Can a Belimo damper actuator (e.g., NF-24SR) be powered from the same transformer as a DMS MSC-MPC Microsmart controller?
TAC IA Series
  • Belimo damper actuator
  • DMS MSC-MPC (Microsmart controller)
The MSC-MPC controller uses full-wave rectification, while Belimo actuators use half-wave rectification. Sharing the same transformer introduces electrical incompatibility, which can lead to component-level damage in the MSC-MPC controller.
  • Do not share the same transformer between MSC-MPC controllers and Belimo actuators.
  • Provide separate power supplies for each device to prevent electrical interference and potential damage.