire Number 2
      • ARM Series 1 & 2 Wire Colour BLUE  =  MD10B-230 or MD20B-230 Wire Number 1 
    • Note: Should the Satchwell AR Series Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the S-E MD Actuator as follows:
      • MD – S1  One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch 
      • AR COMMON Wire Colour ORANGE  =  MD-S1 COMMON Wire Number S1
      • AR N/O contact Wire Colour BROWN  =  MD-S1 N/O contact Wire Number S3     
      • AR N/C contact Wire Colour WHITE  =  MD-S1 N/C contact Wire Number S2 
      • MD – S2  Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches 
      • AR COMMON Wire Colour ORANGE  =  MD-S2 COMMON Wire Number S1
      • AR N/O contact Wire Colour BROWN  =  MD-S2 N/O contact Wire Number S3
      • AR N/C contact Wire Colour WHITE  =  MD-S2 N/C contact Wire Number S2 
      • AR COMMON Wire Colour BLACK  =  MD-S2 COMMON Wire Number S4
      • AR N/O contact Wire Colour RED  =  MD-S2 N/O contact Wire Number S6
      • AR N/C contact Wire Colour BLUE  =  MD-S2 N/C contact Wire Number S5
         
  2. Satchwell AR Series 1 or AR Series 2 Rotary Actuators installed on Satchwell MBF Series Flanged Rotary Shoe Valve Bodies
    • ARE
      • ARE Series 1 & 2 Wire Colour BLUE  =  MD20A-24 Wire Number 2
      • ARE Series 1 & 2 Wire Colour RED  =  MD20A-24 Wire Number 3
      • ARE Series 1 & 2 Wire Colour BLACK  =  MD20A-24 Wire Number 1
      • ARE Series 2        Wire Colour WHITE  =  MD20A-24 Wire Number 5 
    • ARX
      • ARX Series 1 & 2 Wire Colour RED  =  MD20B-24 Wire Number 3
      • ARX Series 1 & 2 Wire Colour BLUE  =  MD20B-24 Wire Number 2
      • ARX Series 1 & 2 Wire Colour BLACK =  MD20B-24 Wire Number 1 
    • ARM – UP TO MARCH 2006
      • ARM Series 1 & 2 Wire Colour RED  =  MD20B-230 Wire Number 3
      • ARM Series 1 & 2 Wire Colour BLUE  =  MD20B-230 Wire Number 2
      • ARM Series 1 & 2 Wire Colour BLACK  =  MD20B-230 Wire Number 1 
    • ARM – SINCE MARCH 2006
      • ARM Series 1 & 2 Wire Colour BROWN  =  MD20B-230 Wire Number 3
      • ARM Series 1 & 2 Wire Colour BLACK  =  MD20B-230 Wire Number 2
      • ARM Series 1 & 2 Wire Colour BLUE  =  MD20B-230 Wire Number 1 
    • Note: Should the Satchwell AR Series Actuator include a wired Auxiliary Switch then the following Accessory should also be wired on the S-E MD Actuator as follows:
      • MD – S1  One independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switch 
      • AR COMMON Wire Colour ORANGE  =  MD-S1 COMMON Wire Number S1
      • AR N/O contact Wire Colour BROWN  =  MD-S1 N/O contact Wire Number S3
      • AR N/C contact Wire Colour WHITE  =  MD-S1 N/C contact Wire Number S2 
      • MD – S2  Two independent SPDT 1 mA…3(0.5) A, 250 V AC Auxiliary Switches 
      • AR COMMON Wire Colour ORANGE  =  MD-S2 COMMON Wire Number S1
      • AR N/O contact Wire Colour BROWN  =  MD-S2 N/O contact Wire Number S3
      • AR N/C contact Wire Colour WHITE  =  MD-S2 N/C contact Wire Number S2 
      • AR COMMON Wire Colour BLACK  =  MD-S2 COMMON Wire Number S4
      • AR N/O contact Wire Colour RED  =  MD-S2 N/O contact Wire Number S6
      • AR N/C contact Wire Colour BLUE  =  MD-S2 N/C contact Wire Number S5
Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 4807
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore