Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,825
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 322
    • 323
    • 324
    • …
    • 509
  • Next »

TS-58XXX & TS-81XXX Cover Kits w/inserts

Issue TS-58XXX & TS-81XXX Cover Kits w/inserts Environment TS-58XXX TS-81XXX Cause Compatible cover kits are not noted in the catalog. Resolution AT-80 Cover Kit will work.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1167 Views

What is the packing Gland for obsolete TAC Globe Valves: VB-9XXX 2" and Smaller.

Issue What is the packing Gland for obsolete TAC Globe Valves: VB-9XXX 2" and Smaller. Environment TAC Globe Valves: VB-9XXX 2" and Smaller Cause Obsolete product. Resolution Part # YBA-616-1 Not listed separately for repair parts.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1330 Views

Packing Gland Nut for TAC VB-9XXX Globe Valves 2 1/2" and larger.

Issue Packing Gland Nut for TAC VB-9XXX Globe Valves 2 1/2" and larger. Environment TAC VB-9XXX Globe Valves 2 1/2" and larger Cause Not listed in repair parts Resolution NYBA-63
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1265 Views

Valve Linkage Kits for Hazardous Location Gear Train Actuators that mount on TAC Globe Valves: VB-7XXX & VB-9XXX.

Issue Valve Linkage Kits for Hazardous Location Gear Train Actuators that mount on TAC Globe Valves: VB-7XXX & VB-9XXX. Environment Valve Linkage VB-7XXX VB-9XXX Cause Part number for Valve Linkage Kits. Resolution Linkages are AV-291, AV-293, AV-295, AV-296 Reference literature # F-27441.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • Field Devices
1044 Views

Updating the Loytec NIC driver

Issue Updating the Loytec NIC driver Environment NIC852 NIC-USB Cause You can run into trouble upgrading the Loytec NIC driver on a PC where there is already an existing TAC Vista installation. If you do the update like this, you should stay clear. Resolution Stop TAC Vista Server, and if it's running as a service, set it to disabled. Unplug the NIC-USB or NIC852. Uninstall the NIC driver. Delete the folder %ProgramFiles%\Loytec\NIC Delete the HKLM\SOFTWARE\LOYTEC folder in the registry Reboot the PC Install the new Loytec driver Reboot the PC Insert the NIC-USB or NIC852 Start TAC Vista server
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • TAC Vista
1359 Views

Setting "Notification on change" for a Xenta Server in Vista does not result in a reduction in traffic

Issue When setting "Notification on change" on a Xenta Server in Vista, nothing seems to happen. There is no reduction in the traffic. Environment XBuilder Confirmed in Vista version 5.1.1 Cause If you have a space in the XBuilder project name (see Project > Settings) "Notification on change" does not work. Resolution In XBuilder, navigate to Project > Settings If there is a space in the Project Name, delete the space or substitute with an underscore Upload the project again.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • TAC Vista
781 Views

Different ranges of SNVT_press, SNVT_press_p, and SNVT_press_f

Issue SNVT_press_p cannot represent a value above 32766 Pa Sending a value of 15psi out of a Menta application using a SNVT_press_p and it is arriving at the receiving controller as 4.75psi. Environment SNVT_press_p Menta LonMaker/NL220 Cause All LON communication is transmitted in metric units, so the data sizes are limited by the valid range of Pascals (or kiloPascals for SNVT_press). Resolution There are three different SNVT types defined to represent a pressure (gauge) value. SNVT_press, SNVT_press_f, and SNVT_press_p. It is important to recognize the valid ranges of data each one can represent. Name Units Maximum Minimum SNVT_press kiloPascals 3,276.70 -3,276.80 psi 475.25 -475.26 inches wc 13,154.74 -13,155.15 SNVT_press_f Pascals 3.40E+38 -3.40E+38 psi 4.94E+34 -4.94E+34 inches wc 1.37E+36 -1.37E+36 SNVT_press_p Pascals 32,766.00 -32,768.00 psi 4.75 -4.75 inches wc 131.48 -131.48
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • TAC Vista
1567 Views

What is the scan rate for the inputs and outputs of a MNL-20R?

Issue What is the scan rate for the inputs and outputs of a MNL-20R? Environment MNL-20R Cause Require fast response time for high-speed applications. Resolution Inputs = 220 ms Outputs = 100 ms
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • TAC IA Series
828 Views

Using Workplace Tech with a MNL-VxRVx controller, the nciBalanceOvrd snvt was used to set the VAV damper to the full closed and full open positions. After 10-15 minutes the overrid...

Issue Using Workplace Tech with a MNL-VxRVx controller, the nciBalanceOvrd snvt was used to set the VAV damper to the full closed and full open positions. After 10-15 minutes the override was automatically cleared. Why does this happen? Environment Workplace Tech MNL-VxRVx controller Cause This is a built-in feature of the MNL-VxRVx controller. Resolution The override on this snvt times out and clears automatically - unless the override is re-applied every few minutes. This feature was added to prevent the damper from being left in an override state accidentally. For example, when using the MicroNet Flow Balance Tool, a damper can be overridden open or closed as a part of a test balance. If the Tool was accidentally disconnected from the controller, or, the user forgot to release the override, the MNL controller will clear the override automatically after 10-15 minutes.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • TAC IA Series
1197 Views

Can a Belimo damper actuator (i.e. NF-24SR) be powered from the same transformer as a DMS MSC-MPC Microsmart controller?

Issue Can a Belimo damper actuator (i.e. NF-24SR) be powered from the same transformer as a DMS MSC-MPC Microsmart controller? Environment Belimo damper actuator DMS MSC-MPC (Microsmart controller) Cause The MSC-MPC controller is a full-wave rectified device and the Belimo actuators are half-wave rectified devices. Resolution It is recommended that the MSC-MPC and the actuator have their own separate power supply. Using the same transformer to power both devices could result in component level damage to the MSC-MPC.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • TAC IA Series
1452 Views

Remove an installed TAC Xenta OP from the LNS network

Issue Remove a TAC Xenta OP that is commissioned in LNS from the LNS network. Product Line TAC Vista Environment TAC Xenta OP installed and commissioned in an LNS network Cause If an installed OP is to be removed from the LNS network, it should be restored to the original factory setting to avoid problems, before it is used in another LonWorks network. Resolution OP version >= 3.40 Check in the OP Service menu #10. OP mode that Mode is set to MAN, Disconnect the OP electrically from the LonWorks network. Remove the OP from the LNS database. OP version < 3.40 Check in the OP Service menu #10. OP mode that Mode is set to TAC or MAN, (in OP version < 3.11, Bindable OFF). Start the LonMaker Browser. Restore SNVT_config_src from cfg_external (1) to cfg_local (0). SNVT_config_src may be called var_2 in the Browser. Disconnect the OP electrically from the LonWorks network. Remove the OP from the LNS database. Factory setting If the OP has been de-installed in an incorrect way, it may be restored to the factory setting in one of two ways: Reconnect the OP to the network, reinstall it and perform the steps above in the correct order, Use the Nodeutil program and perform the following. Select OP Service menu #10. OP mode that Mode is set to TAC or MAN, (in OP version < 3.11, Bindable OFF). Start Nodeutil. Press the Service pin of the OP. Type G (Goto) Type 1, and then press Enter. Type M (Mode) Type S (State) Type C (Configure) Type U (Update) Type 2 (nciNetConfig) and then press Enter. Type 00 (cfg_local) and then press Enter.
View full article
Picard Product_Support
‎2018-09-06 02:35 PM

Labels:
  • TAC Vista
1437 Views

InVue Developer year displays first two digits instead of last two

Issue With InVue Developer, adding dates to a NETWORK 8000 Holiday Schedule OCX, the year displays as "20" instead of "09" (for 2009) or "10" (for 2010). Environment Windows NT Windows 2000 InVue Developer NETWORK 8000 Holiday Schedule OCX Cause By default, Windows NT and Windows 2000 display the short date as "M/d/yyyy" Resolution Go to Windows Control Panel > Regional Options > Date tab Change the Short date format to "MM/dd/yy" Click OK.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
1065 Views

On a Niagara R2 computer, the following error appears (in the Niagara Console) when trying to run Workplace Pro: *** Unjar: c:\niagara\r2.301.522\nre\modules\demo.unjar Extract...

Issue On a Niagara R2 computer, the following error appears (in the Niagara Console) when trying to run Workplace Pro: *** Unjar: c:\niagara\r2.301.522\nre\modules\demo.unjar Extract: c:\niagara\r2.301.522\nre\modules\demo.unjar java.util.zip.ZipException. Environment Niagara R2 computer Cause .unjar files in the listed directory on the computer. Resolution The .unjar files are used by the Niagara installer during installation and have somehow been copied into the listed directory on the computer. Stop the Niagara Service on the computer, delete all .unjar files in the listed directory, then re-start the Niagara Service. Workplace Pro will now function.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
1011 Views

Can one computer be configured to do both Niagara R2 and G3 serial tunneling?

Issue Can one computer be configured to do both Niagara R2 and G3 serial tunneling? Environment Computer Niagara R2 serial Niagara G3 serial Cause Running Niagara R2 and G3 simultaneously on one COM port cause issues. Resolution Yes. The Niagara R2 and G3 serial tunnel client programs install separate services in Windows. They can run simultaneously as long as they are not using the same COM port. If this is not possible, then start and use only one service at a time.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
1010 Views

How does a Niagara R2 Master Enterprise Server work?

Issue How does a Niagara R2 Master Enterprise Server work? Environment Niagara R2 Master Enterprise Server Cause Installation site have Master Enterprise server and need information on the functionality of the Niagara R2 Master Enterprise Server. Resolution Here is a list of features and settings for a Master Enterprise Server: It allows the archiving of logs from subordinate Enterprise Servers It requires the “multisite” feature in its license file.  This allows it to use the “Poll Archive” Service. The Poll Archive Service can be found in the local library / tridiumx / Multisite jar file. The Poll Archive Service is not required for the client devices. The Poll Archive service brings all data from the Application Database (“App” Folder) of the subordinate Enterprise Server. The new polled data is appended to the previous polled data in the Master Enterprise Server. The Address Book of the Master Enterprise Server must include the client stations as subordinates. Poll Archive Groups are individually enabled and each group has its own poll frequency. On the properties of the Poll Archive Service, enable the appropriate Poll Archive Groups and enter the poll frequency, in hours. A Date-Time Trigger object can be linked to the Poll Archive Service, which allows a choice of date and time for polling. Use the “Link From, Link To” method to create the link. A poll can be manually invoked by right-clicking the Services Container, choosing Go – Service Manager and then double-clicking the Poll Archive Service in the Service Manager. On the right of the screen, highlight the Poll Group and click the “Invoke” button on the lower right. It can get log data directly from log objects in a UNC 5x0 or 6x0. In the log object, check the box for “polled” next to archiveSetup. If the Master Enterprise Server is receiving polled data from a log object in a client station (which could be another Enterprise Server, a UNC 6x0 or a UNC 5x0), then the log service for the client station must be set to Archive Remote. If the Master Enterprise Server is receiving polled data from a client station’s already archived data (that is, from another Enterprise Server or a UNC 6x0 with Database Services), then the log service for the client station must be set to Archive Local. The Address Book of the client device does NOT need to include the Master Enterprise Server. The Poll group will be determined by the Master Enterprise Server’s Address Book. The archived data in the Master Enterprise Server can be viewed, as usual, in WorkPlace Pro with the Database Browser, or in the browser using the appdb, archive/index or chart/log servlets.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
1125 Views

A Niagara R2 Enterprise Server station fails to start. The Standard Output Window reports this error: ERROR: Cannot add key entry: 8390 java.lang.IllegalStateException: Missing c...

Issue A Niagara R2 Enterprise Server station fails to start. The Standard Output Window reports this error: ERROR: Cannot add key entry: 8390 java.lang.IllegalStateException: Missing class for: 24 Environment Niagara R2 Enterprise Server station Cause Conflicting jar files. Resolution This is typically related to a missing jar file. This would be a jar file that is NOT part of a released version of Workplace Pro. For example, the Smartware and Distech jar files.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
1238 Views

Can a Network 8000 Microzone II base from 1993 (part numbers MZ2A-105 or MZ2A-106) be used with a MNL-800 controller card (part number MNL-800-101)?

Issue Can a Network 8000 Microzone II base from 1993 (part numbers MZ2A-105 or MZ2A-106) be used with a MNL-800 controller card (part number MNL-800-101)? Environment Network 8000, Microzone II Cause Product  obsolescence Resolution The Microzone II base has been through a few revisions but nothing that would prevent the MNL-800 controller card from working with it.  Most of the revisions had to do with improving the power transient protection. If this is not a concern, then just note that the terminations and terminal labels will be slightly different.  Ensure all I/O is reading correctly before leaving the jobsite. ENCL-MZ800-PAN & ENCL-MZ800-WALL are replacement part numbers for the MZ2A-105 or MZ2A-106.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
1460 Views

Can a second space sensor be added to the Micronet 2000 MN-FLO or MN-FLO3T controller?

Issue Can a second space sensor be added to the Micronet 2000 MN-FLO or MN-FLO3T controller? Environment MicroNet 2000 MN-FLO / MN-FLO3T controller MN-S MN-SO MN-SDK Cause Two MicroNet Sensors to one MicroNet Controller won’t function if the second MicroNet sensors address is not set to 2. Resolution Yes. The MN-FLO and MN-FLO3T supports 2 MN-S / MN-SO / MN-SDK sensors connected simultaneously. Ensure the second sensor added is addressed as "2". The sensors come from the factory addressed as "1". To change the address, simply cut the Trace Foil. The sensor that is address 2 will only function as a temperature indicator. Review the MN-S/MN-SO/MN-SDK General Instructions Guide (F-25715), page 7 Figure 8.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
928 Views

How does the nciSetpts snvt integrate to Niagara R2 for a Viconics Thermostat Model # VT7200C1018E (programID = 80:0:c5:55:0:4:4:1b)

Issue How does the nciSetpts snvt integrate to Niagara R2 for a Viconics Thermostat Model # VT7200C1018E (programID = 80:0:c5:55:0:4:4:1b) Environment Niagara R2 Viconics Thermostat (Model# VT7200C1018E) Cause Information will help configure the Niagara R2 for a Viconics Thermostat. Resolution The correct shadow object is T7XFCr. Use the SnvtTempSetptCmd object to link with the nciSetpts snvt. Note that if a setpoint is changed at the thermostat's local display, it will be used as the controlling setpoint regardless of the value provided by the nciSetpts snvt.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
1095 Views

In a Niagara R2 Enterprise Server station, the DDE Service is installed but it is not communicating to the 3rd-party product.

Issue In a Niagara R2 Enterprise Server station, the DDE Service is installed but it is not communicating to the 3rd-party product. Environment Niagara R2 Enterprise Server station DDE Service Cause No longer support the DDE service. Resolution The DDE driver is an old driver that Tridium did not update over the years. Its last supported operating system is Windows 2000. Product Support Services does not support this driver and Tridium does not recommend using it for any new installations.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC IA Series
954 Views
  • « Previous
    • 1
    • …
    • 322
    • 323
    • 324
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of