Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

DC1100 / DC1400 displays identical temperatures for all connected Sensors. It is not uncommon for a temperature of 39 deg C to be displayed for each Sensor connected to the Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • DC1100 / DC1400 displays identical temperatures for all connected Sensors. It is not uncommon for a temperature of 39 deg C t...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1533 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

DC1100 / DC1400 displays identical temperatures for all connected Sensors. It is not uncommon for a temperature of 39 deg C to be displayed for each Sensor connected to the Controller

Picard Product_Support
‎2018-09-06 01:20 PM

Issue

DC1100 / DC1400 displays identical temperatures for all connected Sensors.  It is not uncommon for a temperature of 39 deg C to be displayed for each Sensor connected to the Controller.

Environment

DC1100 Stand Alone Optimiser / Compensator Controller

DC1400 Stand Alone Optimiser / Compensator Controller

Sensors compatible with DC1100 :-

A701 Room Temperature Sensor

A702 Outside Air Temperature Sensor

A703 Pipe Temperature Sensor

A704 Contact Temperature Sensor

STC 600 D Contact Temperature Sensor           (Original Drayton Sensor = A704)

STO 600 D Outside Air Temperature Sensor      (Original Drayton Sensor = A702)

STP 600 D Pipe Temperature Sensor                 (Original Drayton Sensor = A703)

STR 600 D Room Temperature Sensor              (Original Drayton Sensor = A701)

Sensors compatible with DC1400 :-

STC 600 Contact Temperature Sensor               (Original Satchwell Sensor = DST)

STO 600 Outside Air Temperature Sensor          (Original Satchwell Sensor = DOT)   

STP 660 Pipe Temperature Sensor                     (Original Satchwell Sensor = DWT)

STR 600 Room Temperature Sensor                  (Original Satchwell Sensor = DRT)

39 deg C.

Cause

DC1100 / DC1400 displays identical temperatures for all connected Sensors.  A Sensor temperature of 39 deg C is a common value displayed.

Resolution

  1. Check each Sensor is correctly connected to its appropriate "Common" Terminal of the DC1100 / DC1400 Wiring Base
  2. Check each Sensor Cable Screen is correctly connected to the Earth Terminal of the DC1100 / DC1400 Wiring Base
  3. Check that a good Earth connection exists between the Earth Terminal of the DC1100 / DC1400 Wiring Base and the site Earth
  4. Check that a good site Earth is available for connection to the DC1100 / DC1400 Wiring Base.

N.B.

In the event that the DC1100 / DC1400 continues to display identical temperatures for all connected Sensors following completion of the above checks then it is suggested that the Cold Start procedure is applied to the Controller and the result observed.

Labels (1)
Labels:
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • 6086
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore