Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

How does a Niagara R2 Master Enterprise Server work?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How does a Niagara R2 Master Enterprise Server work?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1225 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How does a Niagara R2 Master Enterprise Server work?

Picard Product_Support
‎2018-09-06 02:34 PM

Issue

How does a Niagara R2 Master Enterprise Server work?

Environment

Niagara R2 Master Enterprise Server

Cause

Installation site have Master Enterprise server and need information on the functionality of the Niagara R2 Master Enterprise Server.

Resolution

Here is a list of features and settings for a Master Enterprise Server:

  1. It allows the archiving of logs from subordinate Enterprise Servers
  2. It requires the “multisite” feature in its license file.  This allows it to use the “Poll Archive” Service. The Poll Archive Service can be found in the local library / tridiumx / Multisite jar file. The Poll Archive Service is not required for the client devices.
  3. The Poll Archive service brings all data from the Application Database (“App” Folder) of the subordinate Enterprise Server. The new polled data is appended to the previous polled data in the Master Enterprise Server.
  4. The Address Book of the Master Enterprise Server must include the client stations as subordinates.
  5. Poll Archive Groups are individually enabled and each group has its own poll frequency. On the properties of the Poll Archive Service, enable the appropriate Poll Archive Groups and enter the poll frequency, in hours.
  6. A Date-Time Trigger object can be linked to the Poll Archive Service, which allows a choice of date and time for polling. Use the “Link From, Link To” method to create the link.
  7. A poll can be manually invoked by right-clicking the Services Container, choosing Go – Service Manager and then double-clicking the Poll Archive Service in the Service Manager. On the right of the screen, highlight the Poll Group and click the “Invoke” button on the lower right.
  8. It can get log data directly from log objects in a UNC 5x0 or 6x0. In the log object, check the box for “polled” next to archiveSetup.
  9. If the Master Enterprise Server is receiving polled data from a log object in a client station (which could be another Enterprise Server, a UNC 6x0 or a UNC 5x0), then the log service for the client station must be set to Archive Remote.
  10. If the Master Enterprise Server is receiving polled data from a client station’s already archived data (that is, from another Enterprise Server or a UNC 6x0 with Database Services), then the log service for the client station must be set to Archive Local.
  11. The Address Book of the client device does NOT need to include the Master Enterprise Server.
  12. The Poll group will be determined by the Master Enterprise Server’s Address Book.
  13. The archived data in the Master Enterprise Server can be viewed, as usual, in WorkPlace Pro with the Database Browser, or in the browser using the appdb, archive/index or chart/log servlets.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3596
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore