DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1328 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods

Picard Product_Support
‎2018-09-06 01:55 PM

on ‎2018-09-06 01:55 PM

Issue

DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods

Environment

DC1100 / DC1400 Discrete Controller installations.

Cause

DC1100 / DC1400 HWS time schedule is not Boiler Linked.

Resolution

Please check the catalog for current equipment

  1. Check Hot Water Link Option is set to Boiler Linked by following Controller access procedure :-
    • Override Setting Switch :- select SET position.
    • Display Screen / Navigation Buttons :- select parameters
    • SYSTEMS MENU / ALTER SETTINGS / ENTER PASS No. (0112)
    • HOT WATER / LINK OPTION
  2. Check LINK OPTION setting
    • If LINK OPTION is set to INDEPENDENT then amend to BOILER LINKED
    • If LINK OPTION is set to BOILER LINKED then PUMP RUN ON may be active
    • If PUMP RUN ON  is active then Boiler outputs will be disabled until PUMP RUN time expires
  3. To amend PUMP RUN ON time :- select parameters
    • SYSTEMS MENU / ALTER SETTINGS / ENTER PASS No. (0112)
    • COMPENSATOR / SET-UP MENU / PUMP RUN-ON
    • Amend Pump Run-On time period to 1 MINUTE and observe
    • BOILER No.1 LED status should change from OFF to ON
    • DC1100 / DC1400 Boiler No. 1 output (Terminal 10) should now be energised.
Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 5157
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now