Setting "Notification on change" for a Xenta Server in Vista does not result in a reduction in traffic
  • Setting "Notification on change" for a Xenta Server in Vista does not result in a reduction in traffic
  • HenrikTarpgaard
    HenrikTarpgaard
‎2018-09-06 02:35 PM
When setting "Notification on change" on a Xenta Server in Vista, nothing seems to happen. There is no reduction in the traffic.
  • XBuilder
  • Confirmed in Vista version 5.1.1
If you have a space in the XBuilder project name (see Project > Settings) "Notification on change" does not work.
  1. In XBuilder, navigate to Project > Settings
  2. If there is a space in the Project Name, delete the space or substitute with an underscore
  3. Upload the project again.
  • 3570