Issue
DC1100 / DC1400 Boiler output does not energize during HWS time schedule ON periods
Environment
DC1100 / DC1400 Discrete Controller installations.
Cause
DC1100 / DC1400 HWS time schedule is not Boiler Linked.
Resolution
Please check the catalog for current equipment
- Check Hot Water Link Option is set to Boiler Linked by following Controller access procedure :-
- Override Setting Switch :- select SET position.
- Display Screen / Navigation Buttons :- select parameters
- SYSTEMS MENU / ALTER SETTINGS / ENTER PASS No. (0112)
- HOT WATER / LINK OPTION
- Check LINK OPTION setting
- If LINK OPTION is set to INDEPENDENT then amend to BOILER LINKED
- If LINK OPTION is set to BOILER LINKED then PUMP RUN ON may be active
- If PUMP RUN ON is active then Boiler outputs will be disabled until PUMP RUN time expires
- To amend PUMP RUN ON time :- select parameters
- SYSTEMS MENU / ALTER SETTINGS / ENTER PASS No. (0112)
- COMPENSATOR / SET-UP MENU / PUMP RUN-ON
- Amend Pump Run-On time period to 1 MINUTE and observe
- BOILER No.1 LED status should change from OFF to ON
- DC1100 / DC1400 Boiler No. 1 output (Terminal 10) should now be energised.